Default Garage fire wall question

If a garage is fully covered in sheet rock and tapped (no leaks) and has a cover for the hatch into the above garage attic area does the wall separating the garage attic from the house attic area need to be sealed off too? The reason I'm asking is that I been in a couple of houses where the hatch to the garage attic was missing and the wall was not closed off. I wrote it up as a fire hazard stating the hatch must be covered or the wall separating the garage from the home must be closed off. Now I'm questioning myself because what if the hatch is removed and not put back. This leaves a direct fire path to the unsealed wall above the garage. My gut is telling me the wall separation is primary and the cover to the hatch is secondary. Is there a code I can reference.



John Scaparo
Innovative Home Inspection, LLC
Canton, Michigan 48187
734.664.5853

john@InnovativeHomeInspection.com


Michigan Licensed Residential Builder

2101201845

InterNACHI MI #09041012, AHIT Member
Plymouth Michigan Home Inspector
Canton Michigan Home Inspector



"Helping To Secure Your Home Investment"

Looking for link exchange partners.
If interested send me your link.

Reply With Quote
Need a home inspection in Connecticut? Check out InterNACHI's listing of Connecticut certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/16/10, 12:38 AM
Tom Leahy Tom Leahy is offline
InterNACHI Member
 
Join Date: Dec 2009
Location: Arlington, Texas
Posts: 358
Default Re: Garage fire wall question

Here's a recent thread that should help ya. http://www.nachi.org/forum/f2/fire-w...explain-53644/



Fort Worth Home Inspector
Dallas Home Inspector
Reply With Quote
  #3  
Old 9/16/10, 8:28 AM
Andrew MacDonald's Avatar
Andrew MacDonald Andrew MacDonald is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Elgin, IL
Posts: 242
Default Re: Garage fire wall question

John,
Don't forget about the wood trim pieces that usually hold the drywall hatch in place. The wood trim is not fire rated and that would be the first thing to burn and allow the drywall hatch to drop out of the ceiling.



Andrew MacDonald
MacDonaldPropertyInspections.com
InsightThermalDiagnostics.com

ITC/FLIR Certified Building Science Thermographer
ITC/FLIR Certified Level 1 Thermographer


Reply With Quote
  #4  
Old 9/16/10, 10:05 AM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Garage fire wall question

Quote:
Originally Posted by amacdonald View Post
John,
Don't forget about the wood trim pieces that usually hold the drywall hatch in place. The wood trim is not fire rated and that would be the first thing to burn and allow the drywall hatch to drop out of the ceiling.
You know something Andrew--I'd bet very few of us had given that a thought--but we will now.

Down the road a life or two may be saved because of your post.

Thank you.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #5  
Old 9/16/10, 10:30 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Garage fire wall question

The access cover should be a rated assembly. It should be self-closing (in CA) and provide and effective seal when shut, just like the entry door to the house.

A drywall cover with wood trim is not a proper access through a garage firewall system.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 9/16/10, 2:15 PM
John Scaparo John Scaparo is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Canton, MI
Posts: 309
Default Re: Garage fire wall question

Andrew, missing fire proof hatch trim or wood trim is a fire hazard. I did not give that much thought. I will be from this point on. Now that I think about it all those pull down stairs that are not fire rated either. I wonder how many others have missed this too. Thanks guys for sharing your experience on this.



John Scaparo
Innovative Home Inspection, LLC
Canton, Michigan 48187
734.664.5853

john@InnovativeHomeInspection.com


Michigan Licensed Residential Builder

2101201845

InterNACHI MI #09041012, AHIT Member
Plymouth Michigan Home Inspector
Canton Michigan Home Inspector



"Helping To Secure Your Home Investment"

Looking for link exchange partners.
If interested send me your link.

Reply With Quote
  #7  
Old 9/16/10, 2:21 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Garage fire wall question

The builder is saying the gap at the drywall/sill plate meets separation requirements.
Attached Thumbnails
garage-fire-wall-question-hpim7228.jpg   garage-fire-wall-question-hpim7229.jpg  



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #8  
Old 9/17/10, 12:39 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: Garage fire wall question

http://www.nachi.org/attached-garage-fire-hazards.htm



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #9  
Old 9/17/10, 9:19 AM
John Scaparo John Scaparo is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Canton, MI
Posts: 309
Default Re: Garage fire wall question

Thanks Nick, that was the information I was looking for. Good learning from all. I will be looking at the attic hatch more closely.



John Scaparo
Innovative Home Inspection, LLC
Canton, Michigan 48187
734.664.5853

john@InnovativeHomeInspection.com


Michigan Licensed Residential Builder

2101201845

InterNACHI MI #09041012, AHIT Member
Plymouth Michigan Home Inspector
Canton Michigan Home Inspector



"Helping To Secure Your Home Investment"

Looking for link exchange partners.
If interested send me your link.

Reply With Quote
  #10  
Old 9/17/10, 9:43 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Garage fire wall question

Quote:
Originally Posted by ccurrins View Post
The builder is saying the gap at the drywall/sill plate meets separation requirements.

I appears to be a solid wood sill plate which would, IMO, be adequate...more so than a 1 3/8" solid wood door which is acceptable.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #11  
Old 10/3/10, 1:05 AM
dhuxted's Avatar
dhuxted dhuxted is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Orangeville, On.
Posts: 66
Default Re: Garage fire wall question

Here is part of what we have in Ontario, I was pretty sure that it had to have a gas seal.
3.1.8. Fire Separations and Closures
3.1.8.1. General Requirements
(1) Any wall, partition or floor assembly required to be a fire separation shall,
(a) except as permitted by Sentence (2), be constructed as a continuous element, and
(b) as required in this Part, have a fire-resistance rating as specified.
(2) Openings in a fire separation shall be protected with closures, shafts or other means in conformance with Articles 3.1.8.4. to 3.1.8.18. and Subsections 3.1.9. and 3.2.8.
3.1.8.2. Combustible Construction Support
(1) Combustible construction that abuts on or is supported by a noncombustible fire separation shall be constructed so that its collapse under fire conditions will not cause the collapse of the fire separation.
3.1.8.3. Continuity of Fire Separations
(1) Except as permitted by Sentence 3.6.4.2.(2), a horizontal service space or other concealed space located above a required vertical fire separation, including the walls of a vertical shaft, shall be divided at the fire separation by an equivalent fire separation within the service space.
(2) The fire separation required by Sentence (1) shall terminate so that smoke-tight joints are provided where it abuts on or intersects,
(a) a floor,
(b) a roof slab, or
(c) a roof deck.
(3) Except as required by Subsection 3.6.3. for a shaft penetrating a roof assembly, a shaft, including an exit enclosure, that penetrates a fire separation, shall,
(a) extend through any horizontal service space or any other concealed space, and
(b) terminate so that smoke-tight joints are provided where the shaft abuts on or intersects,
(i) a floor,
(ii) a roof slab, or
(iii) a roof deck.
(4) The continuity of a fire separation shall be maintained where it abuts another fire separation, a floor, a ceiling, or an exterior wall assembly.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Garage concrete slab question jjonas Structural Inspections 9 8/31/10 3:18 PM
Attached Garage Fire Containment. Please proof this new inspection article. gromicko General Inspection Discussion 38 8/12/09 6:55 PM
Garage fire protection question bwooddell Structural Inspections 10 6/23/07 6:52 PM
Fire wall between garage and attic ltreesh Structural Inspections 12 5/4/06 9:44 PM


All times are GMT -4. The time now is 5:04 AM.