These doors are in the garage wall. The open into the basement. They are solid core doors. The framing around the doors is not a fire rated assembly. How much would you say about them?
Mid America Property Inspections, Inc. Shawnee, KS 66217 www.mapii.com NACHI # 05110992 KHIRB # 0110-0008 KS-Radon Cert.# KS-MS-0035 KS-Termite Cert. # 18933 M0-Termite Cert. # N 5033 |
| Find an InterNACHI certified Ohio Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
How thick are the doors? 1.25 inches of wood is 1/2 hour burn time (if i remember right) Assuming they are closed if/when a fire starts.
|
|
#3
|
||||
|
||||
|
Yes, they are 1 1/2 thick. No self closers.
Mid America Property Inspections, Inc. Shawnee, KS 66217 www.mapii.com NACHI # 05110992 KHIRB # 0110-0008 KS-Radon Cert.# KS-MS-0035 KS-Termite Cert. # 18933 M0-Termite Cert. # N 5033 |
|
#4
|
||||
|
||||
|
The frame is as thick as the door Buck, I don't see a problem with it.
Regarding the 20 minute fire rated "door", there is no such thing. It is properly referred to as a 20 minute fire rated door "assembly" which would include the frame and associated hardware all of which would be included in the door "assembly" This comes from the NFPA 80 Standard which is the authority standard for testing of fire rated door assemblies. Having a label on the door leaf alone would not constitute a proper assembly. That being said, the IRC does specifically permit the solid wood and the steel solid core or honeycomb core doors of 1-3/8" thickness. And it also give you a choice. 1-3/8" door or a 20 minute rated door, which would have a label. LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Poly being applied to Basement walls | dvalley | Interior Inspections | 40 | 11/24/09 11:49 PM |
| Common wall of garage is Laundry room / firewall ? | dnasser | Interior Inspections | 14 | 6/27/09 12:57 AM |
| garage wall fire resistance rating | Joseph A. Leone | Structural Inspections | 9 | 3/2/08 11:00 AM |
| Fire rating | abolt | Structural Inspections | 13 | 9/21/07 9:45 PM |