A quick (hopefully) question. Does anybody know (can provide reference to) what is the building code requirement for the door entering into a condo unit in the city of Philadelphia? (ie) metal, solid, fire rating etc. thanks, Peter Peter Ehrenpreis NACHI #05090693 Vienna, VA VP NOVANACHI (Northern Viginia) Chapter www.novanachi.org "NACHI, The right choice" |
|
#2
|
|||
|
|||
|
Please Note:
Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Entering from a corridor? Entering from the exterior? If from a corridor, and the corridor walls are fire-resistance-rated, then the door needs to be labeled in accordance with the wall rating. If entering from the exterior, I don't believe any rating or any other such requirement exists, other than energy usage requirements.
|
|
#3
|
|||
|
|||
|
Yes,
Entering from a corridor, it is a three story with three units. The bottom unit has a metal door the middle and upper do not. Thanks for any (additional) help. Peter Peter Ehrenpreis NACHI #05090693 Vienna, VA VP NOVANACHI (Northern Viginia) Chapter www.novanachi.org "NACHI, The right choice" |
|
#4
|
||||
|
||||
|
There are no requirements that I am aware of. I see all types of interior doors for condos and apartments here. Raised panels, solid core, metal, metal skin, etc.
It would be in the Philadelphia City Code that is available online if it is in there at all. Scott Gilligan 215-888-4943 Infraspection Institute Level III Certified Thermographer Philadelphia Mold Inspections Philadelphia Home Inspections Philadelphia Commercial Inspections Philadelphia Licensed Home Inspector Pennsylvania - New Jersey - Delaware Infrared Thermal Imaging Inspections President The Greater Philadelphia Chapter of InterNACHI http://pa.nachi.org/greaterphiladelphia Vice President & Webmaster National Association of Commercial Building Inspectors and Thermographers |
|
#5
|
|||
|
|||
|
Please Note:
Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
It depends if the corridor walls are fire-resistance rated or not. The code won't tell you that. Plans on file in the building department might. If the wall has a one-hour rating, the door needs to be a "C" Label door. If it's a 2-hour rated wall, the door needs to be "B" Label. If the wall is unrated, the door, of course, would not require a label.
Normally, corridor walls are designed top have a fire-resistance rating. What rating they have depends on a bunch of factors. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| What is your HVAC procedure? | sstowe | Inspecting HVAC Systems | 66 | 5/28/09 12:48 PM |
| condo for sale Delray Beach FL | rwind | Inspection Classifieds | 0 | 1/13/09 12:40 PM |
| 980 Questions/Answers to the NHIE....Free! | jbushart | Legislation, Licensing & Legal Issues for Inspectors | 50 | 4/20/08 1:26 AM |