Default Shower stall vent

I don't think so, but would a bathroom vent be allowed to be installed in a shower stall under any circumstances?
Reply With Quote
  #2  
Old 2/4/07, 8:27 AM
staylor5's Avatar
staylor5 staylor5 is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Freehold, NJ
Posts: 108
Default Re: Shower stall vent

What do you mean? Is the vent terminated under the stall or just passing under it?
Reply With Quote
  #3  
Old 2/4/07, 8:35 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Shower stall vent

Since there is no electricity connected to the ceiling register itself, there is no safety risk in mounting it in a shower stall.
Reply With Quote
  #4  
Old 2/4/07, 12:17 PM
Michael Masney's Avatar
Michael Masney Michael Masney is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Hamilton, ON
Posts: 96
Default Re: Shower stall vent

It is a bathroom exhaust vent with a fan motor.
Reply With Quote
  #5  
Old 2/4/07, 10:36 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Shower stall vent

Quote:
Originally Posted by mmasney
It is a bathroom exhaust vent with a fan motor.
Mike,

It's OK.
Reply With Quote
  #6  
Old 2/5/07, 9:24 AM
Michael Masney's Avatar
Michael Masney Michael Masney is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Hamilton, ON
Posts: 96
Default Re: Shower stall vent

Thanks for the help, I just figured there could be potential for electric shock with the fan actually in the stall.
Reply With Quote
  #7  
Old 2/5/07, 6:01 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,842
Default Re: Shower stall vent

Are we sure? I don't think fans are rated for wet location installation. Covers are not sealed like wet light fixtures.



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 9/30/08 at 4:09 PM..
Reply With Quote
  #8  
Old 2/5/07, 6:11 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,842
Default Re: Shower stall vent

If thee say fans ok what about this heater?



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 9/30/08 at 4:09 PM..
Reply With Quote
  #9  
Old 2/5/07, 7:16 PM
Michael Masney's Avatar
Michael Masney Michael Masney is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Hamilton, ON
Posts: 96
Default Re: Shower stall vent

I wrote it up as a potential for electric shock and recommended it be moved outside the stall. I agree with Barry, the covers are not sealed. There was also a light in the stall that was a proper sealed fixture for a shower.
Reply With Quote
  #10  
Old 2/6/07, 5:52 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Shower stall vent



Ok, I've done a little more research on exhaust fan installations over shower enclosures, as I've never red-flagged this installation in the past.

I should have stated that the fan must be UL rated for wet locations in order for it to be safely installed over shower enclosures. Most exhaust fan manufacturers do rate their fans to be installed over wet locations.

I'll be revising my reporting methods for this particular install to read, "I recommend further evaluation of shower fan to determine if this exhaust fan is rated for wet locations".

Here are additional links to this particular install...

http://www.mikeholt.com/code_forum/s...ad.php?t=69803

http://www.hvi.org/displayindustryar...ticlenbr=26733

http://pages.quicksilver.net.nz/geoffm/fan_FAQ.htm

http://www.amroyal.com/index.php?cmd=product&item=6385

http://www.keidel.com/design/select/vent-fans.htm

http://www.airkinglimited.com/airkin...d&art_id=10#Q8

http://www.pegasusassociates.com/Bat...tFanP90064.jsp

Last edited by dvalley; 2/6/07 at 5:56 AM..
Reply With Quote
  #11  
Old 2/6/07, 8:30 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,842
Default Re: Shower stall vent

David,
All you have to do is verify by label or stamp in the housing just like IC can lighting and make sure they cease operation when GFCI is tripped. No need for further evaluation unless this simple inspector evaluation fails. If so remove and replace.

BTW as usual the informational links from you are great!
Keep on keeping on.



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #12  
Old 2/6/07, 8:10 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Shower stall vent

Quote:
Originally Posted by badair
David,
All you have to do is verify by label or stamp in the housing just like IC can lighting and make sure they cease operation when GFCI is tripped. No need for further evaluation unless this simple inspector evaluation fails.
Yeah... I know, but I don't get into checking light and fan labels. Takes too much time. I find it easier to add the disclaimer to my 64-page manual.
Reply With Quote
  #13  
Old 1/15/08, 3:53 PM
Michelle B. Cooper Michelle B. Cooper is offline
New User
 
Join Date: Jan 2008
Posts: 1
Please Note: Michelle B. Cooper is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Shower stall vent

The above link has changed to the PegasusAssociates.com website:

http://www.pegasusassociates.com/Bat...FanP90064.html
Reply With Quote
  #14  
Old 1/15/08, 4:27 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,161
Send a message via MSN to bwiley
Default Re: Shower stall vent

Somehow I never thought about reaching up and grabbing the fan motor while taking a shower...



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #15  
Old 1/15/08, 4:58 PM
Richard A. Moran, 2nd Richard A. Moran, 2nd is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Clarksville, MD
Posts: 151
Default Re: Shower stall vent

Talk about kick starting your morning ....

Dick



Dick Moran
True Blue Home Inspections
A Div of RAM2, LLC.
Clarksville, MD
240-832-6838
MD Home Inspector License 29927
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
exhaust fan over shower stall dbook Electrical Inspections 5 4/24/07 5:40 PM
Air admittance valves everywhere apfaff Plumbing Inspections 13 4/16/07 10:17 AM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 6:22 PM
Shower stall light/fan on garage GFCI lprinzi Electrical Inspections 3 10/31/06 5:13 PM


All times are GMT -4. The time now is 8:11 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts