I run into many chimney flue like this one. I always recommend the insulation be pulled back away from all flues and to Seal the gap between the flue and metal flashing with special high-temperture silcone caulk. I would like to hear others points of views on this. Thanks
|
|
#2
|
||||
|
||||
|
Quote:
http://www.csia.org/pressroom/press-...-explained.htm Joseph P. Hagarty, CMI joseph.hagarty@comcast.net Main Line Inspections, Inc. Phone: 610-399-3675 Email: MainLineHI@comcast.net http://pa.nachi.org/mainlinepa/about.html http://www.householdinspector.com National President / NACHI (2003-2004) NACHI Education Committee Member |
|
#3
|
||||
|
||||
|
Quote:
Many manufacturers don't specify fire caulking around factory firestops from what I have found. Maybe someone else can expand on this. |
|
#4
|
||||
|
||||
|
Many manufacturers don't specify fire caulking around factory firestops from what I have found. Maybe someone else can expand on this.[/quote]
It could be due to expansion and contraction of the metals. (guessing) I would check with the MFG on the proper installation of this flue fire stop. In general: I believe any recommendation we make should be carefully checked before we tell the client. The potential for mis-information is huge and could make us look bad and should the client DIY. What happens when it's wrong? Does the warranty or service plan get void... "Dam Home inspector told me to do it".... Be careful.. |
|
#5
|
|||
|
|||
|
Please Note:
jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
good advise Patrick, Thank you everyone for your replies
|
|
#6
|
||||
|
||||
|
Check out the proper attic section required.
http://servicesales.com/metal-fab/shields.html Hope this helps. Marcel |
|
#7
|
||||
|
||||
|
Please Note:
hspinnler is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#8
|
||||
|
||||
|
Quote:
Take the time to write this one up.This is definetly a defect and you can't solve it by moving the insulation away. I would suggest an 'INSULATED ATTIC RADIATION SHIELD' remember that you have to maintain 2" safety clearance from surrounding combustible material. Mario 'Imagination is more important than knowledge' (sometimes) Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007 www.360degreeshomeinspections.com Tel.# 416-722-6132 e-mail torontohomeinspector@yahoo.com |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| WOOD cap over Chimney Flue!?! | mlong | Exterior Inspections | 4 | 9/11/07 11:33 AM |
| Gas and oil hot water tank and Boiler Share Vents | hvanderbeek | Miscellaneous Discussion for Inspectors | 8 | 1/25/07 6:22 PM |
| Flue Size when size matters? | msylvester | Inspecting HVAC Systems | 14 | 1/21/07 12:29 AM |
| Fireplace Enclosure | jpope | Interior Inspections | 19 | 10/25/06 6:08 PM |