Default Plumbing in upper kitchen cabinets??

Inspection today, drain pipes were found to extend below the unfinished ceiling into the upper kitchen cabinets.

Any REAL problems with this? I have not encountered this before?

Thanks,
Attached Thumbnails
plumbing-upper-kitchen-cabinets-img_7320.jpg  



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #2  
Old 2/27/07, 11:48 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Plumbing in upper kitchen cabinets??

Is this a condo or apartment, with separate units at each level? If so, this would be a firewall breach.

If this is a single unit (two floors), it's not really an issue.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 2/27/07, 11:51 PM
sfalvey sfalvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Plumbing in upper kitchen cabinets??

It is a single family house. I didn't think so, but just wanted to see other opinions.

Thanks.



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #4  
Old 2/28/07, 9:46 AM
edavis1 edavis1 is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Taneyville, mo
Posts: 41
Default Re: Plumbing in upper kitchen cabinets??

restaurant health inspector doesnt allow any unenclosed plumbing to run above food or food contact storage areas...I would fear moving around up stairs may cause paint chips or other harmful debris to come in contact with the drinking glasses or serving dishes...thats just my opinion after having been raised in the restaurant business.I am always watching for any hazzord that may effect the food chain.



EDavis
PObox173
Taneyville,Missouri 65759
NACHI06092670
Reply With Quote
  #5  
Old 2/28/07, 11:57 AM
thejnicki's Avatar
thejnicki thejnicki is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Vacaville, CA
Posts: 251
Default Re: Plumbing in upper kitchen cabinets??

Jeff, I have seen plumbing penetrate firewalls before.. It was spec'd that way and acceptible by local jurisdictions, It was sleeved and had firestop around the perimeter at the drywall pentrations..



Timothy Hejnicki
All-Specs Property Inspections
(707) 428-3544
Reply With Quote
  #6  
Old 2/28/07, 12:10 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Plumbing in upper kitchen cabinets??

Quote:
Originally Posted by thejnicki
Jeff, I have seen plumbing penetrate firewalls before.. It was spec'd that way and acceptible by local jurisdictions, It was sleeved and had firestop around the perimeter at the drywall pentrations..
Plumbing penetrations through a firewall are fine if/when done properly. In the above picture however (if this were to be a fire separation), the second floor framing is exposed. That would be considered a breach no matter how you slice it.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 2/28/07 at 12:13 PM..
Reply With Quote
  #7  
Old 2/28/07, 12:28 PM
thejnicki's Avatar
thejnicki thejnicki is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Vacaville, CA
Posts: 251
Default Re: Plumbing in upper kitchen cabinets??

Yes correct, Thanks Jeff..



Timothy Hejnicki
All-Specs Property Inspections
(707) 428-3544
Reply With Quote
  #8  
Old 3/1/07, 7:44 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Plumbing in upper kitchen cabinets??

Well whether or not this is acceptable in a single family, all I can say, this sh#t would not fly with my wife, and most likely write it up myself and find a reason. Standards anyone.???

Marcel
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Plumbing vent next to exhaust vent mpettitt Plumbing Inspections 4 10/12/07 6:38 PM
Kitchen floor slopes?? crichiii Structural Inspections 6 5/29/07 8:24 PM
No "H" clips? jbreazeale Structural Inspections 7 5/17/07 3:28 PM
Plumbing Code changes mcyr Plumbing Inspections 0 9/8/06 6:47 PM
A few useful posts - I forget from whom jmichalski Plumbing Inspections 12 3/30/06 10:06 PM


All times are GMT -4. The time now is 4:00 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts