Default Gas Fireplace

Inspected a home that had converted the wood fireplace to a natural gas. The venting is the original chimney with damper. Is this proper?
Also, the gas piping runs under two doors enroute to the fireplace?
Thanks, Phil
Attached Thumbnails
gas-fireplace-dscf0208.jpg   gas-fireplace-dscf0210.jpg   gas-fireplace-dscf0152.jpg  
Reply With Quote
Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/29/11, 9:01 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Gas Fireplace

The damper needs to be secured in at least a partial opened position.

Are there doors?

I would defer to the conversion log manufacturer's installation instruction in any case.

There is nothing proper about that installation.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 8/29/11, 9:09 PM
Philip F. Canter Philip F. Canter is offline
InterNACHI Member
 
Join Date: Apr 2010
Posts: 6
Default Re: Gas Fireplace

Michael.
The original glass doors are also still in place. The seller agent and homeowner are "resisting" that a pro needs to come in and futher evaluate this.
Reply With Quote
  #4  
Old 8/29/11, 9:23 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Gas Fireplace

Each gas log set will specify the minimum opening of the damper door.

It cannot be able to be closed completely as your picture shows.

Without the installation instructions all you can do is defer it as you have already done.

You need to put the responsibility onto the buyer or seller not yourself.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #5  
Old 8/29/11, 9:24 PM
Philip F. Canter Philip F. Canter is offline
InterNACHI Member
 
Join Date: Apr 2010
Posts: 6
Default Re: Gas Fireplace

Thanks!
Reply With Quote
  #6  
Old 8/29/11, 9:26 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Gas Fireplace

Quote:
ANSI Z21.60 requires the damper be fixed to maintain a minimum permanent net free opening of X amt. based upon the mfrs. specifications and the input BTU firing rate as stated in the code. How you achieve this is actually up to you. You can remove the damper entirely, tie the handle with wire, weld it (Mass) or use one of those clamps provided by the gas log mfr. The clamp must be located so when the damper is attempted to close, it still maintains that specified min. perm. net free opening. That means attaching it to the edge of most dampers is incorrect. I put them on the handle with the damper wide open.
ANSI also requires some sort of screen or doors. You could use mesh curtains, screen cabinet style doors or even glass doors.
All chimneys *should* have caps that minimize rain and animal intrusion and be stainless steel or copper. The codes don't require caps except on chimney liners and factory built fireplaces. I unplug a lot of heater flues that have a 5 foot plug of animal nesting in them.
The gas logset should have an attached rating plate identifying the mfr. model, serial #, input BTU rate, fuel, orifice, and operating instructions as well as a listing mark from an approved testing lab. If you don't find this info. I would recommend removal.
The fireplace and chimney should have a Level II inspection. They must be suitable for continued use burning wood in order to be acceptable for use with vented gas logs.
All the other requirements still apply such as approved gas shutoff and makeup air.
HTIN



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #7  
Old 8/29/11, 9:55 PM
Philip F. Canter Philip F. Canter is offline
InterNACHI Member
 
Join Date: Apr 2010
Posts: 6
Default Re: Gas Fireplace

Thanks. I will copy and paste this to my client. Do you have a comment about the rusty gas piping that runs under the door?
Reply With Quote
  #8  
Old 8/29/11, 10:00 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Gas Fireplace

I would not quote code myself and leave it at verification to the manufactures instructions.

If that is black iron pipe I would not have a comment.

It appears that it was once under a wood threshold that is now gone.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #9  
Old 8/29/11, 10:03 PM
Philip F. Canter Philip F. Canter is offline
InterNACHI Member
 
Join Date: Apr 2010
Posts: 6
Default Re: Gas Fireplace

Understand. Thanks again!!!!
Reply With Quote
  #10  
Old 8/31/11, 10:50 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: Gas Fireplace

If the fire place chimney has no galvanized or stainless flue liner installed after or during the retro fit of the gas fire place insert, the clay Tera-cota flue liners or double wythe walled brick degrade rapidly for the acidic exhaust.
The same goes for furnaces.
The low heat from efficient furnaces makes the chimney draw slower. Combined with the acidic exhaust, the effect will eat away the clay liners or clay brick quickly.
Expensive repair and it may also reduce the venting size.
A Bladder used to deflate after the concrete has dries is inserted into the flue of chimney cavity. Concrete is poured and a vibrator is used to insure there are no voids.
http://www.topstak.co.uk/pumice-conc...lue-liners.php
Not the best site but I am tired.
http://chimneycleaners.com/FAQs/6

SUSPECT: Chimney deficiency. Liner.Safety issue.
RECOMMEND. WETT inspection.http://www.wettinc.ca/what.html
Specialized licensed chimney insert installer.
( any other notes you made . Components that are missing or broken, damaged, bent.)
Good luck.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816

Last edited by ryoung7; 10/5/11 at 10:36 PM..
Reply With Quote
  #11  
Old 8/31/11, 11:04 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Gas Fireplace

WETT only applies top Canada



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #12  
Old 9/1/11, 12:35 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: Gas Fireplace

Thanks Michel.
I will try to remember.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #13  
Old 9/2/11, 11:22 AM
Philip F. Canter Philip F. Canter is offline
InterNACHI Member
 
Join Date: Apr 2010
Posts: 6
Default Re: Gas Fireplace

Thanks again, gentlemen!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Fireplace clean and scan dmacy Interior Inspections 4 11/21/10 8:16 PM
Hearth size??? jcampbell Inspecting HVAC Systems 32 6/1/08 1:56 PM
The Rumford Fireplace: Safety vs. Efficiency mbryan Interior Inspections 2 4/28/08 4:38 PM
Difficult Chimneys thance Inspecting HVAC Systems 2 1/29/08 8:16 PM


All times are GMT -4. The time now is 5:04 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts