Default Paper Backed Batts

Isn't the paper backing supposed to be removed when the batts are placed on the roof sheathing for fire safety?

Last edited by bkelly2; 6/12/09 at 6:47 PM..
Reply With Quote
  #2  
Old 3/8/07, 6:51 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Paper Backed Batts

Now that would protect it from fire, but defeat it's purpose as a vapor barrier. We had inspectors tell us to either remove the paper where exposed, or flip it.

tom
Reply With Quote
  #3  
Old 3/8/07, 7:07 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Paper Backed Batts

Quote:
Originally Posted by tdietrich1
Now that would protect it from fire, but defeat it's purpose as a vapor barrier. We had inspectors tell us to either remove the paper where exposed, or flip it.

tom
If the vapor barrier is left on it is supposed to face the conditioned space Thomas, ie the attic in this case.
There is not much vapor here so I rarely see any vapor barriers in attics.

Is it a fire hazard as installed and was I correct to call it out?
Reply With Quote
  #4  
Old 3/8/07, 7:17 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Paper Backed Batts

Quote:
Originally Posted by bkelly2
Is it a fire hazard as installed and was I correct to call it out?
If you can read the warning, I guess it's in effect.

tom
Reply With Quote
  #5  
Old 3/8/07, 7:23 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Paper Backed Batts

Quote:
Originally Posted by bkelly2
There is not much vapor here so I rarely see any vapor barriers in attics.

Is it a fire hazard as installed and was I correct to call it out?
Non habitatable attics, crawlspaces and the like are exempt of having to cover the paper around here.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #6  
Old 3/8/07, 7:29 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Paper Backed Batts

Quote:
Originally Posted by lkage
Non habitatable attics, crawlspaces and the like are exempt of having to cover the paper around here.
Non Habitable, thanks Larry. I think I will re word my narrative for the next report. I also think I will continue to call it out as it is written in red on the batts.
Reply With Quote
  #7  
Old 3/8/07, 7:34 PM
scosta's Avatar
scosta scosta is offline
Active Poster
 
Join Date: Oct 2005
Location: North Royalton, Oh
Posts: 186
Please Note: scosta is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Paper Backed Batts

Whoa,
Does it say that on the paper?
Manufacturers instructions.
Steve
Reply With Quote
  #8  
Old 3/8/07, 7:53 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Paper Backed Batts

Quote:
Originally Posted by scosta
Whoa,
Does it say that on the paper?
Manufacturers instructions.
Steve
Don't leave the paper exposed.
Reply With Quote
  #9  
Old 3/8/07, 8:09 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Paper Backed Batts

I have an answer.
http://www.naima.org/pages/resources.../pdf/BI472.PDF
Reply With Quote
  #10  
Old 3/8/07, 9:17 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Paper Backed Batts

Quote:
Originally Posted by bkelly2
I would like to endorse this link and reiforce Brian's statements and links on this post.

I have undergone the past month on an 8 million dollar Project for Colby College in Waterville, Maine.

An issue came up about a renovation part of the project of the fact that the cathedral ceiling of the 1984 structure had been insulated with r- 38 batt insulation held in place with cold rolled channels with hat shaped channels .

I brought up the issue with the Architect from Pennsylvania, that the insulation had to be covered with a fire resistive material as indicated on the paper of the vapor retarder insulation material.

It has been ongoing now for a month. The owner feels it is existing conditions and I say it is but has to be upgraded due the extensive repairs and renovations, therefore has to be brought up to Code Compliance.

I was, as of this week advised to remove the paper facing on the insulation.

The biggest issue that I brought up is the fact the whole space above the new suspended ceilings to be, was designed as a plenum ceiling.
When I brought that up to the College Architect. He did not know what to say.

I advised him that if you leave that paper on the insulation, it is a fire hazard to today's Codes, and if you peel the paper off, you are exposing 24 years of dust contamination in your return system. IAQ. What are you going to do when the first employee is going to call in sick due to your air quality.?

Well, the plenum ceiling is now being redesigned as a ducted return system as we speak and the paper is removed off the batt insulation and it is now dangling fibers like stalactites in a cave.

I am still pushing the issue in to removing the insulation , but the money issue would be to finance spraying foam insulation to maintain the Energy Code of R-38 on the steel deck roof. At about $3.50 P.S.F., I would imagine it would bother me too.


Marcel

Reply With Quote
  #11  
Old 3/8/07, 9:26 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Paper Backed Batts

I see this vapor retarder exposed on most of my inspections.

It's simple.....Flip it all so that the vapor retarder is against the warm side of the buildinfg or seal it with drywall. It's combustible and it should not be left exposed.
Reply With Quote
  #12  
Old 3/8/07, 9:32 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Paper Backed Batts

Quote:
Originally Posted by dvalley
I see this vapor retarder exposed on most of my inspections.

It's simple.....Flip it all so that the vapor retarder is against the warm side of the buildinfg or seal it with drywall. It's combustible and it should not be left exposed.

Thanks David and Marcel, had a homeowner (FSBO) not too happy with my call. The Fireman husband did not seem to understand what the writing on the batts meant. Specifically not to leave the paper exposed. They sell fire retardant batts.

We call it the conditioned space here David, as the warm side of the building is the outside most of the time. 88 today.
Reply With Quote
  #13  
Old 3/8/07, 9:37 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Paper Backed Batts

[quote=bkelly2]Thanks David and Marcel, had a homeowner (FSBO) not too happy with my call. The Fireman husband did not seem to understand what the writing on the batts meant. Specifically not to leave the paper exposed. They sell fire retardant batts.

We call it the conditioned space here David, as the warm side of the building is the outside most of the time. 88 today.[/quote]

Happy birthday Brian and hope you get an other decade of this wonderfull world.

Take care;

Marcel
Reply With Quote
  #14  
Old 3/8/07, 9:42 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Paper Backed Batts

[quote=mcyr]
Quote:
Originally Posted by bkelly2
Thanks David and Marcel, had a homeowner (FSBO) not too happy with my call. The Fireman husband did not seem to understand what the writing on the batts meant. Specifically not to leave the paper exposed. They sell fire retardant batts.

We call it the conditioned space here David, as the warm side of the building is the outside most of the time. 88 today.[/quote]

Happy birthday Brian and hope you get an other decade of this wonderfull world.

Take care;

Marcel
Just one more decade???????? Yikes.
I kinda planned on four more decades, guess I shouldn't buy any green bannanas.
Reply With Quote
  #15  
Old 3/8/07, 9:58 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Paper Backed Batts

Quote:
Originally Posted by dvalley
I see this vapor retarder exposed on most of my inspections.

It's simple.....Flip it all so that the vapor retarder is against the warm side of the buildinfg or seal it with drywall. It's combustible and it should not be left exposed.
What David said. . .
Attached Thumbnails
paper-backed-batts-p1310040.jpg   paper-backed-batts-p1310041.jpg   paper-backed-batts-p1310043.jpg   paper-backed-batts-p1310044.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
As promised - Review of Newman's second radon study Caoimhín P. Connell Ancillary Inspection Services & Additional Topics 2 1/26/07 8:05 PM