New construction contractor wanted to argue the fire wall between garage and living space
Said OSB is fire rated? anyone been there before? |
|
#2
|
||||
|
||||
|
Regular OSB is class C and no good for exposed walls as a fire wall.
Fire rated OSB is available but very expensive. I have not seen any of it. I doubt it is there, it would cost more than the regular OSB and sheetrock. |
|
#3
|
||||
|
||||
|
|
|
#4
|
||||
|
||||
|
Please Note:
wforsyth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Wouldn't the contractor be able to show the receipts from the OSB showing that it was fire-rated?
Thanks Marcel for the OSB Guide. |
|
#5
|
||||
|
||||
|
Quote:
Wendy, If he had purchased fire rated OSB he would have had the reciept in his pocket.... Any builder that purchases that will definitely know that he will need to prove its rating later. Any site that has sheetrock workers present will not need to purchase fire rated OSB. added with edit: Having trouble with the pdf documents from Marcel's post.. It looks like the chart that compares sheetrock with osb refers to the sheetrock as type X or higher and appears to show that OSB is the same rating.. Anyone get these to load without aborting? Last edited by bking; 6/4/06 at 3:54 PM.. |
|
#6
|
|||
|
|||
|
I had the same problem with aborting so I quick printed the OSB FIRE PERFORMANCE before it aborted.
Anyway a 16" oc stud wall with mineral wool insulation and 19/32", 5/8" OSB both sides has a 14 minute rating. Not much. |
|
#7
|
||||
|
||||
|
|
|
#8
|
||||
|
||||
|
David, what is your opinion on 7/16 regular OSB?
Equivalent to Type X sheetrock or not? |
|
#9
|
||||
|
||||
|
Quote:
I'm just posting a site that references OSB as an approved firewall. |
|
#10
|
||||
|
||||
|
Thats interesting.....
Sheetrock must have the joints sealed but its ok to butt OSB together for a fire wall? I have now started recommending a smoke detector in garages. I have had mine for 4 years now and not one false alarm. Due to many electrical panels being in garages and the firewalls it is an early warning smoke alarm. here is a link about garages http://homestore.com/HomeGarden/Gara...?poe=homestore |
|
#11
|
||||
|
||||
|
Gentlemen,
There seems to be some confusion here. The Table in http://www.osbguide.com/pdfs/TB117.pdf is in reference to tested assemblies that included gypsum as part of the assembly. These tests were done to demonstrate that OSB and plywood had similar fire characteristics and not to confirm the use of OSB as a firewall material. Bottom line: OSB is NOT a substitute for 5/8" taped Gypsum for the purpose of fire separation. |
|
#12
|
||||
|
||||
|
Thanks Mike !
I can't open that document for more than 10 seconds then it gives an error and has to close. As a summary, any Type X sheetrock is ok Is 1/2 or 5/8 regular sheetrock (taped with one coat) ok for firewall or does it depend on the AHJ ? 1/2 was ok around here in 2001 and still may be, not sure. |
|
#13
|
||||
|
||||
|
This might help.
One-Sided One-Hour Fire-Rated Wall AssembliesIn late 1997, Underwriters Laboratories Inc. (U.L.) promulgated a new fire-rated wall design that recognizes both oriented strand board (OSB) and plywood panels for wall sheathing in one-hour, fire-rated, load-bearing exterior wall assemblies. New fire-rated wall design - U.L. Design U356
Marcel |
|
#14
|
||||
|
||||
|
The issue of concern is the burn through rating(time).
But as in all code compliance issues the local AHJ rules. Allways good to keep that in mind. Hope the following helps. What's the difference between "regular" and "type X" gypsum wallboard? ASTM C 36 designates two types of gypsum wallboard, regular and type X. Type X wallboard, which is typically required to achieve fire resistance ratings, is formulated by adding noncombustible fibers to the gypsum. These fibers help maintain the integrity of the core as shrinkage occurs providing greater resistance to heat transfer during fire exposure. By ASTM definition, type X gypsum wallboard must provide: not less than a one hour fire resistance rating for 5/8" board or a 3/4 hour fire resistance rating for 1/2" board applied in a single layer, nailed on each face of load-bearing wood framing members, when tested in accordance with the requirements of ASTM E 119, Methods of Fire Test of Building Constructions and materials. Additionally, the Gypsum Association requires 1/2" type X gypsum board to achieve a one hour fire resistance rating when applied to a floor ceiling system, as described by GA File Number FC 5410, in GA 600, the Gypsum Association Fire Resistance Design Manu |
|
#15
|
||||
|
||||
|
Marcel's post while informative does not address the issue at hand.
The issue is What is required between the gargage and the interior dwelling space. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Escape, Fire & Smoke Alarms | badair | Interior Inspections | 14 | 1/28/08 7:21 AM |
| Fire rating | abolt | Structural Inspections | 13 | 9/21/07 8:45 PM |
| Service door Fire Rating | jmichael | Interior Inspections | 2 | 8/13/07 10:45 PM |