i have always understood that s.a.'s must be 3 feet away from return vents. did something change with the 2006 irc as I don't see a reference to it?
Richard W. Washington, owner RW Home Inspections, Inc. www.RWHOMEINSPECTIONS.com Texas Real Estate Commission (TREC) Professional Inspector License #7238 Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter InterNACHI member since 2004 Based in Katy, serving Houston and all surrounding communities |
does nobody have an answer?
Never heard of that, are you thinking about a manufacturer's recommendations?
tom |
I've not heard of that rule either. What would the logic be for it? Actually, it would seem like a good spot to me. Any smoke in the home would be drawn towards the R/A if the AHU was running.
Follow the instruction that come with the alarm(s) an these links http://www.nfpa.org/categoryList.asp?categoryID=278&URL=Research%20&%2 0Reports/Fact%20sheets/Smoke%20alarms https://www.usfa.dhs.gov/downloads/pdf/publications/fa-250f.pdf I don't think you can go wrong if they adhere to these guidelines. What others say on the other MB is hearsay without documentation, imo hth Additional helpful links Smoke Alarms and CO Detectors: For more information about smoke alarms and specialized smoke alarms for the blind and hearing impaired, including talking, strobe (up to 177 candela), vibrating and amplified (up to 90 dB) smoke alarm products: BRK Brands: www.brkelectronics.com or 1.800.323.9005 First Alert: www.firstalert.com or 1.800.323.9005 Gentex: www.gentex.com or 1.800.436.8391 Home Depot Supply: www.hdsupply.com Kidde: www.kiddeus.com or 1.800.880.6788 MaxiAids (Provides a variety of products for special needs): www.maxiaids.com http://www.cpsc.gov/CPSCPUB/PUBS/464.pdfhttp://www.usfa.dhs.gov/downloads/pyfff/inhome.html http://www.epa.gov/iaq/co.html ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good Last edited by badair; 5/26/08 at 7:41 AM.. |
thanks. Barry. it's the NFPA i was forgetting since the IRC makes no mention.
Smoke alarms are installed inside return duct, so what is the issue?
Others might though...go ahead and post it.
Commercial, not so much in residential except the big stuff.
Areas to avoid for installation Quote:
No mention of return air compartment or return air ducts. Makes sense as return air areas would pull the smoke there first. Many smokies are indeed place in the return ducts in commercial applications. Hearsay indeed. Last edited by bkelly2; 5/27/08 at 2:25 AM.. |
Here is a duct smoke detector inside a return air duct.
This would shut down the ventilations system when it senses smoke and go into general alarm. Attachment 21527 Hope this helps. Marcel LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 Last edited by mcyr; 11/16/08 at 7:35 PM.. |
Good one Marcel. Tim |
Smoke alarms and detectors shall not be installed within 36 inches horizontal path from the supply registers and should also be installed out of the direct airflow from those registers. Same thing with ceiling fans...36 inch horizontal path from the tip of the blades.
The commercial duct smokes have two pipes mounted on surface of the detector that poke into the duct. The airflow acts as a vacuum and a continuous sample of air goes through the detector. Any evidence of smoke shuts that unit down and system goes into alarm. |