Default Crack in a fire box...pic included

What is the write up for a crack like this ?
Is it serious ? David

Reply With Quote
Find an InterNACHI certified Michigan Home Inspector (and anywhere else in North America)
  #2  
Old 7/16/09, 9:33 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Crack in a fire box...pic included

There are one or more cracks in the manufactured fireplace firebrick. Replacement or an evaluation by a fireplace specialist is recommended.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 7/16/09, 10:39 AM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Re: Crack in a fire box...pic included

thanks for the reply
Reply With Quote
  #4  
Old 7/16/09, 10:43 AM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Crack in a fire box...pic included

1.Our home inspectors do not inspect the internal components of a fireplace and/or their chimney, because it is impossible for a home inspection to determine with any degree of certainty whether the flue is free of defects. In accordance with recommendations made by the National Fire Prevention Association to have all chimneys inspected before buying a home, you should consider contacting our office for a Certified Chimney Specialist to conduct a Level II inspection of the chimney flue prior to close of escrow.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #5  
Old 7/16/09, 12:14 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Crack in a fire box...pic included

Assuming that really is a manufactured fireplace with 'artificial brick' then:
Quote:
A ceramic fiber brick liner or refractory brick panels are missing or damaged in the firebox. While not necessary for safe operation of the fireplace they are recommended to improve heat distribution and to protect and prolong the life of the metal firebox. Repair or replace as needed.



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
  #6  
Old 7/17/09, 8:38 AM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,489
Send a message via Yahoo to bboerner
Default Re: Crack in a fire box...pic included

Quote:
Originally Posted by mnahrgang View Post
1.Our home inspectors do not inspect the internal components of a fireplace and/or their chimney, because it is impossible for a home inspection to determine with any degree of certainty whether the flue is free of defects. In accordance with recommendations made by the National Fire Prevention Association to have all chimneys inspected before buying a home, you should consider contacting our office for a Certified Chimney Specialist to conduct a Level II inspection of the chimney flue prior to close of escrow.
Mark this statement in my opinion could mislead one to believe you didn't inspect the fireplace at all. Are you saying you don't look at the visible area inside the fireplace?



Bill Boerner
STL Home Inspection Services LLC
Serving St. Louis/Surrounding
(314) 805-2137
office@stlhomeinspector.com
http://www.stlhomeinspector.com
Residential, Commercial, Radon, Termite, Lateral Sewer Scopes
Reply With Quote
  #7  
Old 7/17/09, 5:53 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Crack in a fire box...pic included

I do not. This is where the SOP and I differ. I promote a Level II inspection and offer it as an ancillary service. To do even to what the SOP states, could lead the client to believe that the fireplace and chimney have been inspected thoroughly and are safe to use. I always explain that on the phone before booking, and I always tell them to get a level II before using it.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #8  
Old 7/17/09, 9:56 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Crack in a fire box...pic included

Quote:
Originally Posted by mnahrgang View Post
I do not. This is where the SOP and I differ. I promote a Level II inspection and offer it as an ancillary service. To do even to what the SOP states, could lead the client to believe that the fireplace and chimney have been inspected thoroughly and are safe to use. I always explain that on the phone before booking, and I always tell them to get a level II before using it.
With all due respect Mark, that's a little shady in my view. What if a HI chose not to inspect the HVAC system at all and insisted that the client hire the HI's sister HVAC company for that service?

This organization's Code of Ethics states: "The InterNACHI member shall abide by the Code of Ethics and substantially follow the InterNACHI Standards of Practice." I don't think there is an allowance for "differing" with it.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 7/17/09, 10:26 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Crack in a fire box...pic included

Quote:
Originally Posted by jfunderburk View Post
With all due respect Mark, that's a little shady in my view. What if a HI chose not to inspect the HVAC system at all and insisted that the client hire the HI's sister HVAC company for that service?

This organization's Code of Ethics states: "The InterNACHI member shall abide by the Code of Ethics and substantially follow the InterNACHI Standards of Practice." I don't think there is an allowance for "differing" with it.
That's fine, I respect your opinion. And if that is a violation of the COE and the ethics committee choses to remove me from membership, then so be it.

My opinion is that what the SOP states should be done, is completely inadequate, and puts my clients at risk. I find it morally unconscionable to allow anyone to think that their fireplace is safe without a Level II. Since, I am not qualified to do a Level II myself that leaves one option.

As to the COE, I do "substantially" follow them. I just don't inspect fireplaces or their chimneys, and unless you have been trained to do a Level II, I suggest you don't either.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #10  
Old 7/18/09, 12:36 AM
Troy Farmer's Avatar
Troy Farmer Troy Farmer is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Eagle, ID
Posts: 619
Default Re: Crack in a fire box...pic included

Agree


Quote:
Originally Posted by mnahrgang View Post
That's fine, I respect your opinion. And if that is a violation of the COE and the ethics committee choses to remove me from membership, then so be it.

My opinion is that what the SOP states should be done, is completely inadequate, and puts my clients at risk. I find it morally unconscionable to allow anyone to think that their fireplace is safe without a Level II. Since, I am not qualified to do a Level II myself that leaves one option.

As to the COE, I do "substantially" follow them. I just don't inspect fireplaces or their chimneys, and unless you have been trained to do a Level II, I suggest you don't either.



Troy Farmer
Presidential Inspections LLC
Chapter President Southern Idaho
PO Box 2144
Eagle, Idaho 83616
208-573-5300
http://www.presidentialinspection.com
http://info@presidentialinspection.com


"He who can, does. He who can’t, teaches"
"Where would we be without Teachers"
Reply With Quote
  #11  
Old 7/18/09, 11:06 AM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,846
Default Re: Crack in a fire box...pic included

I also recommend a Level II inspection on fireplaces and chimneys but that does not or should not preclude the HI from doing a Level I inspection. That would not only validate the recommendation for the Level II (means the HI actually looked at the fireplace) instead of just pushing the basic responsibility onto another professional but let the customer know the inspector did follow the basic SOP requirement.

The NFPA gives the procedures for a Level I as:

Generally limited to readily accessible (sound familiar) areas of the chimney structure, with additional requirements to insure the flue is clear. Readily accessible areas are those areas that can be reached for inspection or maintenance without the use of tools or ladders. A Level I inspection will include checking the basic appliance installation and connection, checking readily accessible portions of the chimney structure and flue, and determining that the flue is not obstructed.

A Level I Inspection is the recommended level of inspection:

During annual chimney inspections

During routine service of the venting system, including chimney sweeping

Upon direct replacement of the connected appliance with one of similar type

At any other time an inspection is warranted, and conditions of use of the venting system are not changing (like during a home inspection)

It does not take but at few minutes to explain to the customer the scope of the Level I and II, but also allows the inspector to stress the importance of them following through on getting the Level II. I tell mine I am not qualified to perform the Level II but they should insist on having the chimney cleaned (which is part of the Level II) and inspected by a certified CSIA contractor.



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill








Last edited by dedwards; 7/18/09 at 11:12 AM..
Reply With Quote
  #12  
Old 7/18/09, 11:17 AM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,489
Send a message via Yahoo to bboerner
Default Re: Crack in a fire box...pic included

Quote:
Originally Posted by dedwards View Post
I also recommend a Level II inspection on fireplaces and chimneys but that does not or should not preclude the HI from doing a Level I inspection. That would not only validate the recommendation for the Level II (means the HI actually looked at the fireplace) instead of just pushing the basic responsibility onto another professional but let the customer know the inspector did follow the basic SOP requirement.

The NFPA gives the procedures for a Level I as:

Generally limited to readily accessible (sound familiar) areas of the chimney structure, with additional requirements to insure the flue is clear. Readily accessible areas are those areas that can be reached for inspection or maintenance without the use of tools or ladders. A Level I inspection will include checking the basic appliance installation and connection, checking readily accessible portions of the chimney structure and flue, and determining that the flue is not obstructed.

A Level I Inspection is the recommended level of inspection:

During annual chimney inspections

During routine service of the venting system, including chimney sweeping

Upon direct replacement of the connected appliance with one of similar type

At any other time an inspection is warranted, and conditions of use of the venting system are not changing (like during a home inspection)

It does not take but at few minutes to explain to the customer the scope of the Level I and II, but also allows the inspector to stress the importance of them following through on getting the Level II. I tell mine I am not qualified to perform the Level II but they should insist on having the chimney cleaned (which is part of the Level II) and inspected by a certified CSIA contractor.
Agreed 100%.



Bill Boerner
STL Home Inspection Services LLC
Serving St. Louis/Surrounding
(314) 805-2137
office@stlhomeinspector.com
http://www.stlhomeinspector.com
Residential, Commercial, Radon, Termite, Lateral Sewer Scopes
Reply With Quote
  #13  
Old 7/18/09, 12:14 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Crack in a fire box...pic included

Quote:
Originally Posted by bboerner View Post
Agreed 100%.
We'll have to disagree. A level I gives that false an impression .... A client could still light up (thinking "we got it inspected"), and have a major problem in the flue.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
Find an InterNACHI certified Michigan Home Inspector (and anywhere else in North America)
  #14  
Old 7/18/09, 12:29 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Crack in a fire box...pic included

Quote:
Originally Posted by jfunderburk View Post
With all due respect Mark, that's a little shady in my view. What if a HI chose not to inspect the HVAC system at all and insisted that the client hire the HI's sister HVAC company for that service?

This organization's Code of Ethics states: "The InterNACHI member shall abide by the Code of Ethics and substantially follow the InterNACHI Standards of Practice." I don't think there is an allowance for "differing" with it.
I don't see how it's differing since there is language for excluding systems..

Quote:
1.1. A Home Inspection is a non-invasive, visual examination of a residential dwelling, performed for a fee, which is designed to identify observed material defects within specific components of said dwelling. Components may include any combination of mechanical, structural, electrical, plumbing, or other essential systems or portions of the home, as identified and agreed to by the Client and Inspector, prior to the inspection process.
If someone called up for simply a structural inspection, you would NOT have to inspect the roof, HVAC, Plumbing, etc.
Reply With Quote
  #15  
Old 7/18/09, 12:49 PM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,489
Send a message via Yahoo to bboerner
Default Re: Crack in a fire box...pic included

Quote:
Originally Posted by mnahrgang View Post
We'll have to disagree. A level I gives that false an impression .... A client could still light up (thinking "we got it inspected"), and have a major problem in the flue.
That's their problem. I told them in my report they should get a level 2 and the reasons behind it along with doing my level 1 inspection. If they still want to light up the fireplace without taking my advice atleast I know after reading about them in the local paper I did my job. Sad to say however you can't hold everyone's hand.



Bill Boerner
STL Home Inspection Services LLC
Serving St. Louis/Surrounding
(314) 805-2137
office@stlhomeinspector.com
http://www.stlhomeinspector.com
Residential, Commercial, Radon, Termite, Lateral Sewer Scopes
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM