Default Opinion: Smoke Alarm Location

Interesting scenario today: Two co-workers hired me together to inspect two identical floor-plan homes that are almost next door to one another. The homes are both new construction, same builder/same super, finished at the same time. There were a number of differences in how some things were executed between the two homes. It's interesting to see how much drift there is from house to house

One of the differences involved the required smoke alarm outside the master bedroom. In the attached image the open arched doorway leads to a small alcove with a return air chase and thermostat and the doorway to the master bedroom. House #2 (not the one in the photo) had the smoke alarm that is required to be outside of the sleeping area located inside the alcove approximately at the point of the lower arrow (this location I know is OK); House #1 had the same smoke alarm located as you see in the photo at the top of the arrow (on the upper level ceiling).

I'm curious as to whether you believe this location to be correct/acceptable or improper and why in either case.

I am leaning toward improper because I'm thinking that placing outside the open passageway constitutes it not being "in the immediate vicinity" for the sleeping room, even though the location is technically on the first floor.

Please give me your thoughts. I'll hold out on finalizing the report comment until I've heard some opinions.

Thanks.
Attached Thumbnails
opinion-smoke-alarm-location-p1210048small.jpg  

Last edited by cevans; 6/16/09 at 12:02 AM..
Reply With Quote
Find an InterNACHI certified Nevada Home Inspector (and anywhere else in North America)
  #2  
Old 6/16/09, 12:06 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Opinion: Smoke Alarm Location

I would defiantly recommend them right in the bedrooms as the CPSC recommends in a case like this.
You want them 6 inches from the wall ceiling intersection and not near vents or dead air space.
Reply With Quote
  #3  
Old 6/16/09, 12:17 AM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 358
Default Re: Opinion: Smoke Alarm Location

That smoke alarm is not anywhere near the bedroom door. If it's required to be out side the bedroom I'd write it up as being wrong.
Reply With Quote
  #4  
Old 6/16/09, 12:21 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 2,694
Default Re: Opinion: Smoke Alarm Location

Quote:
Originally Posted by dokeefe View Post
That smoke alarm is not anywhere near the bedroom door. If it's required to be out side the bedroom I'd write it up as being wrong.
Agree. No need to over-analyze it. It's wrong, so report it as such.



"You cannot depend on your eyes when your imagination is out of focus"...Mark Twain


Jeffrey R. Jonas
Critical Eye Property Inspections
JRJ Consultants
Owatonna, Minnesota

NACHI07013103
IAC2-01-1567


Reply With Quote
  #5  
Old 6/16/09, 12:47 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 658
Default Re: Opinion: Smoke Alarm Location

Quote:
Originally Posted by relliott View Post
I would defiantly recommend them right in the bedrooms as the CPSC recommends in a case like this.
You want them 6 inches from the wall ceiling intersection and not near vents or dead air space.
I should have elaborated: There are smoke alarms inside of each sleeping room. The alarm in question is the one that is required to be located outside of each separate sleeping area.

Edit: Just found the location requirement in NFPA 72 11.5.1.1: "Outside of each separate dwelling unit sleeping area within 6.4M (21 feet) of any door to a sleeping room, the distance measured along a path of travel."

Another pertinent section: 11.5.3.1.2: "Where dwelling units include great rooms or vaulted/cathedral ceilings extending over multiple floors, smoke alarms that are located on the upper floor that are intended to protect the aforementioned area shall be permitted to be considered as part of the lower floor(s) protection scheme to meet the requirements of 11.5.1.3.1


Based on this, it appears that the location on the upper ceiling is OK


BTW: smoke alarms should be located so that the closest edge is not less than 4 inches from the wall ceiling juncture, wall mounted units should have the top edge also not more than 12 inches below the wall ceiling juncture.

Last edited by cevans; 6/16/09 at 1:02 AM..
Reply With Quote
  #6  
Old 6/16/09, 1:11 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Libertyville, Il
Posts: 444
Default Re: Opinion: Smoke Alarm Location

Your smoke is fine. It satisfies being within 21 ft of the door and it looks to be within 36 inches of the peak but not closer than 4.

Jeff



Jeff Wicklander
Corwick Home Services
224-715-0457
Reply With Quote
  #7  
Old 6/16/09, 1:12 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Libertyville, Il
Posts: 444
Default Re: Opinion: Smoke Alarm Location

Nevermind.......I waited too long to type. You edited in the correcxt info.

Jeff



Jeff Wicklander
Corwick Home Services
224-715-0457
Reply With Quote
  #8  
Old 6/16/09, 1:28 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Opinion: Smoke Alarm Location

Some code depends on location.
In Illinois it is with in 15 feet of bedrooms for both smoke and carbon monoxide detectors since Jan 1st of 2006.

That is if living space is considered in danger of Co2.

Central Boilers do not count in multi units.
Reply With Quote
  #9  
Old 6/16/09, 9:31 AM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 358
Default Re: Opinion: Smoke Alarm Location

So, it's OK. But I would not want to rely on that smoke detector to wake me up in the middle of the night!
Reply With Quote
  #10  
Old 6/16/09, 9:34 AM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 358
Default Re: Opinion: Smoke Alarm Location

Are the smoke detectors in that house interconnected, so if one alarm sounds they all activate? This would be OK because of the alarm in each bedroom.
Reply With Quote
  #11  
Old 6/16/09, 7:31 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 658
Default Re: Opinion: Smoke Alarm Location

Yes all alarms are interconnected for smoke and CO alerts. It would be quite a challenge for a hearing person to sleep through these.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
smoke alarms and return vents rwashington Interior 17 6/6/09 4:43 PM
Smoke Detector placement jwicklander Electrical 0 9/17/08 7:43 PM
Escape, Fire & Smoke Alarms badair Interior 14 1/28/08 8:21 AM
2 questions staylor5 Electrical 9 3/23/07 11:40 PM


All times are GMT -4. The time now is 3:03 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts