Default Smoke Detector testing..Question

Who is responible for testing that a smoke detector works ?

My Home inspector school advised that we only note and inform

that they are in the correct areas.....

What is the a Home Inspectors responsibility in this area ?


David
Reply With Quote
  #2  
Old 9/22/08, 2:31 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Smoke Detector testing..Question

It is prudent to note the number and location, but unwise to officially record their working status unless you intend to back that up if they fail during a fire.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #3  
Old 9/22/08, 2:40 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,567
Default Re: Smoke Detector testing..Question

I like to tell people that moving into a new home is a great time to replace smoke detectors to make sure they have all new and properly functioning units...a very small price for a very important item...jmo....jim



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #4  
Old 9/22/08, 2:40 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,515
Default Re: Smoke Detector testing..Question

Quote:
Originally Posted by jbushart View Post
It is prudent to note the number and location, but unwise to officially record their working status unless you intend to back that up if they fail during a fire.
Agree, and I always put a statement in my reports, in BOLD and included in the Summary, that all fire detectors should be tested for proper operation immediately upon moving into home.



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
  #5  
Old 9/22/08, 5:03 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Smoke Detector testing..Question

I note the locations, test the accessible units installed using the test button and recommend upgrading to current required locations when needed.

www.mauihomeinspections.com
Reply With Quote
  #6  
Old 9/22/08, 5:32 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Smoke Detector testing..Question

My General Comment...

Smoke Detectors
- Detectors are noted as present but not sounded or inspected.
- Recommend the installation of smoke detectors at each level and bedroom of the home.
Placement should be in accordance with the manufacturer's recommendations.
- Recommend the installation of Carbon Monoxide (CO) detectors in homes with Gas / Oil fired
appliances. Placement should be in accordance with the manufacturer's recommendations.
- Recommend the installation of Carbon Monoxide (CO) detectors in homes with attached
Garages. Placement should be in accordance with the manufacturer's recommendations.
- Recommend the replacement of smoke detectors at 10 year intervals per the manufacturer's recommendations.




Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #7  
Old 9/22/08, 5:42 PM
cmcdonald cmcdonald is offline
New User
 
Join Date: Mar 2007
Location: Jaffrey, NH
Posts: 80
Please Note: cmcdonald is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Smoke Detector testing..Question

As a general rule, I also note if the location is at least 4 inches from the wall (for ceiling mounted detectors) and if the detector is at least 4 inches from the ceiling but not more than 12 inches from the ceiling for wall mounted detectors.

Just my two cents.
Reply With Quote
  #8  
Old 9/22/08, 6:11 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Smoke Detector testing..Question

Remember using the test button , only tests the energy source to the unit,and not function.
Reply With Quote
  #9  
Old 9/22/08, 7:32 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Smoke Detector testing..Question

Check your state's SOP, if you are in a licensing state. Or, check the SOP of whatever certifying association you are a member of. Here's what NC says:

"C. Report on presence or absence of smoke detectors, and operate their test function, if accessible, except when detectors are part of a central system."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 9/22/08, 7:33 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Smoke Detector testing..Question

Check your state's SOP, if you are in a licensing state. Or, check the SOP of whatever certifying association you are a member of. Here's what NC says:

"C. Report on presence or absence of smoke detectors, and operate their test function, if accessible, except when detectors are part of a central system."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #11  
Old 9/22/08, 9:54 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Smoke Detector testing..Question

"C. Report on presence or absence of smoke detectors, and operate their test function, if accessible, except when detectors are part of a central system."[/quote]


I accidentally tested a central system once so I was able to verify the response time of the police and fire department (which was actually pretty good.

www.mauihomeinspections.com
Reply With Quote
  #12  
Old 9/24/08, 12:33 AM
mjones6 mjones6 is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Roundlake Beach, IL
Posts: 250
Default Re: Smoke Detector testing..Question

The smoke and co2 meters I bought for my house recommended they be replaced every 5 years. I'm not gonna guess how old detectors are in a house. I recommend they be replaced and the client checks with the local fire dept. for recommendations.



Mark Jones
Allmark Home Inspection Services Inc.
Serving all of Northern Illinois, Vernon Hills, Libertyville, Gurnee, Fox Lake, Round Lake

Phone: 847 651 2053
E-Mail: AllmarkInspect@aol.com

www.AllmarkHomeInspection.com
Reply With Quote
  #13  
Old 9/24/08, 12:40 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Smoke Detector testing..Question

Quote:
Originally Posted by jbushart View Post
It is prudent to note the number and location, but unwise to officially record their working status unless you intend to back that up if they fail during a fire.
I agree also Jim, explain it makes noise, but I'll be damned if I know whether it detects smoke.

I recommend they replace them, who knows what somebody might have done to one of them, or all of them, their cheap, and save lives, buy new ones.
Reply With Quote
  #14  
Old 9/24/08, 8:01 AM
Douglas Cossar's Avatar
Douglas Cossar Douglas Cossar is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Whitby, On
Posts: 1,228
Default Re: Smoke Detector testing..Question

Quote:
Originally Posted by Mark Thorman View Post
"C. Report on presence or absence of smoke detectors, and operate their test function, if accessible, except when detectors are part of a central system."

I accidentally tested a central system once so I was able to verify the response time of the police and fire department (which was actually pretty good.

www.mauihomeinspections.com[/quote]

The fire department in my neck of the woods charges $800.00/truck for false alarms. I never test if there is an alarm system installed.
I always suggest replacement as well.

Cheers



Doug Cossar CMI, NHI
Accurate Home Inspection
Services Inc.
Whitby Ontario
www.accuratehomeinspections.ca
05021384
Reply With Quote
  #15  
Old 9/24/08, 11:45 AM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Smoke Detector testing..Question

Quote:
Originally Posted by dcossar View Post
alarms. I never test if there is an alarm system installed.
I always suggest replacement as well.

Cheers
If you trigger an alarm system during an inspection, you can sometimes demonstrate your superior knowledge to the buyers and the realtor and disable the beepbeep by taking the cover off and clipping one of the speaker wires. Don't ask how I know this.

John Kogel
www.allsafehome.ca
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Smoke Detector placement jwicklander Electrical Inspections 0 9/17/08 6:43 PM
Smoke and CO2 detectors Michael Merino General Inspection Discussion 10 4/16/08 12:23 PM
Smoke alarm history Marc D. Shunk Electrical Inspections 6 2/12/08 1:18 AM
WA State Legislative update hmiller Legislation, Licensing & Legal Issues for Inspectors 153 5/4/07 11:55 PM
Answer to a common question about GFCI's jtedesco1 Electrical Inspections 4 1/12/06 9:29 PM


All times are GMT -4. The time now is 4:05 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts