Default Insulation Questions?

A new condo with with 17" floor trusses between the first unit and the unit above. Can anyone tell me if 17" of loose fill fiber glass insulation will provide similar sound proof qualities as the same amount of fiber glass batts?

Is there a code that states how much insulation is required (zone 5 - Michigan) above the garage when the garage is located below a heated living area?

Thank you,

Kevin
Reply With Quote
  #2  
Old 2/2/08, 11:06 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation Questions?

Quote:
Originally Posted by kgoff
A new condo with with 17" floor trusses between the first unit and the unit above. Can anyone tell me if 17" of loose fill fiber glass insulation will provide similar sound proof qualities as the same amount of fiber glass batts?

Yes, if blown to proper density and not overfluffed to give depth but not the material.

Is there a code that states how much insulation is required (zone 5 - Michigan) above the garage when the garage is located below a heated living area?

Thank you,

Kevin
If you have 17" deep floor trusses full of insulation here also, the R50 should be more than enough to meet any code.
Reply With Quote
  #3  
Old 2/3/08, 12:26 AM
bjones1 bjones1 is offline
Active Poster
 
Join Date: Mar 2005
Location: Coe Hill, On
Posts: 364
Send a message via MSN to bjones1
Please Note: bjones1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation Questions?

For effective sound-proofing, insulation on it's own isn't enough. The ceiling joists between units should be strapped with resilient channel.

http://www.soundproofing.org/infopages/channel.htm

Last edited by bjones1; 2/3/08 at 12:29 AM..
Reply With Quote
  #4  
Old 2/3/08, 12:39 AM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation Questions?

Quote:
Originally Posted by bjones1
For effective sound-proofing, insulation on it's own isn't enough. The ceiling joists between units should be strapped with resilient channel.

http://www.soundproofing.org/infopages/channel.htm
And any holes that sound can travel through should be caulked/foamed (airsealed) since sound will follow the air if there are any direct airflow lines. Have to be careful to identify and stop "flanking sound" also.
Reply With Quote
  #5  
Old 2/3/08, 5:29 PM
Kevin R. Goff Kevin R. Goff is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Holt, MI
Posts: 94
Default Re: Insulation Questions?

Thank you for the feedback!

Kevin Goff
Reply With Quote
  #6  
Old 2/3/08, 5:47 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,353
Default Re: Insulation Questions?

I believe that STC ratings that you are interested in might be found here.
bJones is on the right track.




STC RATINGS FOR VARIOUS WALL ASSEMBLIES

Below are the STC ratings of various wall assemblies, each presented to help illustrate concepts, improvements and rules of thumb. The estimated ratings are based on laboratory test results from various compendiums of STC ratings. It is recommended to consult a professional acoustician for more detailed information or to analyze the specifics of your project/assembly.

To view different wall assemblies, click on each point below that may apply to your project.

1. Insulation will noticeably improve the STC rating of an assembly.
2. Staggered or double stud walls are higher rated than single stud walls.
3. Metal stud walls perform better than wood stud walls.
4. Resilient channel can improve the STC rating of an assembly.
5. Adding additional layers of drywall can improve the STC rating of an assembly.
6. Drywall between double studs can dramatically reduce the STC rating of an assembly.


1. Insulation will noticeably improve the STC rating of an assembly.
Description
Estimated STC Rating
Wall Assembly
3 5/8" metal studs, 5/8" gyp (2 layers total), No insulation
38 - 40

3 5/8" metal studs, 5/8" gyp (2 layers total), Batt insulation
43 - 44

back to top


2. Staggered or double stud walls are higher rated than single stud walls.
Description
Estimated STC Rating
Wall Assembly
2x4 stud, 5/8" gyp (2 layers total),
Batt insulation

34 - 39

Staggered studs, 5/8" gyp (2 layers total),
Batt insulation

46 - 47

2x4 studs, 5/8" gyp (2 layers total),
Batt insulation

56 - 59

back to top


3. Metal stud walls perform better than wood stud walls.
(NOTE: This only applies to single stud assemblies. For double stud assemblies, there is virtually no difference.)

Description
Estimated STC Rating
Wall Assembly
2x4 stud, 5/8" gyp (2 layers total), Batt insulation
34 - 39

3 5/8" metal studs, 5/8" gyp (2 layers total), Batt insulation
43 - 44

back to top


4. Resilient channel can improve the STC rating of an assembly.
(NOTE: These ratings are based on laboratory tests. Because of the special care required when installing resilient channels, actual results could be substantially lower.)

Description
Estimated STC Rating
Wall Assembly
2x4 stud, 5/8" gyp (2 layers total), Batt insulation
34 - 39

2x4 stud, 5/8" gyp (2 layers total), Resilient Channel, Batt insulation
45 - 52

back to top


5. Adding additional layers of drywall can improve the STC rating of an assembly.
Description
Estimated STC Rating
Wall Assembly
2x4 stud, 5/8" gyp (2 layers total), Batt insulation
34 - 39

3 5/8" metal studs, 5/8" gyp (3 layers total), Batt insulation
39 - 40

2x4 stud, 5/8" gyp (4 layers total), Batt insulation
43 - 45

back to top


6. Drywall between double studs can dramatically reduce the STC rating of an assembly.
Description
Estimated STC Rating
Wall Assembly
2x4 studs, 5/8" gyp (4 layers total), Batt insulation
44 - 45

2x4 studs, 5/8" gyp (2 layers total), Batt insulation
56 - 59

2x4 studs,5/8" gyp (3 layers total), Batt insulation
59 - 60

2x4 studs, 5/8" gyp (4 layers total), Batt insulation
58 - 63

back to top


Rules of Thumb
Recommended Ratings
Weaknesses - What You Should Know
The difference between STC and NRC
STC Ratings for Masonry Walls

Marcel





Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #7  
Old 2/3/08, 11:13 PM
bjones1 bjones1 is offline
Active Poster
 
Join Date: Mar 2005
Location: Coe Hill, On
Posts: 364
Send a message via MSN to bjones1
Please Note: bjones1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation Questions?

I've installed resilient channel on numerous occasions, going back 20 + years. In theory, with the channel, your drywall basically floats, away from the ceiling joists or wall studs. In a lot of the higher end homes, It's used on the walls separating the bathrooms. Guess they dont want to hear what's goin' on in there
Reply With Quote
  #8  
Old 2/4/08, 5:57 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,353
Default Re: Insulation Questions?

I always thought it was for the Master bedroom walls.

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #9  
Old 2/4/08, 6:48 PM
bjones1 bjones1 is offline
Active Poster
 
Join Date: Mar 2005
Location: Coe Hill, On
Posts: 364
Send a message via MSN to bjones1
Please Note: bjones1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Insulation Questions?

Quote:
Originally Posted by mcyr
I always thought it was for the Master bedroom walls.

Marcel
If they had Kids, they knew how to be wery wery quiet, so soundproofing wasn't needed there
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
IAC2 In new residential construction mcyr IAC2 Forum 0 10/9/07 7:45 PM
Vaulted Ceiling Insulation rcooke Canadian Inspectors 3 1/22/07 11:24 AM
New Old Insulation rcooke Canadian Inspectors 1 12/13/06 6:25 PM
Crawlspace Insulation gbrasseur Structural 12 12/3/06 4:18 PM


All times are GMT -4. The time now is 7:04 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts