  #16  
Old 3/15/07, 8:21 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Question about pull down attic stairs

Quote:
Originally Posted by mcyr
It will give us something to write in our reports though, right?

Marcel
</IMG></IMG>
Exactly.

As I said, it's simply a recommendation to upgrade if your client was interested in a fire rated pull-down. Other than that, it's good ole' 5/8" fire rated drywall.

As you stated, many builders will install the cheapest version of pull-downs in order to recoup their costs and make profits at the same time.
Reply With Quote
  #17  
Old 3/16/07, 2:31 AM
jkormos's Avatar
jkormos jkormos is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Medinah, IL
Posts: 641
Default Re: Question about pull down attic stairs

Well if it is in the garage, and if there is a fire wall separation between the garage attic area and the living space attic area then no problem.



Joe Kormos
A-1st Look Home Inspectors Inc.
630-201-0933
Your 1st Choice in Property Inspection Professionals
www.a-1stlookhomeinspectors.com
www.a-1stlook.com
Let us look before you buy...for peace of mind
“Thinking is the hardest work there is, that’s why so few engage in it. ” Henry Ford
Reply With Quote
  #18  
Old 3/16/07, 8:29 AM
waksell waksell is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Orlando, FL
Posts: 199
Default Re: Question about pull down attic stairs

Quote:
Originally Posted by dvalley
Exactly.

As I said, it's simply a recommendation to upgrade if your client was interested in a fire rated pull-down. Other than that, it's good ole' 5/8" fire rated drywall.

As you stated, many builders will install the cheapest version of pull-downs in order to recoup their costs and make profits at the same time.
This is what I was looking for. I hate to criticize something without giving a possible solution.
Reply With Quote
  #19  
Old 3/21/07, 10:07 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,843
Default Re: Question about pull down attic stairs

I called Memphis Stairs again and they sent out 18 pages about their products built with Dricon Fire Retardant Treated wood http://www.dricon.com/



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #20  
Old 3/22/07, 2:26 AM
jhugenroth jhugenroth is offline
InterNACHI Member
 
Join Date: May 2004
Location: Fresno, CA
Posts: 1,152
Please Note: jhugenroth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question about pull down attic stairs

Quote:
Originally Posted by jkormos
Well if it is in the garage, and if there is a fire wall separation between the garage attic area and the living space attic area then no problem.
Problem is, most I've seen DON'T have a fire wall between garage attic and house.
Reply With Quote
  #21  
Old 3/27/07, 12:57 PM
InspectorRiggs InspectorRiggs is offline
New User
 
Join Date: Sep 2006
Posts: 14
Please Note: InspectorRiggs is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question about pull down attic stairs

How many of you guys would actually write that up? It would seem that unless you are doing a Code Inspection, mentioning code deficiencies on an occupied structure could get you into hot water....because if you mention ONE code deficiency, and not any others that probably will exist, you have opened yourself up now to everything you don't happen to catch.
Reply With Quote
  #22  
Old 3/27/07, 3:57 PM
jhugenroth jhugenroth is offline
InterNACHI Member
 
Join Date: May 2004
Location: Fresno, CA
Posts: 1,152
Please Note: jhugenroth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question about pull down attic stairs

Quote:
Originally Posted by InspectorRiggs
How many of you guys would actually write that up? It would seem that unless you are doing a Code Inspection, mentioning code deficiencies on an occupied structure could get you into hot water....because if you mention ONE code deficiency, and not any others that probably will exist, you have opened yourself up now to everything you don't happen to catch.
I always write it up. I don't mention code.It is written up as a safety concern.

Most safety issues have their basis in code anyway. A lack of a GFCI in a new house bathroom receptacle is a "code" item, yet you wouldn't hesitate to write that up, would you?
Reply With Quote
  #23  
Old 3/27/07, 7:09 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Question about pull down attic stairs

Quote:
Originally Posted by InspectorRiggs
How many of you guys would actually write that up? It would seem that unless you are doing a Code Inspection, mentioning code deficiencies on an occupied structure could get you into hot water....because if you mention ONE code deficiency, and not any others that probably will exist, you have opened yourself up now to everything you don't happen to catch.
I red flag these on a weekly basis. I'm not into code compliance, I'm looking out for the safety of my clients.
Reply With Quote
  #24  
Old 3/27/07, 7:24 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,918
Default Re: Question about pull down attic stairs

Quote:
Originally Posted by InspectorRiggs
How many of you guys would actually write that up? It would seem that unless you are doing a Code Inspection, mentioning code deficiencies on an occupied structure could get you into hot water....because if you mention ONE code deficiency, and not any others that probably will exist, you have opened yourself up now to everything you don't happen to catch.
Noting or writing up as you call it of a fold down stairwell would not necessarily denote or admit that you are quoting Code Compliance.
That is not our job.

Writing up a folding stairwell that was observed as being installed contrary to the Manufacturers Specifications for installation is our job.
When a big red sticker says screw here and I see a clinched sixteen penny nailed from the opposite side, I will write it up too.

Sometimes one has to bend forward to the fact the Manufactures have evolved to recommending certain procedures to install their Products for a reason unknown to many unless deep research is done to find out why.

Bottom line, is write hard and teach. There are certain standards of installations that need to be adhered too, that might pertain to the safety of the occupants of the dwelling.


Hope this helps.

Marcel
Reply With Quote
  #25  
Old 3/27/07, 9:21 PM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question about pull down attic stairs

I agree 100%. Though I apply today's standards to every house. I could be inspecting abe lincoln's log cabin and if it doesn't have gfci in the necessary places, it gets written as a safety hazard. Realtors usually say,"it was code when it was built" but my philosophy is that the house should updated to conform to today's standards. Example....I inspected a house in which the gas water heater was in a "closet" in the garage....flush with the wall. The closet was tiny, basically enough space only for the heater and the heater was on the floor. It said right on the heater that it needed to be 18 inches off the floor if installed in a flammable area. The realtor called me and asked if I looked where it was installed to see there wasn't room to raise it. Well, then you should have put an electric heater in.
Reply With Quote
  #26  
Old 3/27/07, 9:53 PM
jhugenroth jhugenroth is offline
InterNACHI Member
 
Join Date: May 2004
Location: Fresno, CA
Posts: 1,152
Please Note: jhugenroth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question about pull down attic stairs

Quote:
Originally Posted by Scott Schultz
I agree 100%. Though I apply today's standards to every house. I could be inspecting abe lincoln's log cabin and if it doesn't have gfci in the necessary places, it gets written as a safety hazard. Realtors usually say,"it was code when it was built" but my philosophy is that the house should updated to conform to today's standards. Example....I inspected a house in which the gas water heater was in a "closet" in the garage....flush with the wall. The closet was tiny, basically enough space only for the heater and the heater was on the floor. It said right on the heater that it needed to be 18 inches off the floor if installed in a flammable area. The realtor called me and asked if I looked where it was installed to see there wasn't room to raise it. Well, then you should have put an electric heater in.
I know this has been talked about on another thread, but electric water heaters have an ignition source ( heating element) that should be 18" from the floor in a garage as well.
Reply With Quote
  #27  
Old 3/27/07, 10:18 PM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question about pull down attic stairs

So what's the answer? the IPC states that electric water heaters don't need to be raised but others think there is an ignition source. Is there anything out there, studies or something, that prove that electric heaters can be ignited by automobile fumes? If so then that'll settle it for me and I'll recommend that ALL heaters be raised. Usually, you will see the electric ones raised but I thought that was to protect it from getting hit by the car.
Reply With Quote
  #28  
Old 3/28/07, 7:38 AM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,025
Default Re: Question about pull down attic stairs

Yesterdays inspection, the pull down was cut 6" too short AND it was jsut sitting on the trim no nail, screws, biling wire, bubble gum, or duct tape. I am gald I caught it because there was a new lexus parked under it.



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #29  
Old 3/30/07, 2:35 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Question about pull down attic stairs

I use this as a reference for how to retro-fit in my reports:

http://www.aohomeinspection.com/pdf/Firewalls.pdf



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #30  
Old 3/31/07, 12:03 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: Question about pull down attic stairs

Quote:
Originally Posted by Scott Schultz
So what's the answer? the IPC states that electric water heaters don't need to be raised but others think there is an ignition source. Is there anything out there, studies or something, that prove that electric heaters can be ignited by automobile fumes? If so then that'll settle it for me and I'll recommend that ALL heaters be raised. Usually, you will see the electric ones raised but I thought that was to protect it from getting hit by the car.

I used to think the electric ones had an ignition source but the intent and location of the code relates to gas fired appliances.

The contactors in the electric water heaters are adequately sealed to not allow any sparks. The elements do not spark unless a wire is loose on one.

The gas water heaters also need to be protected by a steel post.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
code for minimum floor space at top of stairs? areid Miscellaneous Discussion for Inspectors 12 4/16/07 10:39 AM
Attic Pull Down Stairs charper Structural Inspections 7 2/21/07 4:31 PM
Attic ventilation question pdoane Interior Inspections 8 8/27/06 3:22 PM


All times are GMT -4. The time now is 9:34 AM.