A question came up on the correct size that an rafter collar tie should be and how many should be used. Does any body know the correct answer for this? I see mostly 2x4's. If you can help please let me know, and what your source is.
Thanks
Rick
Reply With Quote
  #2  
Old 5/2/06, 8:23 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Collar Ties

Too many variables to answer your question properly, please re-phrase and explain the condition , and pictures would help.

Marcel
Reply With Quote
  #3  
Old 5/2/06, 9:01 PM
John Bowman's Avatar
John Bowman John Bowman is offline
Active Poster
 
Join Date: Dec 2003
Location: ROME, PA
Posts: 2,202
Please Note: jbowman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Collar Ties

Richard,

Most jurisdictions have only one regulation for collar ties, and that regulation is: They must be at least one inch thick. Some have two regulations, they must be at least one inch thick and placed at least every four foot.

How's that. Not much was it.
Reply With Quote
  #4  
Old 5/2/06, 9:12 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Collar Ties

John;

Every little bit helps, right?

I would prefer something of the 1 1/2" thickness to match the pitch of the roof action.

Since I don't know the pitch of the roof, I guess one could say that the 1" would be inadequate.

Marcel
Reply With Quote
  #5  
Old 5/2/06, 11:25 PM
jmichalski's Avatar
jmichalski jmichalski is offline
Active Poster
 
Join Date: Aug 2004
Location: Souderton, PA
Posts: 2,532
Please Note: jmichalski is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Collar Ties

Most of the collar ties I have seen are at least 1" think and spaced on every third rafter. I have seen all kinds of material used to comprise collar ties including left over floor boards, 2 x 4's, 2x8's, and furring strips.

They come in all shapes and sizes. I recommended upsizing the furring strips as they were not doing the job (mostly split and rafters were beginning to seperate from the ridge board.)
Reply With Quote
  #6  
Old 5/3/06, 6:44 AM
John Bowman's Avatar
John Bowman John Bowman is offline
Active Poster
 
Join Date: Dec 2003
Location: ROME, PA
Posts: 2,202
Please Note: jbowman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Collar Ties

Quote:
Originally Posted by jmichalski
Most of the collar ties I have seen are at least 1" think and spaced on every third rafter. I have seen all kinds of material used to comprise collar ties including left over floor boards, 2 x 4's, 2x8's, and furring strips.

They come in all shapes and sizes. I recommended upsizing the furring strips as they were not doing the job (mostly split and rafters were beginning to seperate from the ridge board.)
Don't forget the good ole mighty cable. It's sometimes fun living in cow country. I'll still never forget the house that was plumbed by an ole time farmer. Must have been at least 200 feet of garden hose used.
Reply With Quote
  #7  
Old 5/3/06, 7:47 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Collar Ties

Quote:
Originally Posted by jbowman
I'll still never forget the house that was plumbed by an ole time farmer. Must have been at least 200 feet of garden hose used.
John,

That farmer moved out here...

Last edited by dvalley; 10/7/07 at 5:41 PM..
Reply With Quote
  #8  
Old 5/3/06, 10:07 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: Collar Ties

Many builders will think one inch thick includes a 1x6 and it does not.

A 2x6 is the minimum any one should consider.
Even if some code allows a 2x4 it is just plain wrong unless the length of it is less than 3 feet.
Reply With Quote
  #9  
Old 5/3/06, 7:46 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Collar Ties

Quote:
Originally Posted by bking
Many builders will think one inch thick includes a 1x6 and it does not.

A 2x6 is the minimum any one should consider.
Even if some code allows a 2x4 it is just plain wrong unless the length of it is less than 3 feet.
Bruce,

1x's are fine...
Reply With Quote
  #10  
Old 5/5/06, 8:56 AM
twheeler
Guest
 
Posts: n/a
Please Note: is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Collar Ties

Here in Canada, the minimum size is 1x4, and they must be placed at all jack rafters that exceed the span requirements, after all, they are not only used for strength, but to reduce the span. Also in Canada, there is a code for the amount of nails used in collar ties.
Reply With Quote
  #11  
Old 5/9/06, 2:31 AM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Collar Ties

Richard,

You should post this in the structural section. There are some some sharp structual engineers that will likely reply to your post. They may not be monitoring the interior section.

Does eveyone know the difference between a rafter tie and a collar tie? A rafter tie is placed in the lower third of the roof framing to prevent rafter/wall spreading. A collar tie is placed in the upper third of the roof framing and holds the rafter down to the ridge.

Last edited by pdickerson; 5/9/06 at 3:00 AM..
Reply With Quote
  #12  
Old 5/10/06, 8:01 AM
Rick Koehler Rick Koehler is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Dingmans Ferry, PA
Posts: 20
Default Re: Collar Ties

Thanks to all. It is just what I thought, there is no right answer. All different sizes are used. I may look up the local code and let all know.
Regards
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Handle ties on circuit breakers chellickson Electrical Inspections 18 5/7/07 5:20 PM
vent collar fix by new home builder srowe Exterior Inspections 5 1/28/07 5:03 PM
Brick Ties psmothers Exterior Inspections 4 6/7/06 7:43 PM
Collar Ties--When Required? jfunderburk Structural Inspections 7 5/6/06 2:49 PM
No Brick Ties - Wall Buldge Stew Structural Inspections 1 4/22/06 7:56 AM


All times are GMT -4. The time now is 1:40 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts