Two questions:
1. I know garage door springs require safety cables but do the single over the door torsion springs for garage doors require safety cables as well.

2. What is maximum height for the photo-electric devices. I called one out as too high. That one must have been at least 3' high. When checking these devices out, it was nice to have the real estate do her can-can dance.
Reply With Quote
  #2  
Old 4/10/07, 3:15 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,447
Default Re: Garage door

#1 Check with manufacturer--it depends on the age and type of equipment. Some of the older ones required safety cables--newer ones don't.

#2 4" to 8" -- varies with AHJ.

3' is a bit much, though...



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #3  
Old 4/10/07, 3:18 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,161
Send a message via MSN to bwiley
Default Re: Garage door

Usually the torsion bar acts as a retainer.

If your AHJ won't answer about the height, refer to the manufacturers instructions.



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #4  
Old 4/10/07, 7:10 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Garage door

http://www.dasma.com/safetygdopeners.asp

Quote:
The Six-Inch Rule. The photo eyes mentioned above should not be installed higher than six inches above the garage floor. If the eyes are installed higher, a person or pet could get under the beam and not be detected by the photo eyes.
Reply With Quote
  #5  
Old 4/10/07, 7:51 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,918
Default Re: Garage door

Brian;

Those were good safety tips that we can not advertize enough to protect the general HomeOwner and protect the little ones.

Good posts.

Marcel
Reply With Quote
  #6  
Old 4/11/07, 12:09 AM
sturetsky sturetsky is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 27
Default Re: Garage door

I agree with Blaine, the torsion bar in the "over the door" torsion springs will act as a retainer should the spring break.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Automatic garage door openers..what are concerns? lfreeze Structural Inspections 8 5/18/07 11:38 AM
Garage ceiling & door header Al Barb Interior Inspections 7 3/27/07 1:07 PM
Garage Door Safety...No Reverse...Advice Please gliebig Exterior Inspections 33 3/17/07 8:28 PM
Hollow core door off garage kblair1 Interior Inspections 22 12/3/06 7:39 PM


All times are GMT -4. The time now is 3:51 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts