There was a recessed light above the shower that was not I/C rated. It turned on the same time the vent fan was turned on. I removed the bulb and covered up the hole with some Greenboard drywall. I cannot reach the light fixture in the attic to save my life as it is installed all the way back to where the soffit are on the other side of the wall.
My question is, can I now cover the fixture with some insulation? You can feel the cold air coming down from the opening in the ceiling (with the temp. piece of drywall removed.) I still have the exhaust fan operational and connected to the light fixture, just removed the bulb like I said. Many thanks in advance..... |
| Find an InterNACHI certified District Of Columbia Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Quote:
Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
|
#3
|
||||
|
||||
|
Quote:
I agree. Simply upgrade the fixture to an IC rated fixture and you now have the light you need. You will eventually miss that light (that you removed) as the shower cavity will now become be a dark dungeon. |
|
#4
|
||||
|
||||
|
I have a related thread I posted yesterday if someone could jump in I would appreciate it.
http://www.nachi.org/forum/f19/fixtu...-shower-45261/ |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Recessed Light? IC or Not IC Rated?? | crichiii | Electrical Inspections | 1 | 4/23/09 11:00 PM |
| Exploding light bulbs | kweiss | Electrical Inspections | 25 | 10/10/08 3:03 AM |
| IAC2 In new residential construction | mcyr | IAC2 Indoor Air Forum | 0 | 10/9/07 7:45 PM |