Safety glass and/or a bar at 36 inches that can withstand 50 psi.
Chuck |
|
#3
|
||||
|
||||
|
no 2 the glass. Grnd floor?
|
|
#4
|
||||
|
||||
|
Yeah the floor has pretty lights outside
Why do you say no? |
|
#5
|
|||
|
|||
|
If the bottom pane of glass is 9 sq. ft. or less, then no.
http://www.nachi.org/safety-glass-for-inspectors.htm http://www.deckmagazine.com/article/54.html InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
Last edited by gromicko; 11/13/09 at 8:15 PM.. |
|
#6
|
||||
|
||||
|
|
|
#7
|
||||
|
||||
|
Bob...your photo shows an improper installation. The 2006 IRC states:
Quote:
|
|
#8
|
||||
|
||||
|
Ahhh because it is not required. The lights in your eyes???
2nd floor needs protection as MB pointed out. Also if it is one you inspected probably needs gfci too, someone might run an exteinson cord out the window to a blender |
|
#9
|
||||
|
||||
|
How perceptive.
1988 highrise with no GFCI in Kitchen. My second place in two weeks with a heat pump. |
|
#10
|
|||
|
|||
|
Quote:
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#11
|
||||
|
||||
|
I think we need to read this right;
R308.4 Hazardous Locations. The following shall be considered specific hazardous locations for the purposes of glazing: (not the semi-colon) 1-7 7. Glazing in an individual fixed or operable panel, other than those listed above, that meets these conditions: a. pane greater than 9 sq. ft. b. bottom edge less than 18" c. top edge greater than 36 " d. one or mor walkings surfaces within 36" horizontally of the glazing. Unless I am wrong, it needs to be safety glazed because it meets item b. and meets item d. of article 7. LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#12
|
||||
|
||||
|
Must meet all 4 criteria.
It seems a protective bar must be placed at 36 in. ![]() ![]() I never measured sq ft so here is another measurement that shows the lower handle at about 23 in up off the floor as a clue. www.chicagopropertyinspection.com www.elliotthomeinspection.com www.chicagolandhomeinspection.com www.homeandcondoinspector.com www.homeandcondoinspection.com http://www.homeinspectorpro.com/ (Report Software) Bob Elliott http://www.chicagolandhomeinspector.com/ Last edited by belliott; 11/13/09 at 9:13 PM.. |
|
#13
|
|||
|
|||
|
Correct...
http://www.nachi.org/safety-glass-for-inspectors.htm R308.4: The Following shall be Considered Specific Hazardous Locations for the Purposes of Glazing: 1. Glazing in swinging doors except jalousies. 2. Glazing in fixed and sliding panels of sliding door assemblies, and panels 3. Glazing in storm doors. 4. Glazing in all unframed swinging doors. 5. Glazing in doors and enclosures for hot tubs, whirlpools, saunas, steam rooms, bathtubs, and showers. Glazing in any part of a building wall enclosing these compartments where the bottom exposed edge of the glazing is less than 60 inches (1524 mm) measured vertically above any standing or walking surface. 6. Glazing in an individual fixed or operable panel adjacent to a door where the nearest vertical edge is within a 24-inch (610 mm) arc of the door in a closed position and whose bottom edge is less than 60 inches (1524 mm) above the floor or walking surface. 7. Glazing in an individual fixed or operable panel, other than those locations described in Items 5 and 6 above, that meets all of the following conditions: 7.1. Exposed area of an individual pane larger than 9 square feet (0.836 mm). 7.2. Bottom edge less than 18 inches (457 mm) above the floor. 7.3. Top edge more than 36 inches (914 mm) above the floor. 7.4. One or more walking surfaces within 36 inches (914 mm) horizontally of the glazing. InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
| Find an InterNACHI certified South Carolina Home Inspector (and anywhere else in North America) |
|
#14
|
||||
|
||||
|
I think that is where it is confusing Bob,
does it? I read it like either or on all of them. Maybe not, don't know, I'll have to dig it up somewhere. LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#15
|
||||
|
||||
|
Yeah, your right Larry, I failed to read the meet all conditions:
I owe you one. Got to keep my glasses on for krist sake LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Clarification on Safety Glass | jweinberg | General Inspection Discussion | 4 | 12/25/06 1:35 AM |
| Electrical Safety Information | jtedesco1 | Electrical Inspections | 0 | 2/19/06 1:48 AM |
| Wired for Safety Video | jtedesco1 | Electrical Inspections | 0 | 1/4/06 6:31 AM |