Default Range vent into attic

I understand the rule of thumb is to vent to the outside. However, I came across a vent system from the range to the attic space above garage. At the termination point in the attic is a box with a filter and grill. Has anyone seen anything similiar? Is this acceptable? Any code issues?

Thanks,
Frank
San Antonio, TX
Attached Thumbnails
range-vent-into-attic-imgp1206.jpg  
Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/9/11, 1:18 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 9,868
Send a message via Yahoo to jfunderburk
Default Re: Range vent into attic

It should not terminate in the attic. Period. You can't fix stupid.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Service Award Winner 2013, 2012, 2011, 2010.
Ph: 704-351-1776
NACHI ID: NACHI05120170
www.aohomeinspection.com

Reply With Quote
  #3  
Old 7/9/11, 1:25 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 12,048
Default Re: Range vent into attic

What Joe said.


M1503.1 General. Range hoods shall discharge to the outdoors through a single-wall duct. The duct serving the hood shall have a smooth interior surface, shall be air tight and shall be equipped with a backdraft damper. Ducts serving range hoods shall not terminate in an attic or crawl space or areas inside the building.

Exception:
Where installed in accordance with the manufacturer's installation instructions, and where mechanical or natural ventilation is otherwise provided, listed and labeled ductless range hoods shall not be required to discharge to the outdoors.






CBC HOME INSPECTIONS

Christopher Currins
Professional Home Inspector In Edwardsville, Glen Carbon, Godfrey, Maryville,
Fairview Heights, O'Fallon and surrounding areas of S
outhern Illinois

We Make It Safer
Reply With Quote
  #4  
Old 7/9/11, 1:41 PM
Robert F. Eldridge Robert F. Eldridge is offline
InterNACHI Member
 
Join Date: Dec 2008
Posts: 2
Default Re: Range vent into attic

Thanks for the information....
Frank
Reply With Quote
  #5  
Old 7/9/11, 2:08 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Minnesota & Northern Iowa
Posts: 19,352
Default Re: Range vent into attic

Quote:
Originally Posted by ccurrins View Post
What Joe said.


M1503.1 General. Range hoods shall discharge to the outdoors through a single-wall duct. The duct serving the hood shall have a smooth interior surface, shall be air tight and shall be equipped with a backdraft damper. Ducts serving range hoods shall not terminate in an attic or crawl space or areas inside the building.

Exception: Where installed in accordance with the manufacturer's installation instructions, and where mechanical or natural ventilation is otherwise provided, listed and labeled ductless range hoods shall not be required to discharge to the outdoors.
Ahhh... BUT...

Is the GARAGE ATTIC considered "inside the building"???

One has to assume the garage is attached.

Other questions come to mind, such as "FireWall", "FireRated Damper", etc...
Reply With Quote
  #6  
Old 7/9/11, 3:16 PM
James F. McKee's Avatar
James F. McKee James F. McKee is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 6,582
Default Re: Range vent into attic

just call the fire department now...only a matter of time....



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com

440 225 8688
Reply With Quote
  #7  
Old 7/9/11, 3:40 PM
cevans cevans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: TX
Posts: 3,494
Please Note: cevans is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Range vent into attic

Quote:
Originally Posted by jjonas View Post
Ahhh... BUT...

Is the GARAGE ATTIC considered "inside the building"???

One has to assume the garage is attached.

Other questions come to mind, such as "FireWall", "FireRated Damper", etc...
"Ducts serving range hoods shall not terminate in an attic or..."

"Shall not terminate in an attic" stands alone, there are no "if"s, "but"s "except"s, "maybe"s or "sometime"s after that other than for listed ductless hoods.

No other questions need be asked/answered to determine that it is improper to vent the range hood into the attic.
Reply With Quote
  #8  
Old 7/9/11, 8:06 PM
mstankiewicz mstankiewicz is offline
InterNACHI Member
 
Join Date: Nov 2010
Posts: 151
Default Re: Range vent into attic

I agree with Jonas.
First we do not have all the facts. Just one picture.

International Mechanical Code (IMC) 2009. Chapter 5 Section 505.1-exception 1.
Also section 501.2 Exhaust Discharge. Exception 1. Whole house ventilation-type attic vents---

Jonas is right. There are more questions. This system may be allowed.
Reply With Quote
  #9  
Old 7/10/11, 12:14 AM
cevans cevans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: TX
Posts: 3,494
Please Note: cevans is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Range vent into attic

Quote:
Originally Posted by mstankiewicz View Post
I agree with Jonas.
First we do not have all the facts. Just one picture.

International Mechanical Code (IMC) 2009. Chapter 5 Section 505.1-exception 1.
Also section 501.2 Exhaust Discharge. Exception 1. Whole house ventilation-type attic vents---

Jonas is right. There are more questions. This system may be allowed.
When was this described as a "Whole house ventilation-type attic vent"? The question was in reference to a vent for a range.

Besides, you are referencing a general requirement. The specific code section for Domestic Kitchen Exhaust Systems is 505.1. Specific requirements always take precedence over general sections.

Quote:
SECTION 505 DOMESTIC KITCHEN EXHAUST EQUIPMENT

505.1 Domestic systems. Where domestic range hoods and domestic appliances equipped with downdraft exhaust are located within dwelling units, such hoods and appliances shall discharge to the outdoors through sheet metal ducts constructed of galvanized steel, stainless steel, aluminum or copper. Such ducts shall have smooth inner walls and shall be air tight and equipped with a backdraft damper.

Exceptions:

1. Where installed in accordance with the manufacturer's installation instructions and where mechanical or natural ventilation is otherwise provided in accordance with Chapter 4, listed and labeled ductless range hoods shall not be required to discharge to the outdoors.
2. Ducts for domestic kitchen cooking appliances equipped with downdraft exhaust systems shall be permitted to be constructed of Schedule 40 PVC pipe and fittings provided that the installation complies with all of the following:
2.1. The duct shall be installed under a concrete slab poured on grade.
2.2. The underfloor trench in which the duct is installed shall be completely backfilled with sand or gravel.
2.3. The PVC duct shall extend not more than 1 inch (25 mm) above the indoor concrete floor surface.
2.4. The PVC duct shall extend not more than 1 inch (25 mm) above grade outside of the building.
2.5. The PVC ducts shall be solvent cemented.
Also, assuming that this is a detached dwelling or townhouse, the applicable code would be the IRC not the IMC (though neither code allows venting to the attic, but you might as well reference the correct applicable code).

Lastly, and most important for the Texas inspector who posted the original question is what the TREC SOP requires of him
Quote:
(c) Range exhaust vent. The inspector shall report as Deficient:
(1) inoperative unit(s);
(2) a vent pipe that does not terminate outside the structure, if the unit is not of a re-circulating type or configuration;
(3) inadequate vent pipe material;
(4) unusual sounds or vibration levels from the blower fan(s);
(5) blower(s) that do not operate at all speeds; and
(6) deficiencies in the:
(A) filter;
(B) vent pipe;
(C) light and lens;
(D) secure mounting of the unit; and
(E) switches.
If that thing he photographed is attached to a range vent, as he described in his posted question, our Texas inspector needs to report it as deficient.

Last edited by cevans; 7/10/11 at 12:30 AM..
Reply With Quote
  #10  
Old 7/10/11, 1:30 AM
mstankiewicz mstankiewicz is offline
InterNACHI Member
 
Join Date: Nov 2010
Posts: 151
Default Re: Range vent into attic

Mr Evans,

Not hear to argue with you.

As Inspector's we will start to see more ductless range hood exhaust's.

The Purpose of the International Building Codes is for Health, Safety and Welfare of people in dwellings. The 2009 Building Code is addressing the fact that "where installed in accordance with manufacturer installation instructions, and where mechanical or natural ventilation is otherwise provided, listed and labeled ductless range hoods shall not be required to discharge to the outdoors".

This all has to do with "green energy" and Indoor air quality. Internachi IAC2, US Dept of Energy, HVAC Manufacture's, ASHRAE, American Lung Association and on and on.

The new range hood system will have not just one fan, but 3 or 4 fans, the grease from cooking will be filtered out of the air, the moisture and heat will go thru HRV's and ERV's-Heat and Energy Recovery systems.

Your Texas inspector questions that he asked where very clear to me. Really does not matter to me what State he is from, he is an InterNachi member.

SOP's? The Inspector asked question's. Pardon me, I just thought it might be a learning thing. "Has anyone seen anything similiar?" "Is this acceptable?" "Any code issue's?

I still have questions as to what type system and manufacturer. Who knows, there could be required fire damper's for the system. There are question's.

Again, you will see these type systems going forward. They do need to be tested and installed per manufacturer specifications. The new 2009 Building Code recognizes that fact.

The InterNachi IAC2 training and certification is free to all members. It's the future-"Air Quality".
Reply With Quote
  #11  
Old 7/10/11, 1:42 AM
cevans cevans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: TX
Posts: 3,494
Please Note: cevans is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Range vent into attic

Quote:
Originally Posted by mstankiewicz View Post
Mr Evans,

Not hear to argue with you.

As Inspector's we will start to see more ductless range hood exhaust's.

The Purpose of the International Building Codes is for Health, Safety and Welfare of people in dwellings. The 2009 Building Code is addressing the fact that "where installed in accordance with manufacturer installation instructions, and where mechanical or natural ventilation is otherwise provided, listed and labeled ductless range hoods shall not be required to discharge to the outdoors".

This all has to do with "green energy" and Indoor air quality. Internachi IAC2, US Dept of Energy, HVAC Manufacture's, ASHRAE, American Lung Association and on and on.

The new range hood system will have not just one fan, but 3 or 4 fans, the grease from cooking will be filtered out of the air, the moisture and heat will go thru HRV's and ERV's-Heat and Energy Recovery systems.

Your Texas inspector questions that he asked where very clear to me. Really does not matter to me what State he is from, he is an InterNachi member.

SOP's? The Inspector asked question's. Pardon me, I just thought it might be a learning thing. "Has anyone seen anything similiar?" "Is this acceptable?" "Any code issue's?

I still have questions as to what type system and manufacturer. Who knows, there could be required fire damper's for the system. There are question's.

Again, you will see these type systems going forward. They do need to be tested and installed per manufacturer specifications. The new 2009 Building Code recognizes that fact.

The InterNachi IAC2 training and certification is free to all members. It's the future-"Air Quality".
Ductless vent hoods have been around as long as I can remember, yes there will be new twists on them, but recirculating range hoods are not new stuff. Of course, a ductless system would find it quite challenging to send the exhaust air from the kitchen into the attic above the garage without the use of ducts now wouldn't it???

And these ultra modern, high efficiency, UL listed, range hood vents of which you speak are going to terminate inside the attic, inside of site-built, wooden boxes with HVAC return grills screwed onto the front of them.

So in direct answer to our inspector's questions (assuming his basic premise that this is part of the range vent is correct):
  • No one has ever seen this
  • No it's not acceptable (actually you should refer to it as a defect, as TREC does - we don't determine acceptability)
  • Yes there are code issues with whichever code you choose to apply to the situation (even though IBC does not apply)

That is unless there's a hidden UL listing sticker with accompanying installation instructions that are consistent with what we see hidden somewhere on that wooden box. LOL

Last edited by cevans; 7/10/11 at 2:06 AM..
Reply With Quote
  #12  
Old 7/19/11, 9:58 AM
ROBERT YOUNG, CMI's Avatar
ROBERT YOUNG, CMI ROBERT YOUNG, CMI is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: H4B2R8
Posts: 9,765
Send a message via Yahoo to ryoung7
Default Re: Range vent into attic

Quote:
Originally Posted by jfunderburk View Post
It should not terminate in the attic. Period. You can't fix stupid.

No more needs to be said.



Robert Young's "Montreal Home Inspection Services Inc."
Home inspector Montreal | Montreal Home Inspector
"Putting information where you need it most, "in your hands!"
montrealbuildinginspector.com
lavalhomeinspector.com
Reply With Quote
  #13  
Old 7/19/11, 10:22 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Missouri
Posts: 24,917
Default Re: Range vent into attic

Quote:
Originally Posted by reldridge View Post
Is this acceptable? Any code issues?

Thanks,
Frank
San Antonio, TX
Two separate and distinct questions.

Is it acceptable? No. There is never a legitimate reason to intentionally introduce moisture to attic space.

Any code issues? Who cares?
Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/19/11, 11:00 AM
ROBERT YOUNG, CMI's Avatar
ROBERT YOUNG, CMI ROBERT YOUNG, CMI is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: H4B2R8
Posts: 9,765
Send a message via Yahoo to ryoung7
Default Re: Range vent into attic

Quote:
Originally Posted by jbushart View Post
Two separate and distinct questions.

Is it acceptable? No. There is never a legitimate reason to intentionally introduce moisture to attic space.

Any code issues? Who cares?
Yes we are not code inspectors.
James;
Would it be better if he explains the 2 entries lines and there terminations to the client in his report?
What each one is for and where it goes.
The narrative will help the client understand what is going on.
If they both terminate in the box, there is a conflict and must be looked into by a professional.
Ether way thew exhaust must continue out the attic or be vented outside..



Robert Young's "Montreal Home Inspection Services Inc."
Home inspector Montreal | Montreal Home Inspector
"Putting information where you need it most, "in your hands!"
montrealbuildinginspector.com
lavalhomeinspector.com

Last edited by ryoung7; 7/19/11 at 11:38 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Roof decking condensation. Homewood Interior Inspections 15 3/5/10 11:00 AM
Microwave range vent clearance mbarnett Inspecting HVAC Systems 3 5/15/08 5:21 AM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing, Ethics & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Is inadequate roof or attic ventilation a defect? gliebig Exterior Inspections 85 1/16/08 6:56 PM
vent pipe in attic brepanshek Inspecting HVAC Systems 2 3/6/07 2:32 PM

All times are GMT -4. The time now is 3:36 PM.
no new posts