Default Smoke alarm requirements

Is there a code requirement for smoke installations that someone can provide?? House built in 2006 & were installed outside two bedrooms but not inside. I know it's not right, just need backing up.

Thanks, hope everyone had a great weekend!
Reply With Quote
Need a home inspection in Tennessee? Check out InterNACHI's listing of Tennessee certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/19/10, 1:00 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,850
Default Re: Smoke alarm requirements

I would recommend going to your own local AHJ to find out what is required in your area. You are going to get 50 different answers to this inquiry and some are going to be guesses based on what they have been told or for their jurisdictions. Codes change all the time and from county to county, state to state. Go to the source rather than this board (or any HI board). There is is more BS pumped out here than a Havana radio station.



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
  #3  
Old 4/19/10, 1:04 PM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Re: Smoke alarm requirements

Quote:
Originally Posted by dedwards View Post
I would recommend going to your own local AHJ to find out what is required in your area. You are going to get 50 different answers to this inquiry and some are going to be guesses based on what they have been told or for their jurisdictions. Codes change all the time and from county to county, state to state. Go to the source rather than this board (or any HI board). There is is more BS pumped out here than a Havana radio station.
LOL. Thanks for the helpful insight, Doug.
Reply With Quote
  #4  
Old 4/19/10, 3:49 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Smoke alarm requirements

That being said, I pretty much say, I do not test Smoke Detectors..and then either; there were no smoke detectors in the bedrooms and we recommend installing them...or there were smoke detectors in all of the bedrooms.

Really does not matter what the code says.......
Reply With Quote
  #5  
Old 4/19/10, 4:27 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Smoke alarm requirements

Quote:
Originally Posted by bkelly2 View Post
That being said, I pretty much say, I do not test Smoke Detectors..and then either; there were no smoke detectors in the bedrooms and we recommend installing them...or there were smoke detectors in all of the bedrooms.

Really does not matter what the code says.......
As well as Carbon Monoxide detectors, and in many cases, one is not enough.

Safety first !!!
Reply With Quote
  #6  
Old 4/19/10, 4:37 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Smoke alarm requirements

Quote:
Originally Posted by jjonas View Post
As well as Carbon Monoxide detectors, and in many cases, one is not enough.

Safety first !!!
Yes to CO detectors, although if there is no Fireplace and it is an All Electric Home I not recommend them myself
Reply With Quote
  #7  
Old 4/19/10, 4:48 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Smoke alarm requirements

Quote:
Originally Posted by bkelly2 View Post
Yes to CO detectors, although if there is no Fireplace and it is an All Electric Home I not recommend them myself
Unless there is an attached garage!
Reply With Quote
  #8  
Old 4/19/10, 5:54 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Smoke alarm requirements

Here in Maine, all Jurisdictions that have adopted the NFPA 101 will need to comply with the requirements below.
Checking code requirements in the Jurisdiction you are in might be prudent.



24.3.4 Detection, Alarm and Communications Systems.
Approved single-station smoke alarms shall be installed in accordance with 9.6.2.10 in the following locations:
(1) All sleeping rooms (exceptions: Smoke alarms shall not be required in sleeping rooms in existing one and two-family dwellings.)
(2) Outside of each separate sleeping area, in the immediate vicinity of the sleeping rooms
(3) On each level of the dwelling unit, including basements
(Exception No. 1: Dwelling units protected by an approved smoke detection system in accordance with Section 9.6 and equipped with an approved means of occupant notification.) (Exception No. 2: In existing one and two-family dwellings approved smoke alarms powered by batteries shall be permitted.
9.6.2.10 Smoke Alarms
9.6.2.10.1 Where required by another section of this Code, single-station smoke alarms shall be in accordance with the household fire-warning equipment requirements of the NFPA 72, National Fire Alarm Code, and are arranged to function in the same manner.
9.6.2.10.2 Smoke alarms, other than battery –operated devices as permitted by other sections of this Code, or battery-operated devices complying with 9.6.1.4 and the low-power wireless system requirements of NFPA 72, National Fire Alarm code, shall receive their operating power from the building electrical system.
9.6.2.10.3 * In new construction, unless otherwise permitted by another section of this Code, where two or more smoke alarms are required within a living unit, suite of rooms, or similar area, they shall be arranged so that operation of any smoke alarms shall cause the alarm in all smoke alarms within the living unit, suite of rooms, or similar area to sound.

(Exception: this requirement shall not apply to configurations that provide equivalent distribution of the alarm signal.)
Reply With Quote
  #9  
Old 4/19/10, 7:21 PM
Greg Keene, CPI's Avatar
Greg Keene, CPI Greg Keene, CPI is offline
InterNACHI Member
 
Join Date: May 2007
Location: Evergreen, CO
Posts: 628
Default Re: Smoke alarm requirements

Joshua - as far back as 2003 - IRC
R313.1 Smoke Alarms. Smoke alarms shall be installed in the the following locations:
1. In each sleeping room.
2. OUtside each separate sleeping area in the immediate vicinity of the bedrooms.
3. etc, etc, etc,



Greg Keene
Clear Choice Home Inspections
Evergreen, CO
303-674-3234
greg@clearchoice-hi.com
Reply With Quote
  #10  
Old 4/20/10, 3:45 AM
J. Christopher Weise J. Christopher Weise is offline
InterNACHI Member
 
Join Date: Oct 2007
Location: Woodstock, GA
Posts: 169
Default Re: Smoke alarm requirements

1. On the ceiling or wall outside of each separate sleeping area in the vicinity of bedrooms.
2. In each room used for sleeping purposes.
3. In each story within a dwelling unit, including basements and cellars but not including crawl spaces and uninhabitable attics.
4. The units shall be interconnected such that the activation of one alarm will activate all alarms.
5. When primary power is interrupted the smoke alarm shall receive power from a battery.
6. The smoke alarm shall be supplied by a single branch circuit serving one or more of the required lighting outlets and permanently connected ahead of the switching devices.
7. AFCI protected.

Last edited by jweise; 4/20/10 at 3:51 AM..
Reply With Quote
  #11  
Old 4/20/10, 10:36 AM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Re: Smoke alarm requirements

Try the ICC Residential Building Code Book....IRC
Reply With Quote
  #12  
Old 4/20/10, 12:59 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Smoke alarm requirements

http://www.nachi.org/forum/f19/smoke...acement-32766/

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Florida Licensing Bill - Action Soon jburkeson1 Legislation, Licensing & Legal Issues for Inspectors 250 7/1/10 4:50 PM
2 questions staylor5 Electrical Inspections 14 12/18/09 2:32 AM
Smoke Detector placement jwicklander Electrical Inspections 0 9/17/08 6:43 PM


All times are GMT -4. The time now is 4:04 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts