Is this just a cosmetic issue or something else (clearance to combustibles OK)?
Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
Last edited by kshepard; 10/2/08 at 1:40 AM.. |
|
#2
|
||||
|
||||
|
This does not appear to be an approved fire-stop and if it is and has been cut or altered (bent-to-hell) it no longer serves it's intended purpose.
I'd write it and let the flue experts dicker it out, and take responsibility. If that bracket is screwed to the flue it's wrong. Is that moisture staining I see behind it? Imagine that! ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good |
|
#3
|
||||
|
||||
|
Barry it's a vaulted ceiling and I wasn't sure whether the firestop had to be at the lower (ceiling) plane or whether it could be at the upper (roof sheathing) plane.
Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
|
#4
|
||||
|
||||
|
I'll say living space side based on your photo and be proven wrong by others.
This may not be the first time I was wrong. ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good Last edited by badair; 10/12/06 at 4:32 PM.. Reason: because i wanted to |
|
#5
|
|||
|
|||
|
fire stop should be in the living space and well sealed to keep any flame from entering the attic space
|
|
#6
|
||||
|
||||
|
Quote:
Inside, outside? No matter. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#7
|
|||
|
|||
|
Must be firestopped. Absolutely, wether inside or out.
David J. Moran DJM Home Inspections, LLC Clarkston, MI 48346 |
|
#8
|
|||
|
|||
|
please explain 'fire stopped'.
Peter Siposs Absolute Home Inspections Home, Mold, IAQ, Radon, & Lead Based Paint Liberty Lake, WA Serving Eastern WA & Northern ID Nachi# 05100181 peter@absolute-home-inspections.com |
|
#9
|
|||
|
|||
|
Is there an attic cavity above this or is the flue going outside from here??
|
|
#10
|
|||
|
|||
|
If the flue passes through each level of the home i.e. bsmt. floor structure, first floor ceiling to attic, should be fire stopped at each level. Best application is sheet metal. Should be a tight fit around the flue. The flue should be a double wall thickness (B-vent) which usually carries a 1" clearance from combustible materials. A single wall type flue (C-vent) usually carries a 6" minimum clearance from combustible materials. This installation will "slow down" the spread of fire to each level of the home. With the flue cavity opened to other levels, could be considered a "stack effect" if opened.
Regards Joe Nichols Master Inspector/Owner The HomeBiz Inspection Team Frederick County, MD |
|
#11
|
|||
|
|||
|
Peter, Sorry, the sheet metal "panning" would be considered the "fire stopping".
Joe |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Gas Furnace Flue | Skip Erwin | Inspecting HVAC Systems | 1 | 9/6/07 9:24 PM |
| Single wall furnace flue | sspradling | Inspecting HVAC Systems | 8 | 6/29/07 7:23 PM |
| Furnace flue termination clearances | jfunderburk | Inspecting HVAC Systems | 7 | 3/19/07 10:46 AM |
| Furnace flue how close to wood | abishop | Inspecting HVAC Systems | 13 | 5/30/06 2:15 AM |
| Oil Furnace Flue Clearance | jfunderburk | Inspecting HVAC Systems | 3 | 2/28/06 7:17 PM |