Unhappy Floor Joist Insulation

I live in Alaska, Juneau specifically. I just had an energy audit and the was told that I needed to have my crawl space insulated. I have a crawl space with a vapor barrier on the dirt floor, and closeable vents for air circulation. I installed solid foam insulation on the interior walls and solid foam insulation on the rim joist.

The fellow that completed my inspection told me he could install the recommended insulation of the floor joists. The work has been completed, but I am wondering if it was completed correctly.

Fiberglass batting without a vapor retardant was placed between the floor joists. Nothing is holding it in place except the resistance of the fiberglass to the wooden joists.

I have read that the proper method of insulation of the floor joist is to use fiberglass with a vaper retardant layer that is installed against the flooring. The insulation is held in place with netting, something called lighting rods, or clear plastic polyethylene sheeting - 6 mil.

I have not yet paid the fellow that completed the installation. He is also the state certified energy inspector. I really need some guidance.

Thanks so much for any assistance you might provide. This just does not seem to me to be a correct installation.

Happy Holidays!
Reply With Quote
  #2  
Old 12/20/08, 2:24 AM
canderson canderson is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Orwell, VT
Posts: 73
Default Re: Floor Joist Insulation

Gail,
Was a building paper/vapor barrier installed on the bottom of the floor prior to the batting being placed? You are correct in saying that thier should be something holding the batting from falling. Also be sure to where a resperator/mask if you should venture in there. Without a picture or further details it is hard to determine.
Reply With Quote
  #3  
Old 12/20/08, 7:15 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Floor Joist Insulation

Gail,

A vapor retarder (against the living area side) is definitely the best way to go when installing insulation in your floor joist cavities. The retarder will prevent moisture build-up on the floor sheathing where cold air is divided from the warm air.

It's also best to have this insulation secured in place with chicken wire or some sort of single heavy gauge wire.

Never install polyethylene sheeting to hold the insulation in place. Poly is a vapor barrier (not a retarder) that will not allow condensation to leave the cavity and will cause a Mold build-up throughout the floor joist cavities.

In your type of climate, I also recommend closing your vents to the crawl space and simply condition it. Go HERE to see how I show all my HI clients how to insulate their crawl space.

Good Luck. I was stationed in Ft. Richardson Alaska and I love it out there. Especially the northern lights and the midnight sun.
Reply With Quote
  #4  
Old 12/20/08, 9:03 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Floor Joist Insulation

The "heated crawlspace" in David's link is, by far, my preference, too.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #5  
Old 12/21/08, 7:10 AM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Floor Joist Insulation

Mr. Valley, your instructions for a heated crawl space tell the homeowner everything except how to heat it. Without a source of heat, it cannot be considered a "conditioned" crawl space, and thus would be a code violation in most jurisdictions.
Reply With Quote
  #6  
Old 12/21/08, 7:20 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Floor Joist Insulation

Quote:
Originally Posted by Richard A. Hetzel View Post
Mr. Valley, your instructions for a heated crawl space tell the homeowner everything except how to heat it. Without a source of heat, it cannot be considered a "conditioned" crawl space, and thus would be a code violation in most jurisdictions.
Who's going to send expensive heat into a void that's not being utilized?

Conditioning in my situation is simply keeping the cold air from entering this cavity in the first place. The warm floor will conduct minimum heat into this area. A direct heat supply to this cavity is indeed an option, but not necessary. That's why I mention the pipe insulation.
Reply With Quote
  #7  
Old 12/21/08, 12:08 PM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Floor Joist Insulation

"Conditioning" according to the code is either (1) the crawl space is used as a supply plenum for heated cand cooled air supply, or (2) contimuously operated mechanical ventilation is provided at 1 CFM per 50 sq. ft. of crawl space floor area, or (3) the crawl space is supplied with conditioned air.

Any sealed crawl space which is not conditioned in one of those three ways is a code violation in jurisdictions which have adopted the International Construction Code.

So, to answer your question, those who wish for their crawl space to meet the code definition of a "conditioned" crawl space will supply conditioned air to it. The code defines "conditioned", not anyone else.
Reply With Quote
  #8  
Old 12/21/08, 1:48 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Floor Joist Insulation

Quote:
Originally Posted by Richard A. Hetzel View Post
"Conditioning" according to the code is either (1) the crawl space is used as a supply plenum for heated cand cooled air supply, or (2) contimuously operated mechanical ventilation is provided at 1 CFM per 50 sq. ft. of crawl space floor area, or (3) the crawl space is supplied with conditioned air.

Any sealed crawl space which is not conditioned in one of those three ways is a code violation in jurisdictions which have adopted the International Construction Code.

So, to answer your question, those who wish for their crawl space to meet the code definition of a "conditioned" crawl space will supply conditioned air to it. The code defines "conditioned", not anyone else.
Please find something to do....Conditioned or un-conditioned crawlspaces is not a code violation because it's not a living area. You either condition it or you don't.
Reply With Quote
  #9  
Old 12/21/08, 3:44 PM
gail smith gail smith is offline
New User
 
Join Date: Dec 2008
Posts: 2
Please Note: gail smith is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Floor Joist Insulation

I went back down in my crawl space and took these images for further reference. No vapor retardant against the warm floor was installed. I also had foil quilt insulation that install in the fall and remove in the spring against the metal vents, just to reduce cold air coming into the crawl space. It has been removed. The current temp is 27 degrees outside and 42 degrees in the crawl space. Obviously, the crawl space is unheated. I am concerned that the pipes might freeze.

This fellow does state certified energy evaluations as well as weatherization. Now he wants to be paid for this, prior to the installation of new windows in the back of my house.

I don't want to pay him for this work if it has not been done correctly. It does seem from the remarks so far that the work is not correct.

Please review photos.

Thanks all and Merry Christmas.

Gail Smith, Juneau, Alaska
Attached Thumbnails
floor-joist-insulation-img_3479.jpg   floor-joist-insulation-img_3488.jpg   floor-joist-insulation-img_3490.jpg   floor-joist-insulation-img_3491.jpg  
Reply With Quote
  #10  
Old 12/21/08, 4:02 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Floor Joist Insulation

Quote:
Originally Posted by gail smith View Post
I went back down in my crawl space and took these images for further reference. No vapor retardant against the warm floor was installed. I also had foil quilt insulation that install in the fall and remove in the spring against the metal vents, just to reduce cold air coming into the crawl space. It has been removed. The current temp is 27 degrees outside and 42 degrees in the crawl space. Obviously, the crawl space is unheated. I am concerned that the pipes might freeze.

This fellow does state certified energy evaluations as well as weatherization. Now he wants to be paid for this, prior to the installation of new windows in the back of my house.

I don't want to pay him for this work if it has not been done correctly. It does seem from the remarks so far that the work is not correct.

Please review photos.

Thanks all and Merry Christmas.

Gail Smith, Juneau, Alaska
Gail,

A vapor retarder is required on that installation. Here is a link from Owens Corning.

Also, the pipes should be insulated to prevent freezing and bursting.
Reply With Quote
  #11  
Old 12/22/08, 7:49 PM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Floor Joist Insulation

Quote:
Please find something to do....Conditioned or un-conditioned crawlspaces is not a code violation because it's not a living area. You either condition it or you don't.
Maybe you should find something specific to do, such as reading the code. Who says that, because it's not a living area, the code doesn't apply? Start with Section R408.2.
Reply With Quote
  #12  
Old 12/28/08, 8:44 PM
Jack L. Gilleland's Avatar
Jack L. Gilleland Jack L. Gilleland is offline
InterNACHI Member
 
Join Date: May 2007
Location: Clayton, OH
Posts: 1,173
Default Re: Floor Joist Insulation

Gail the work is substandard and should be corrected to prevent more damage. I would contact someone from the local office that has authority over this type of installation (different in a lot of states) and report the it. Did you have to pay for all the excess insulation laying in the crawl?



In the world view we are all important and our mere existence effects all life.

Jack Gilleland
Home Inspection Services Clayton
Commercial, Multifamily, and Residential
jgilleland1@att.net
Ohio_Commercial and_Home_Inspections
linkedIn
activerain
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"A Bridge Too Far" mcyr Exterior Inspections 7 12/18/08 5:38 PM
Options in selecting materials for basement construction wdevries Canadian Inspectors 2 8/4/08 1:30 PM
Vaulted Ceiling Insulation rcooke Canadian Inspectors 4 1/22/07 12:24 PM
New Old Insulation rcooke Canadian Inspectors 1 12/13/06 5:25 PM