Default Nail pops at the base of vaulted ceiling-no roof leak

Two homes with the same condition- nail pops at the base of a vaulted ceiling. Both at 8000 ft. in CO. Both homes had kitchens open to the effected room. Both homes less than 10 yrs. old with good roofs. The last had Ice & Water Shield at the roof edges as insurance against damage from ice damming.
Pops were on the ceiling a few inches above the ceiling/wall junction. No stains. No other nail pops anywhere. The effected rooms each had a ceiling fan.

My theory- during the winter, air carrying moisture from the kitchen is pulled up the wall by air currents created by the ceiling fan. That part fo the roof may be low on insulation so that when moist air reaches it, condensation forms, raising moisture levels in the drywall mud enough to cause the nail pops.

Nail pops- I know that metal expands by a factor of about 17 as it turns to rust. Is this what pops loose the mud covering the nail?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940

Last edited by kshepard; 10/2/08 at 2:39 AM..
Reply With Quote
  #2  
Old 8/15/07, 8:49 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,836
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Nail pops at the base of vaulted ceiling-no roof leak

I think it just has to do with the low insulation levels at that point. Moisture already in the wood freezes and pushes the nail out.

Similar from what you described except the origin of the moisture and the rust.
Reply With Quote
  #3  
Old 8/15/07, 10:25 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Nail pops at the base of vaulted ceiling-no roof leak

I think its the differential temps in the roof joists, not moisture related per se. The wood expands and contracts, thus the nail pops. I believe this is why screws should be used.
Reply With Quote
  #4  
Old 8/15/07, 10:27 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Nail pops at the base of vaulted ceiling-no roof leak

Quote:
Originally Posted by phinsperger
I think it just has to do with the low insulation levels at that point. Moisture already in the wood freezes and pushes the nail out.

Similar from what you described except the origin of the moisture and the rust.
Typical cases nailpopping happen when drywall is applied to lumber with higher humidities, more likely to be above 19-20% moisture content with a fair amount of shrinkage to occur as the house dries. When the wood dries and shrinks, a small gap is left between the back of the drywall and the stud. When a bit of force is applied to the face of the drywall, the nail/screw head pops out the filler/paint.

I'm wondering: as these houses dried and shrank, the wall drywall panels pushed the cathedral drywall back up against the rafter/truss which caused the typical nailpop. On the rest of the upper slopes, the gap exists but the drywall is hanging on the nail/screw heads and has not been pushed up, hence no pops.
Reply With Quote
  #5  
Old 8/16/07, 12:37 AM
homebild homebild is offline
Active Poster
 
Join Date: Nov 2006
Location: Pennsylvania
Posts: 195
Please Note: homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Nail pops at the base of vaulted ceiling-no roof leak

The nail pops are lkely the result of structural deficiencies.

1st, you have perhaps 70psf or greater snow loading conditions.
2nd, you have cathedral and vaulted ceilings in place which appear to be under-engineered for the conditions.

Seems to me that what is occuring is that the ceiling rafters are over-stressed for loads and conditions and bending excessively under load.

As the bearing wall(s) push out from overloading, the nails 'pop' near their rafter connection to such walls.

Structural defect if you ask me.

Undersized rafters for the loads and spans.
No cross-lateral connections to prevent bearing walls from spreading under load.
Reply With Quote
  #6  
Old 8/16/07, 1:02 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Nail pops at the base of vaulted ceiling-no roof leak

Quote:
Originally Posted by homebild
The nail pops are lkely the result of structural deficiencies.

1st, you have perhaps 70psf or greater snow loading conditions.
2nd, you have cathedral and vaulted ceilings in place which appear to be under-engineered for the conditions.

Seems to me that what is occuring is that the ceiling rafters are over-stressed for loads and conditions and bending excessively under load.

As the bearing wall(s) push out from overloading, the nails 'pop' near their rafter connection to such walls.

Structural defect if you ask me.

Undersized rafters for the loads and spans.
No cross-lateral connections to prevent bearing walls from spreading under load.
Nailpops have never usually been connected with structural failure but just an aesthetic deficiency. Kenton mentions no cracks in drywall and none were visible in pictures......these I would expect if the place was moving.
Reply With Quote
  #7  
Old 8/16/07, 9:32 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Nail pops at the base of vaulted ceiling-no roof leak

Quote:
2nd, you have cathedral and vaulted ceilings in place which appear to be under-engineered for the conditions.
How do you know that? All from a picture and nail pops?
Reply With Quote
  #8  
Old 8/16/07, 9:38 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,944
Default Re: Nail pops at the base of vaulted ceiling-no roof leak

I expect the homes built at different times of the year.
More moisture in the wood led to more shrinking.
I would say screws on both sides of the nails repair and paint .
I would be surprised if there was any more nail pops.

.......... Cookie



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #9  
Old 8/16/07, 12:59 PM
klott's Avatar
klott klott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,709
Default Re: Nail pops at the base of vaulted ceiling-no roof leak

It could be the same forces that cause truss uplift. The rafters get longer in winter due to the cold moist air and because they are fastened at the birdmouth and the ridge beam, they bow up in the center.The drywall hanger puts up the ceiling first, the bottom edge of the ceiling drywall,where it meets the wall, hangs up and does not follow the upward movement of the rafter when it bows. When the rafter returns to its original shape and size in the summer, it retightens up on the nail, when the rafter comes back down it pops the mud off. I bet if you could get to the back side of the wallboard, you would see the rafter seperated from the top plate. It doesn't take much movement for this to happen.
Reply With Quote
  #10  
Old 8/16/07, 1:52 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Nail pops at the base of vaulted ceiling-no roof leak

My assessment is that the nails are too close to the ceiling/wall juncture.

The closest nails should be 7 to 8 inches away and double nailed. This creates a floating angle.

Cathedral ceilings move a lot. When the sheet rock is attached directly to the roof rafters this condition is accentuated. If the nails are further away from the juncture, there is room for the sheet rock to flex and there is a lesser chance of the nail to pop.
Reply With Quote
  #11  
Old 8/16/07, 2:02 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,944
Default Re: Nail pops at the base of vaulted ceiling-no roof leak

Quote:
Originally Posted by klott
It could be the same forces that cause truss uplift. The rafters get longer in winter due to the cold moist air and because they are fastened at the birdmouth and the ridge beam, they bow up in the center.The drywall hanger puts up the ceiling first, the bottom edge of the ceiling drywall,where it meets the wall, hangs up and does not follow the upward movement of the rafter when it bows. When the rafter returns to its original shape and size in the summer, it retightens up on the nail, when the rafter comes back down it pops the mud off. I bet if you could get to the back side of the wallboard, you would see the rafter seperated from the top plate. It doesn't take much movement for this to happen.
If a home has truss uplift an easy way to hide it is put trim around the exterior and only fasten it to the ceiling.
This allows the ceiling to move up or down as the season changes and you never see a crack as the trim also goes up and down.

. Cookie



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #12  
Old 8/16/07, 2:10 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Nail pops at the base of vaulted ceiling-no roof leak

Nail pops are a common occurance in all new construction and are basically a simple fix.

As many have already stated here, it's simply the high moisture content in the lumber. Framing lumber used in new construction often shrinks after it is installed. Kiln dried lumber often has a moisture content that ranges between 15 - 20 percent. The moisture content can drop to 10 percent after installation.

Also, if there's a lot of rainfall during the rough framing and the lumber is stored outside and not covered up, some builders typically do not wait for the framing to completely dry before the drywall is installed. Now you've got moisture laden framing that'll take longer for the drying process, causing nail pops as it dries.

Another common cause of nail pops is "operator error". The drywall installer fails to push the drywall firmly against the framing lumber as it is being fastened. This failure results in a small void space between the back of the drywall and the framing lumber. If someone or something pushes against the drywall, the drywall pushes back into the gap and the nail pushes right out to the surface.

If framing lumber is allowed to dry properly and drywall screws are utilized, nail pops will likely not occur.
Reply With Quote
  #13  
Old 8/16/07, 5:29 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,407
Send a message via ICQ to kshepard
Default Re: Nail pops at the base of vaulted ceiling-no roof leak

No sign of foundation movement. The homes were both new enough to have had modern engineering and look typical in rafter size.

Although it's real dry here, lumber (especially studs) gets unloaded from flat cars at the lumber yard soaking wet and wrapped in plastic. It's often taken to a jobsite right away where they pull off the plastic and use it to build with. Dry air... wet lumber... definitely some shrinkage there. This in addition to the typical settling due to gaps at framing connections.
Thermal expansion and contraction onlone could contribute too.

After the first year or two the lumber would probably have reached moisture equilibrium content with the environment and have finished shrinking, so damage is probably from the first year or two and shouldn't be ongoing.

So if the studs shrink, but drywall doesnt, wall drywall pushes up and closes any gap behind the ceiling drywall, popping nails. If there was no gap created by the guys doing the hanging, rafters might expand when they freeze, leaving behind a gap after they dry and shrink.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #14  
Old 8/16/07, 6:13 PM
homebild homebild is offline
Active Poster
 
Join Date: Nov 2006
Location: Pennsylvania
Posts: 195
Please Note: homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Nail pops at the base of vaulted ceiling-no roof leak

Quote:
Originally Posted by rwand1
How do you know that? All from a picture and nail pops?
1. Location. Colorado is generally a very high snow load region.
2. Presence of cathedral and vaulted ceilings.
3. Lack of any structural cross laterals to hold opposite bearing walls together and keep them from spreading

Basically what can happen under excessive load, and from undersized rafters and cathedral or vaulted ceilings that do not have any cross lateral bracing is a similar condition to 'truss lift' as another member already mentioned:

The center of the rafter moves down and the ends move up.

It is the ends moving up that can cause nail pops in the symptomatic manner described.

Also, nailpops are becoming much rarer in newer contruction as building codes allow fewer fasteners to be used when adhesive is used. Most contractors opt to use adhesive and fewer fasteners , except where requried, and these fasteners are required at the ends or edges of boards....right where these pops occur.

Personally, I would check for structural defects like undersized rafters for the spans first, and only then consider other causes once structural causes are ruled out....and unless you can have an engineer rule them out...you'd better consider structural causes.

It may be nothing and may be simply the use of wrong type fasteners, moisture in the lumber, or other less dramatic causes...

But structural reasons should not immediately be ruled out in this case and should be your first causation item to investigate.

JMHO
Reply With Quote
  #15  
Old 8/16/07, 9:18 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Nail pops at the base of vaulted ceiling-no roof leak

Was it ever verified that the installation was with screws or nails?

Just curious before I give my two cents. ha. ha.

Marcel
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior Inspections 6 10/13/07 9:10 AM
Ice Gaurd membrane dmacy Exterior Inspections 36 6/14/07 1:21 AM
Roof Repair? Maybe NO jhagarty Exterior Inspections 9 2/15/07 2:19 AM
Vaulted Ceiling Insulation rcooke Canadian Inspectors 3 1/22/07 11:24 AM
Common Defects List by Age of House trausch Inspection Education & Training 10 6/12/06 5:52 AM


All times are GMT -4. The time now is 6:32 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts