Default Electric heater in garage

Does a electric heater installed in a garage need to be installed 18 inches of the floor? The one in the photo is 15 inches off the floor.

Thank you, for your input.
Attached Thumbnails
electric-heater-garage-101_4203.jpg  
Reply With Quote
Find an InterNACHI certified Oregon Home Inspector (and anywhere else in North America)
  #2  
Old 3/24/09, 9:25 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 11,037
Default Re: Electric heater in garage

Buck,
Not sure about the heater, but don't think I would be concerned with it. But I am curious if that outlet above the hose reel and the heater are GFCI protected?
Jeff
Reply With Quote
  #3  
Old 3/24/09, 9:49 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,531
Default Re: Electric heater in garage

Yes, they were protected.
Reply With Quote
  #4  
Old 3/24/09, 10:47 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,707
Send a message via Yahoo to jfunderburk
Default Re: Electric heater in garage

As far as I know, the code about ignition sources is specific to gas appliances.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 3/25/09, 12:36 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Electric heater in garage

Quote:
Originally Posted by jfunderburk View Post
As far as I know, the code about ignition sources is specific to gas appliances.
The UBC addresses electric appliances as well.

Devices generating a glow, spark or flame capable of igniting flammable vapors shall be installed such that sources of ignition are at least 18 inches (457 mm) above the floor of any room in which Class I flammable liquids or flammable gases are used or stored.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electric Water Heater in Garage bglickman Plumbing Inspections 10 4/10/08 9:25 PM
Electrical Safety Media Center jtedesco1 Electrical Inspections 1 3/15/08 9:18 AM
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 72 3/12/08 12:19 AM


All times are GMT -4. The time now is 1:33 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts