Inspection today had basement stairs that came to a landing on ground floor, landing has rooms on both sides. Back side room has 12" step to floor off landing. Both sides have 6' of clear headroom to knock your head on when stepping off the landing. Around here, typically 6'8" is minimum. Ceilings are 7'. Do I call out a code or remark "typical" conditions?
Scott Falvey Clear View Home Inspections, LLC Newbury, NH NACHI#05051292 www.clearviewhomeinspectionsllc.com |
|
#2
|
||||
|
||||
|
Scott;
I do not think that I would call it typical condition, because it is not and believe that noting what you have seen would be in order in your report. To the affect that it is not the standard of building standards and also it kind of runs away from the code requirements of a riser height of 7 3/4" and 10" tread and the 6' 8" head room requirements. Note what you see and let the Client decide what they want to do with the issue. Hope this helps. |
|
#3
|
||||
|
||||
|
Please Note:
Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
You say it's a basement. Is it a finished living space, heated and all that? If it's just a 'crete floor basement, I'd mention the safety hazard and call it done. If it's finished as a bedroom (don't forget heat, egress, and closet) then you'd have to check you local code, but still would just note it. We're not codeies.
|
|
#4
|
|||
|
|||
|
Basement is in process of being "finished". Seller has framed walls, some drywall up, heat would only come from radiation from mechanical room, no closets, would not consider finished space suitable for bedrooms. Seller is selling house with trim, window trim and "finished" basement unfinished. Oh also, the windows were installed over the outside finish texture sheets and then trimmed over.
Scott Falvey Clear View Home Inspections, LLC Newbury, NH NACHI#05051292 www.clearviewhomeinspectionsllc.com |
|
#5
|
||||
|
||||
|
I would write it up as less than standard clearance and let the buyer decide.
If they are "little people" or it's former secretary Robert Reich(4-8") they wouldn't care. You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#6
|
||||
|
||||
|
Please Note:
Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#7
|
|||
|
|||
|
Hi Jay,
No flashing, even if there were, it could only be between the window nailing flange and the trim. The windows are in the middle of a full 4'x8' sheet. They did use caulk, does that count? Scott Falvey Clear View Home Inspections, LLC Newbury, NH NACHI#05051292 www.clearviewhomeinspectionsllc.com |
|
#8
|
||||
|
||||
|
Please Note:
Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#9
|
||||
|
||||
|
|
|
#10
|
|||
|
|||
|
Please Note:
rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Before I render an opinion, how old is the house? Does it predate current construction practice/code?
|
|
#11
|
|||
|
|||
|
House is 3 years old.
Scott Falvey Clear View Home Inspections, LLC Newbury, NH NACHI#05051292 www.clearviewhomeinspectionsllc.com |
|
#12
|
|||
|
|||
|
Please Note:
rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Okay thanks, so you have a situation on your hands that do not meet code requirements. The question then that must be asked; how did this pass given that an occupancy permit was likely granted?
|
|
#13
|
|||
|
|||
|
Not necessarily Ray, we have many towns in this area that do not have building officials. The structure just goes up and somebody moves in. Kinda nice huh?
Scott Falvey Clear View Home Inspections, LLC Newbury, NH NACHI#05051292 www.clearviewhomeinspectionsllc.com |
|
#14
|
||||
|
||||
|
Quote:
1. lack of liabilty for the goverment employee 2. lack of training 3. lack of time 4. human error 5. complacency 6. short inspector 7. left tape measure in truck They admit around here that they only have time to look for problems that "jump out at them" |
|
#15
|
|||
|
|||
|
" The basement has sub-standard aspects that could imply that the work was done without a permit. Some of the conditions observed include low head clearance in the stairway, stair risers that do not conform to modern building practices and no source of heating or cooling in the rooms, I recommend that you check with the county building department to determine if permits were issued, signed off on and a certificate of occupancy was issued." I also recommend that you consult with a licensed contractor with a view of having these conditions corrected because the costs of these corrections could effect your overall evaluation of the property."
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Where do I put the Aquarium? | mcyr | Structural Inspections | 3 | 11/6/07 3:05 PM |
| Electrical Questions - Please help | Adam Demarco | Electrical Inspections | 8 | 2/25/07 9:59 PM |
| HVAC ducts per room | bwooddell | Inspecting HVAC Systems | 3 | 7/27/06 9:36 AM |
| Exhaust fan in room with gas water heater and furnace | jweinberg | Inspecting HVAC Systems | 7 | 2/18/06 1:23 PM |