InterNACHI


Go Back   InterNACHI Message Board > Specific Inspection Topics > Interior

Interior Contains discussions about the interior portion of a home inspection. This includes stairs, walls, floors, ceilings, smoke detectors, et cetera.

Reply
 
LinkBack Thread Tools Display Modes
  #1  
Old 9/15/08, 8:09 AM
David C. Mull's Avatar
David C. Mull David C. Mull is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Lititz, PA
Posts: 21
David C. Mull .
Default Kitchen gas stove venting

Must a natural gas stove in a kitchen be vented? To the exterior?
Reply With Quote
Find an InterNACHI certified West Virginia Home Inspector (and anywhere else in North America)
  #2  
Old 9/15/08, 8:21 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: GARLAND, TX
Posts: 2,962
Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute Barry Adair has a reputation beyond repute
Default Re: Kitchen gas stove venting

Yesterday's reply



badair
http://www.adairinspection.com
972-487-5634
Dallas & Garland, TX 75228 & 75042

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39
04080595

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #3  
Old 9/15/08, 8:22 AM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 2,873
James F. McKee is very trusted source of information James F. McKee is very trusted source of information James F. McKee is very trusted source of information James F. McKee is very trusted source of information James F. McKee is very trusted source of information James F. McKee is very trusted source of information James F. McKee is very trusted source of information James F. McKee is very trusted source of information James F. McKee is very trusted source of information James F. McKee is very trusted source of information James F. McKee is very trusted source of information
Default Re: Kitchen gas stove venting

Quote:
Originally Posted by dmull1 View Post
Must a natural gas stove in a kitchen be vented? To the exterior?


No...not necessary
Reply With Quote
  #4  
Old 9/15/08, 1:24 PM
Robert E. Elliott's Avatar
Robert E. Elliott Robert E. Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 5,572
Robert E. Elliott .
Default Re: Kitchen gas stove venting

Quote:
Originally Posted by jmckee View Post

No...not necessary
May not be required , but always a good idea.

Some people like greasy walls .
Reply With Quote
  #5  
Old 9/15/08, 3:54 PM
Mark Thorman Mark Thorman is offline
New User
 
Join Date: Mar 2008
Posts: 78
Mark Thorman is generally well trusted
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Kitchen gas stove venting

2000 IRC G2424.8
The following applainces shall not be required to be vented: 1. ranges
Where the applainces and equipment are installed so that the aggregate input rating exceeds 20 Btu per hour per cubic foot of volume of the room space in which the applaince is installed, one or more shall be provided with a venting system or other approved means for conveying the vent gases to the outdoor atmosphere. etc....

www.mauihomeinspection.com
Reply With Quote
  #6  
Old 9/15/08, 4:01 PM
Robert E. Elliott's Avatar
Robert E. Elliott Robert E. Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 5,572
Robert E. Elliott .
Default Re: Kitchen gas stove venting

Quote:
Originally Posted by Mark Thorman View Post
2000 IRC G2424.8
The following applainces shall not be required to be vented: 1. ranges
Where the applainces and equipment are installed so that the aggregate input rating exceeds 20 Btu per hour per cubic foot of volume of the room space in which the applaince is installed, one or more shall be provided with a venting system or other approved means for conveying the vent gases to the outdoor atmosphere. etc....

www.mauihomeinspection.com
I think we all agree on that Mark.

Now that it is out of the way, do you mention lack of a exterior routed vent?
I always refer to it verbally at the very least, and especially in a small galley kitchen.
Reply With Quote
  #7  
Old 9/15/08, 4:19 PM
Mark Thorman Mark Thorman is offline
New User
 
Join Date: Mar 2008
Posts: 78
Mark Thorman is generally well trusted
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Kitchen gas stove venting

Yes, in writting as a safety hazard.

www.mauihomeinspections.com
Reply With Quote
  #8  
Old 9/15/08, 5:15 PM
Brian K. Doles's Avatar
Brian K. Doles Brian K. Doles is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 2,611
Brian K. Doles has a reputation beyond repute Brian K. Doles has a reputation beyond repute Brian K. Doles has a reputation beyond repute Brian K. Doles has a reputation beyond repute Brian K. Doles has a reputation beyond repute Brian K. Doles has a reputation beyond repute Brian K. Doles has a reputation beyond repute Brian K. Doles has a reputation beyond repute Brian K. Doles has a reputation beyond repute Brian K. Doles has a reputation beyond repute Brian K. Doles has a reputation beyond repute
Default Re: Kitchen gas stove venting

Quote:
Originally Posted by dmull1 View Post
Must a natural gas stove in a kitchen be vented? To the exterior?
I had to research this today for a project on Wed. I always thought it was no, but found out the city (City of Covington, GA) requires it.

So results will vary from place to place.




Brian K Doles
Atlanta, GA - Providing Infrared Thermal Home Inspections
Home Inspections
Commercial Inspections
Infrared Thermal Imaging

Colby Home Services
All of metro Atlanta including Conyers, Covington, Stone Mountain, Midtown, Buckhead, Perimeter
Customer Testimonials


Home Inspector Pro Software - A Professionals choice in software.

Reply With Quote
  #9  
Old 10/11/08, 9:16 PM
Sean Corcoran Sean Corcoran is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: St. Catharines, Ontario
Posts: 105
Sean Corcoran is often very helpful Sean Corcoran is often very helpful
Default Re: Kitchen gas stove venting

Quote:
Originally Posted by Mark Thorman View Post
2000 IRC G2424.8
The following applainces shall not be required to be vented: 1. ranges
Where the applainces and equipment are installed so that the aggregate input rating exceeds 20 Btu per hour per cubic foot of volume of the room space in which the applaince is installed, one or more shall be provided with a venting system or other approved means for conveying the vent gases to the outdoor atmosphere. etc....

www.mauihomeinspection.com


So, If I'm reading this correct the answer is YES It does require it... but generally only in a very small kitchen? I personally have a gas range not vented outside. The hood I use has a charcoal filter that works quite well. My range is in a VERY large Kitchen where as the whole main floor is an open concept of 1200 square feet.
Reply With Quote
  #10  
Old 10/11/08, 9:52 PM
Brian A. MacNeish Brian A. MacNeish is online now
Active Poster
 
Join Date: Apr 2007
Posts: 2,124
Brian A. MacNeish is well trusted Brian A. MacNeish is well trusted Brian A. MacNeish is well trusted
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Kitchen gas stove venting

Quote:
Originally Posted by scorcoran View Post
So, If I'm reading this correct the answer is YES It does require it... but generally only in a very small kitchen? I personally have a gas range not vented outside. The hood I use has a charcoal filter that works quite well. My range is in a VERY large Kitchen where as the whole main floor is an open concept of 1200 square feet.
Do you replace the charcoal every 3 or 4 weeks?
Reply With Quote
  #11  
Old 10/11/08, 10:18 PM
Robert E. Elliott's Avatar
Robert E. Elliott Robert E. Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 5,572
Robert E. Elliott .
Default Re: Kitchen gas stove venting

Quote:
Originally Posted by Brian A. MacNeish View Post
Do you replace the charcoal every 3 or 4 weeks?
Hahaha
Have you checked prices on them?

Some come with a little dot that lets you know when to change.

It all depends on use.
Reply With Quote
  #12  
Old 10/11/08, 11:14 PM
Brian A. MacNeish Brian A. MacNeish is online now
Active Poster
 
Join Date: Apr 2007
Posts: 2,124
Brian A. MacNeish is well trusted Brian A. MacNeish is well trusted Brian A. MacNeish is well trusted
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Kitchen gas stove venting

[quote=relliott;423425]Hahaha
Have you checked prices on them?

Some come with a little dot that lets you know when to change.

It all depends on use.[/quote]

That's what I was getting at.......There's so little charcoal in those filters that 2-3 weeks (or less) of regular use will render its odour absorbtion capability used up.......time to replace again @ $15-$25.

The standard thin charcoal filter installed on recirculating range hoods is one of the biggest scams going on in air quality/filtration!!!
Reply With Quote
  #13  
Old 10/12/08, 2:25 AM
Sean Corcoran Sean Corcoran is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: St. Catharines, Ontario
Posts: 105
Sean Corcoran is often very helpful Sean Corcoran is often very helpful
Default Re: Kitchen gas stove venting

I guess really it depends on what you're cooking... We actually don't use the stove all that much so they tend to last signifigantly longer although I must say that I am a bit anal about changing it.

I would suggest though, that if someone told me it was a safety issue... I'd like to hear the explanation behind it...
Reply With Quote
Find an InterNACHI certified West Virginia Home Inspector (and anywhere else in North America)
  #14  
Old 10/12/08, 4:59 AM
Robert E. Elliott's Avatar
Robert E. Elliott Robert E. Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 5,572
Robert E. Elliott .
Default Re: Kitchen gas stove venting

In a small window less kitchen there is more of a chance of carbon monoxide effecting someone.

In general, like I said above , grease , and a charcoal will help kill odor.

The charcoal filter may not be anywhere as good as venting out, but it helps.

Think of all the oils coming out of your food misted on to the walls as it can get that way.

I do lots of Condos, and some of them have no way to be vented out.In a small place you do not want to go without some method of cutting down on the scum which can coat your walls.
Reply With Quote
  #15  
Old 10/12/08, 7:17 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 6,135
David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute
Default Re: Kitchen gas stove venting

Quote:
Originally Posted by scorcoran View Post
So, If I'm reading this correct the answer is YES It does require it... but generally only in a very small kitchen? I personally have a gas range not vented outside. The hood I use has a charcoal filter that works quite well. My range is in a VERY large Kitchen where as the whole main floor is an open concept of 1200 square feet.

Sean,

I write up all ranges that are missing a venting hood. It is not necessary to vent to the exterior. Interior self-ventilators are fine.