Hi everyone,

I am remodeling a recently bought home. One of the upstairs rooms is a game room and I plan on putting a pool table (1000 lbs) in it.

The original floor joists were 2x6 16" OC - I glued and nailed another joist on to existing joist - so now it is 4x6 16" OC. If I would add another joist in between, that would make the joist system 2x6 8" OC. The joist span is 13'.

I want to know which one would be better to try.

How can I find out since there are no calculators I can find online that will allow me to get the appropriate spans as a function of sistered 4x6 joists or at a spacing of 8" OC?

The thing is the former owner added a second story, but did not reinforce the 2x6 ceiling (floor for the 2nd floor) joists. He simply laid 2x4's perpendicular to the "ceiling" joists 16" OC and used a single layer of tounge and grooved 3/4" floor boards. Upon inspection there are many places where the crossing 2x4 do not even tough the underlying joists.

The rest of information: Southern Pine grade #2; dead and live load of 10 and 40, respectively; deflection of L/360.

Maybe you could help me with an exact answer or tell me where should I look to calculate myself.

Thanks in advance!
Reply With Quote
  #2  
Old 11/17/07, 7:37 PM
jking2 jking2 is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Troy, MI
Posts: 183
Default Re: floor joists

Since this was originally a single story home, the joists may not be the only thing that was not sized adequately to support a second floor. All elements of the structure, from the foundation up should be evaluated. Since the first floor ceiling has apparently been removed for you to see the joist arrangement, could remodeling of the home include relocation of the game room to the first floor?

Jim King
Reply With Quote
  #3  
Old 11/17/07, 8:36 PM
bzimbelman bzimbelman is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Silver City, NM
Posts: 353
Default Re: floor joists

Quote:
Originally Posted by Kyra Bloom
Hi everyone,

I am remodeling a recently bought home. One of the upstairs rooms is a game room and I plan on putting a pool table (1000 lbs) in it.

The original floor joists were 2x6 16" OC - I glued and nailed another joist on to existing joist - so now it is 4x6 16" OC. If I would add another joist in between, that would make the joist system 2x6 8" OC. The joist span is 13'.

I want to know which one would be better to try.

How can I find out since there are no calculators I can find online that will allow me to get the appropriate spans as a function of sistered 4x6 joists or at a spacing of 8" OC?

The thing is the former owner added a second story, but did not reinforce the 2x6 ceiling (floor for the 2nd floor) joists. He simply laid 2x4's perpendicular to the "ceiling" joists 16" OC and used a single layer of tounge and grooved 3/4" floor boards. Upon inspection there are many places where the crossing 2x4 do not even tough the underlying joists.

The rest of information: Southern Pine grade #2; dead and live load of 10 and 40, respectively; deflection of L/360.

Maybe you could help me with an exact answer or tell me where should I look to calculate myself.

Thanks in advance!
Go to Western Wood Producers and register, they have two nice calculators which will answer your question.

-- bz
Reply With Quote
  #4  
Old 11/18/07, 9:34 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: floor joists

As James stated consult a qualified engineer familiar with your type structure and second floor additions to design any alterations to the existing walls/floors.

The monies spent here will save you in the long run.

You can't rely on just the span tables alone without knowing the design and integrity of the underlaying supporting materials. An engineer can figure this out for you.



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #5  
Old 11/18/07, 9:40 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,611
Default Re: floor joists

Quote:
Originally Posted by badair
As James stated consult a qualified engineer familiar with your type structure and second floor additions to design any alterations to the existing walls/floors.

The monies spent here will save you in the long run.

You can't rely on just the span tables alone without knowing the design and integrity of the underlaying supporting materials. An engineer can figure this out for you.
Exactly for me to give advice on work I can not see particularly for a none home inspector who I have no idea how much knowledge they have could cause me grief in the future .
I want them to use some one in their area who has the proper qualifications.
... Cookie



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #6  
Old 11/18/07, 9:49 AM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: floor joists

A pool table produces, not uniform load, but concentrated load, divided between at least four and possibly as many as eight legs. Much depends on exactly where these concentrated loads will exist. The answer to the question will not be found in any reference source. It should be sought from a qualified design professional who is aware of all conditions which would affect the solution.

The original joists were substandard for the span based on uniform load requirements. The doubled joists may or may not be sufficient for the uniform load required by code, and their ability to carry concentrated loads must be calculated based on absolutely complete information about the existing conditions and the exact location and number of legs of the pool table.
Reply With Quote
  #7  
Old 11/18/07, 10:24 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: floor joists

Quote:
Originally Posted by Richard A. Hetzel
A pool table produces, not uniform load, but concentrated load, divided between at least four and possibly as many as eight legs. Much depends on exactly where these concentrated loads will exist. The answer to the question will not be found in any reference source. It should be sought from a qualified design professional who is aware of all conditions which would affect the solution.

The original joists were substandard for the span based on uniform load requirements. The doubled joists may or may not be sufficient for the uniform load required by code, and their ability to carry concentrated loads must be calculated based on absolutely complete information about the existing conditions and the exact location and number of legs of the pool table.
Exactly; and maybe this post http://www.nachi.org/forum/f23/do-put-aquarium-22264/
Is worth reading again and the title may or could be changed to Where do I put this Pool Table?

Any sub floor framing that will be introduced to a concentrated load should be well analyzed by a structural engineer.

Any span tables will only give you typical distributed load and Code related values and nothing else that could impair the capacities of the system.

Marcel
</IMG></IMG>
Reply With Quote
  #8  
Old 11/18/07, 10:31 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: floor joists

Here is just one example where the structural members below could not support the weight above. Me thinks someone goofed the design or something was not included. This was during the construction process.




ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #9  
Old 11/18/07, 10:34 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: floor joists

Please go ahead and put it on the lowest floor to start with because, if you don't get the qualified help needed, that is most likely where it will end up anyway.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #10  
Old 11/18/07, 10:49 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: floor joists

1. Slate Pool Table= fun

2. Slate Pool Table= heavy

3. Slate Pool Table= basement

4. Slate Pool Table= on first floor framing/ undesigned, see item #3

Marcel
Reply With Quote
  #11  
Old 11/19/07, 1:16 AM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: floor joists

I once remodeled an attic into a 2nd floor living space. The attic had 2x6 floor joists with similar spans. It would have been a big pain in the behind to install deeper joists. The engineer's solution (suggested by the builder) was to sister a steel c-channel onto the floor joists. He specified a 4" deep c-channel, through bolted with 1/4" bolts, 16" on center. It took the bounce right out of the floor. I even jacked some of the sag out of the floor before installing the steel. Of course we had to verify that the foundation walls and footings, bearing walls, and headers were all capable of handling the additional loads. I only had to add one additional post in the basement to carry the extra weight. The engineering was definitely money well spent on that project!!!
Reply With Quote
  #12  
Old 11/19/07, 6:16 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: floor joists

"Click To Enlarge"
floor-joists-joist-span1.jpg
Reply With Quote
  #13  
Old 11/19/07, 7:04 AM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: floor joists

Sorry, but the answer to the original question is not found in that or any other joist table. That table does not take into account the concentrated loads that result from something like a pool table, nor does it include doubled joists, and how is one to know which "species group" of lumber one is dealing with? The original question requires specific calculations to answer, and the original questioner would do well to read Mr. Dickerson's post above for an example of what the proper answer was in his case, not that the same answer will be right in this case.

Last edited by Richard A. Hetzel; 11/23/07 at 10:16 AM..
Reply With Quote
  #14  
Old 11/19/07, 7:04 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: floor joists

Anyone who proceeds to modify a structure without consultation from a licensed and insured structural engineer is foolish and will be sorry.

I believe that I can state that no one on this web site (unless an SE shows up) is qualified to comment. If they do, they are opening themselves up to liability.

Hope this helps;



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #15  
Old 11/19/07, 8:08 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: floor joists

Will, this is an easy one.

The original question at hand does not meet the structural loadings per the IRC structural criteria as framed.

It is inadequate and a pool table that weighs 1000# is completely out of the question until a qualified Structural Engineer assesses the existing conditions as it is.
Pictures would help, but 2 x 6 framing for the span noted in the post is unheard of.

Recommendation for further review by a Structural Engineer is the foremost action needed here.

Marcel
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 1:10 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts