Jerry Bettencourt is very trusted source of information Jerry Bettencourt is very trusted source of information Jerry Bettencourt is very trusted source of information Jerry Bettencourt is very trusted source of information Jerry Bettencourt is very trusted source of information Jerry Bettencourt is very trusted source of information
Default Question about UFFI Insulation?

I have an inspection coming up Friday and the client is very concerned about past UFFI insulation that was in the house that the seller who has owned the home for over 50 years says they had removed back in the eighties when all the hype started about UFFI. I have explained to the client already about the findings that UFFI is not as major a problem as it was once believed and will provide some literature for her about it. My question is that the sellers say that the removal process was that the contractor opened the walls up removed the UFFI and also scubbed the cavities with brushes, they then insulated with fiberglass and closed up and repaired the walls. Does this sound like the right way to remove it? Its sounds OK to me , but I just would like to hear from someone with some more experience with UFFI. Thanks.



JERRY BETTENCOURT
HOMETEST HOME INSPECTIONS
www.hometestinspections.com
www.hamiltonthermalimaging.com
hometestinspections@hotmail.com
I will keep my thoughts positive because my thoughts become my words. I will keep my words positive because my words become my actions. I will keep my actions positive because my actions become my values. I will keep my values positive because my values become my DESTINY!
United Family Martial Arts Student Creed
Reply With Quote
  #2  
Old 10/22/08, 10:21 PM
Brian A. MacNeish Brian A. MacNeish is online now
Active Poster
 
Join Date: Apr 2007
Posts: 2,223
Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question about UFFI Insulation?

Quote:
Originally Posted by jbettencourt View Post
I have an inspection coming up Friday and the client is very concerned about past UFFI insulation that was in the house that the seller who has owned the home for over 50 years says they had removed back in the eighties when all the hype started about UFFI. I have explained to the client already about the findings that UFFI is not as major a problem as it was once believed and will provide some literature for her about it. My question is that the sellers say that the removal process was that the contractor opened the walls up removed the UFFI and also scubbed the cavities with brushes, they then insulated with fiberglass and closed up and repaired the walls. Does this sound like the right way to remove it? Its sounds OK to me , but I just would like to hear from someone with some more experience with UFFI. Thanks.
Yes!! Our small company did about 20 houses then.

In most cases in the 1980's, this work was done under a partial grant process from the federal Dept of Consumer affairs......but no gov. records are available. Ask if any records / contractor invoices available from vendor?

After the walls were brushed, they were sprayed twice (and then allowed to dry) with a solution containing metabisulphite to neutralize UFFI chemicals that may be seeped into the wood.

The work in our area was always inspected by CMHC staff at various stages and sometimes with unannounced site visits!!
Reply With Quote
  #3  
Old 10/22/08, 10:28 PM
Jerry Bettencourt Jerry Bettencourt is offline
InterNACHI Member
 
Join Date: Oct 2007
Location: Stoney Creek, ON
Posts: 353
Jerry Bettencourt is very trusted source of information Jerry Bettencourt is very trusted source of information Jerry Bettencourt is very trusted source of information Jerry Bettencourt is very trusted source of information Jerry Bettencourt is very trusted source of information Jerry Bettencourt is very trusted source of information
Default Re: Question about UFFI Insulation?

The sellers are an old couple in their 80's moving to a retirement home, the buyer says that the sellers son says that he has copies of the contractors documents that did the removal. Thanks for the info Brian.



JERRY BETTENCOURT
HOMETEST HOME INSPECTIONS
www.hometestinspections.com
www.hamiltonthermalimaging.com
hometestinspections@hotmail.com
I will keep my thoughts positive because my thoughts become my words. I will keep my words positive because my words become my actions. I will keep my actions positive because my actions become my values. I will keep my values positive because my values become my DESTINY!
United Family Martial Arts Student Creed
Reply With Quote
  #4  
Old 10/23/08, 6:15 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 576
Bill Smith is often very helpful Bill Smith is often very helpful
Default Re: Question about UFFI Insulation?

Question - why bother to remove the UFFI insulation? My understanding is that any potential problems from out-gassing happened a long time ago.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #5  
Old 10/23/08, 6:39 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: GARLAND, TX
Posts: 3,152
Barry Adair .
Default Re: Question about UFFI Insulation?

Quote:
Originally Posted by bsmith View Post
Question - why bother to remove the UFFI insulation? My understanding is that any potential problems from out-gassing happened a long time ago.
Answer: The "suits" got involved...mining for courtroom gold



badair
http://www.adairinspection.com
972-487-5634
Dallas & Garland, TX 75228 & 75042

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39
04080595
Voted, by a slim margin, InterNACHI U.S. Member of the Year 2008

life is the random lottery of events followed by numerous narrow escapes...accept the good
http://www.gunlaws.com/images/unitys.gif
Reply With Quote
  #6  
Old 10/23/08, 7:19 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 4,757
Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute
Default Re: Question about UFFI Insulation?

For our American friends;
This is an article from our Gov. agency resposible for housing [CMHC] very interesting read.

Jerry,

Also, just for your info, sometimes it was more cost effective to remove the facade, whatever that was [brick, wood siding etc.], instead of the interior finishes. Furthermore, sometimes the UFFI was left in place and an HRV was installed and the house was sealed tight as a remedial measure. Very similar to an R-2000 home.





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com

Last edited by mkyriacou; 11/17/08 at 5:18 PM.
Reply With Quote
  #7  
Old 10/23/08, 7:37 PM
Jerry Bettencourt Jerry Bettencourt is offline
InterNACHI Member
 
Join Date: Oct 2007
Location: Stoney Creek, ON
Posts: 353
Jerry Bettencourt is very trusted source of information Jerry Bettencourt is very trusted source of information Jerry Bettencourt is very trusted source of information Jerry Bettencourt is very trusted source of information Jerry Bettencourt is very trusted source of information Jerry Bettencourt is very trusted source of information
Default Re: Question about UFFI Insulation?

Thanks Mario, that is some of the literature that I am providing to the client tomorrow.



JERRY BETTENCOURT
HOMETEST HOME INSPECTIONS
www.hometestinspections.com
www.hamiltonthermalimaging.com
hometestinspections@hotmail.com
I will keep my thoughts positive because my thoughts become my words. I will keep my words positive because my words become my actions. I will keep my actions positive because my actions become my values. I will keep my values positive because my values become my DESTINY!
United Family Martial Arts Student Creed
Reply With Quote
  #8  
Old 10/24/08, 9:01 PM
Brian A. MacNeish Brian A. MacNeish is online now
Active Poster
 
Join Date: Apr 2007
Posts: 2,223
Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question about UFFI Insulation?

Quote:
Originally Posted by mkyriacou View Post
For our American friends;
This is an article from our Gov. agency resposible for housing [CMHC] very interesting read.

Jerry,

Also, just for your info, sometimes it was more cost effective to remove the facade, whatever that was [brick, wood siding etc.], instead of the interior finishes. Furthermore, sometimes the UFFI was left in place and an HRV was installed and the house was sealed tight as a remedial measure. Very simalar to an R-2000 home.
Not even close to an R2000 home!!!
Reply With Quote
  #9  
Old 10/24/08, 9:46 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 4,757
Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute
Default Re: Question about UFFI Insulation?

Quote:
Originally Posted by Brian A. MacNeish View Post
Not even close to an R2000 home!!!
No?
Is an R-2000 home not sealed tight?
Does an R-2000 home have an HRV?

Give it a rest BOY, you are way out in left field or on "Kool Aid"!





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #10  
Old 10/24/08, 9:47 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 4,757
Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute
Default Re: Question about UFFI Insulation?

I wish I could give you red all day long!





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #11  
Old 10/26/08, 1:06 AM
Brian A. MacNeish Brian A. MacNeish is online now
Active Poster
 
Join Date: Apr 2007
Posts: 2,223
Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question about UFFI Insulation?

Quote:
Originally Posted by mkyriacou View Post
No?
Is an R-2000 home not sealed tight?
Does an R-2000 home have an HRV?

Give it a rest BOY, you are way out in left field or on "Kool Aid"!
Mario:

Our company was doing remedial work on UFFI homes from 1981-86 and did about 20+ homes.....all but 2 were full exterior siding/sheathing removal. Only 2 were sealed with HRV's.....the first in 1981. The level of airsealing was not even close to an R2000 home since it did not entail any interior renovation but simply caulking/sealing at receptacles, switches, trim, etc. Air leakage at the partition/exterior walls and floors/exterior walls in 2 story houses was still untouched. The HRV was put in not because the house had become tight enough to need an HRV as in an R2000 house, but simply to provide lots of air exchange with heat recovery to remove any formaldehyde that may have entered the living space.

Another reason I can say that it was not even close to an R2000 home is that for 9-10 years until 1992, I was a site advisor/inspector, researcher, and the NB "troubleshooter" for the R2000 program...if there was a real or perceived problem with an R2000 home, I was called to go visit, inspect and recommend remediation. BTW, in 1989 and in 1993, 2 of my clients, whom I helped develop their energy efficient building skills, were named "Canada's R2000 Builder of the Year", not bad for a little place like Moncton (Pop 80,000)!! If you wish to confirm this, I can give you the names of the 2 builders and you can call them!!

Mario, I don't think I'm "out in left field", just try not to talk about things I don't know much about!!

BTW.......I don't see you adding much technical content to these boards......A lot of "rah!! rah!! rah!!", "attaboy"...etc. Maybe all your technical help is on the member boards that I don't see........maybe I should join just to confirm!!!

Yes, Mario, you give me more reds than anyone else, big boy!!
Reply With Quote
  #12  
Old 10/26/08, 11:40 AM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 4,757
Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute
Default Re: Question about UFFI Insulation?

Quote:
Originally Posted by Brian A. MacNeish View Post
Mario:

Our company was doing remedial work on UFFI homes from 1981-86 and did about 20+ homes.....all but 2 were full exterior siding/sheathing removal. Only 2 were sealed with HRV's.....the first in 1981. The level of airsealing was not even close to an R2000 home since it did not entail any interior renovation but simply caulking/sealing at receptacles, switches, trim, etc. Air leakage at the partition/exterior walls and floors/exterior walls in 2 story houses was still untouched. The HRV was put in not because the house had become tight enough to need an HRV as in an R2000 house, but simply to provide lots of air exchange with heat recovery to remove any formaldehyde that may have entered the living space.

Another reason I can say that it was not even close to an R2000 home is that for 9-10 years until 1992, I was a site advisor/inspector, researcher, and the NB "troubleshooter" for the R2000 program...if there was a real or perceived problem with an R2000 home, I was called to go visit, inspect and recommend remediation. BTW, in 1989 and in 1993, 2 of my clients, whom I helped develop their energy efficient building skills, were named "Canada's R2000 Builder of the Year", not bad for a little place like Moncton (Pop 80,000)!! If you wish to confirm this, I can give you the names of the 2 builders and you can call them!!

Mario, I don't think I'm "out in left field", just try not to talk about things I don't know much about!!

BTW.......I don't see you adding much technical content to these boards......A lot of "rah!! rah!! rah!!", "attaboy"...etc. Maybe all your technical help is on the member boards that I don't see........maybe I should join just to confirm!!!

Yes, Mario, you give me more reds than anyone else, big boy!!


Quote:

The HRV was put in not because the house had become tight enough to need an HRV as in an R2000 house, but simply to provide lots of air exchange with heat recovery to remove any formaldehyde that may have entered the living space.
Here we go with yet another book from MacNeish!!
The above "Dumb" statement is one of many from you!!
I give up with you.





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #13  
Old 10/26/08, 12:13 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 4,757
Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute
Default Re: Question about UFFI Insulation?

Quote:
Yes, Mario, you give me more reds than anyone else, big boy!!
Do you ever wonder why you get reds from me?

The first [of many] reason and the most important is that you published a private communication between yourself and me.
You can't be trusted with private e-mail. The second reason, you are a pompus *****hole, should I go on?





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #14  
Old 10/26/08, 5:20 PM
Brian A. MacNeish Brian A. MacNeish is online now
Active Poster
 
Join Date: Apr 2007
Posts: 2,223
Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful Brian A. MacNeish is often very helpful
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question about UFFI Insulation?

Quote:
Originally Posted by mkyriacou View Post
Do you ever wonder why you get reds from me?

The first [of many] reason and the most important is that you published a private communication between yourself and me.
You can't be trusted with private e-mail. The second reason, you are a pompus *****hole, should I go on?
Mario:

You, I and this whole board knows that the mentioned email was changed/items deleted to remove any way of identifying it as yours!! I simply said it was from a Canadian INACHI member (about 540 Canuck members at that time) and his comment on joining INACHI. If you remember......YOU OUTTED YOURSELF.....by owning the email.

I had no intention to say from whom I received it!! Calm down!!
Reply With Quote
  #15  
Old 10/26/08, 5:48 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 4,757
Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute Mario A. Kyriacou, CHI has a reputation beyond repute