Default Common wall of garage is Laundry room / firewall ?

the backwall wall is common to the laundry room.....the door opens
to a bonus room......the house was built in 1964....the common wall is wood ....Should I recommed that drywall be installed? ( as a fire barrier)


all of the wall ......left of the door is a laundry room. Directly thru the
door is a bonus room (living area)



Reply With Quote
Find an InterNACHI certified South Carolina Home Inspector (and anywhere else in North America)
  #2  
Old 6/23/09, 8:19 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 1,893
Default Re: Common wall of garage is Laundry room / firewall ?

Depends how thick the plywood is. The door is not fire rated.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #3  
Old 6/25/09, 12:02 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Common wall of garage is Laundry room / firewall ?

The wall and door must be a rated assembly.

This is what I would state;

Quote:
There is no firewall separation between the garage and the residence, which is mandated. You should consult and employ the services of a qualified contractor to install the components necessary to maintain a separation that will comply with State or Local requirements.
For the door, I would state;

Quote:
The house entry door is not identified as being fire-rated and must be, to maintain the necessary firewall separation between a garage and living quarters, and will need to be replaced.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 6/25/09, 12:10 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,707
Send a message via Yahoo to jfunderburk
Default Re: Common wall of garage is Laundry room / firewall ?

Jeff, do you feel there is a duty to upgrade an older home to today's standards? I cringe at the word "mandated" and "will need to be replaced". This is still America and buyers nor sellers don't have to do as we say. I would phrase it a little less authoritatively, such as:

"There is no firewall separation between the garage and the residence, which is required by today's commonly accepted construction standards...We recommend installation of a functional fire barrier for safety reasons." (Emphasis added.)



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 6/25/09, 12:36 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Common wall of garage is Laundry room / firewall ?

Quote:
Originally Posted by jfunderburk View Post
Jeff, do you feel there is a duty to upgrade an older home to today's standards?
No, but to the best of my knowledge, there has always been a fire separation requirement for an attached garage.

If I considered it an "upgrade" to newer standards, I would word it that way.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 6/25/09, 12:59 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Common wall of garage is Laundry room / firewall ?

Quote:
Originally Posted by jpope View Post
No, but to the best of my knowledge, there has always been a fire separation requirement for an attached garage.

If I considered it an "upgrade" to newer standards, I would word it that way.
Agreed, that requirement goes back to the 1920's if memory serves

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #7  
Old 6/25/09, 1:02 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,707
Send a message via Yahoo to jfunderburk
Default Re: Common wall of garage is Laundry room / firewall ?

Well if so, it must not have been enforced here in the Carolinas. I grew up in a home built in 1972 with a plywood separation (Mother still lives there). Most homes around here older than 20 years old do not have a functional fire barrier.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 6/25/09, 1:28 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Common wall of garage is Laundry room / firewall ?

Hi Joe,

that may well be the case in your area, but that would surprise me.

The 1 hours firewall rule was in the 1st edition of the UBC in 1927 (yeah I just had to look it up) and UBC and others are the for-runners of todays IRC/IBC.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #9  
Old 6/25/09, 7:47 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Common wall of garage is Laundry room / firewall ?

Quote:
Originally Posted by jfunderburk View Post
Jeff, do you feel there is a duty to upgrade an older home to today's standards?
There's absolutely no requirement to upgrade an older home to today's code standards, but I would always recommend a firewall upgrade (separating living area from garage area) in older homes simply as a safety feature.
Reply With Quote
  #10  
Old 6/25/09, 8:54 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,469
Default Re: Common wall of garage is Laundry room / firewall ?

Quote:
Originally Posted by dvalley View Post
There's absolutely no requirement to upgrade an older home to today's code standards, but I would always recommend a firewall upgrade (separating living area from garage area) in older homes simply as a safety feature.
Exactly...I recommend the same.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #11  
Old 6/25/09, 11:51 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Common wall of garage is Laundry room / firewall ?

I don't consider it an "upgrade" when it is/was a required component.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 6/26/09, 4:32 AM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Common wall of garage is Laundry room / firewall ?

It could be that the laundry to bonus room is the intended firewall. Was there a fire rated door possibly at that location?

www.MauiHomeInspections.com
Reply With Quote
  #13  
Old 6/26/09, 9:22 AM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,856
Default Re: Common wall of garage is Laundry room / firewall ?

David,

Was this garage created from an existing car port?





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
Find an InterNACHI certified South Carolina Home Inspector (and anywhere else in North America)
  #14  
Old 6/27/09, 12:40 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,407
Send a message via ICQ to kshepard
Default Re: Common wall of garage is Laundry room / firewall ?

With this sort of thing, I mention that it may not have been required at the time the home was built, but that widely-accepted modern standards require it for safety reasons, then I recommend it be brought into compliance with modern standards.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #15  
Old 6/27/09, 12:57 AM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Common wall of garage is Laundry room / firewall ?

Quote:
Originally Posted by mkyriacou View Post
David,

Was this garage created from an existing car port?

This idea gets my vote which makes it an incomplete carport to garage conversion and repairs should be peformed to bring it into the accepted standard that has been in force since the first building code in 1927.

www.MauiHomeInspections.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
something else to chew on john bubber Structural Inspections 662 1/31/12 2:33 PM
Where do I put the Aquarium? mcyr Structural Inspections 3 11/6/07 4:05 PM
Fire wall tyeager Structural Inspections 38 8/24/07 12:17 PM
Common Defects List by Age of House trausch Inspection Education & Training 10 6/12/06 5:52 AM


All times are GMT -4. The time now is 4:49 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts