Default Insulation clearance around non-IC-rated lighting fixtures

Is there an actual recommendation about insulation clearances around non-IC-rated recessed lighting fixtures, or should insulation just not touch them?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940

Last edited by kshepard; 10/2/08 at 2:40 AM..
Reply With Quote
  #2  
Old 11/2/06, 11:29 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Insulation clearance around non-IC-rated lighting fixtures

Kenton,

the minimum is a 3" clearance

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 11/2/06, 11:32 PM
rarmstrong1 rarmstrong1 is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Sandy Springs, GA
Posts: 33
Default Re: Insulation clearance around non-IC-rated lighting fixtures

Maintain 3 inches of clearance from insulation material. IRC 2003 N1102.11.2
Reply With Quote
  #4  
Old 11/3/06, 1:41 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,407
Send a message via ICQ to kshepard
Default Re: Insulation clearance around non-IC-rated lighting fixtures

Thanks guys




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #5  
Old 11/3/06, 12:10 PM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: Insulation clearance around non-IC-rated lighting fixtures

Quote:
Originally Posted by rarmstrong1
Maintain 3 inches of clearance from insulation material. IRC 2003 N1102.11.2
I have seen many manufactures state in their instructions to keep at least 6" or 8" of clearance, depending on the style of can light.



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #6  
Old 11/3/06, 6:04 PM
rdawes's Avatar
rdawes rdawes is offline
Active Poster
 
Join Date: Nov 2004
Location: Plano, TX
Posts: 427
Please Note: rdawes is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation clearance around non-IC-rated lighting fixtures

About half of the ones I see have a sticker that says 3" clearance minimum. I always take a picture of it for the report. Make the point quite well.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Question about exposed styrofoam insulation. mlong Exterior Inspections 9 12/21/07 9:33 AM
Light Bulbs- All Ya Wanna Know pabernathy Electrical Inspections 9 4/18/07 8:22 PM
Vaulted Ceiling Insulation rcooke Canadian Inspectors 3 1/22/07 11:24 AM
Wiring of residential lighting fixtures jtedesco1 Electrical Inspections 0 12/19/06 9:14 AM
New Old Insulation rcooke Canadian Inspectors 1 12/13/06 6:25 PM


All times are GMT -4. The time now is 7:35 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts