Need some help with understair protection. Correct me if I am wrong but there should be fireblocking below this stairway (see pictures).The open space is the floor joist area for the second floor. Better yet, I was under the impression if you were able to access the bottom of the stairway the walls and ceiling should be sheetrocked with 1/2" rock?
|
|
#2
|
||||
|
||||
|
James, you are correct but I'm not sure which code specifies those requirements.
Attachment 6280 Last edited by mboyett; 4/9/09 at 9:38 PM.. |
|
#3
|
||||
|
||||
|
R314.8 Under stair protection. Enclosed accessible space under stairs shall have walls, under stair surface and any soffits protected on the enclosed side with 1/2-inch (12.7 mm) gypsum board. Erby Crofutt B4U Close Home Inspections Georgetown, Kentucky KY Lic# HI-2041 www.b4uclose.com http://www.kentuckyradon.com Kentucky Home Inspections Kentucky Home Inspectors NACHI02090301 "LIKE" me on Facebook Kentucky Homeowner Resources @ http://www.kentuckyhomeinspections.com BLOG by Erby, The Central Kentucky Home Inspector Join Active Rain HERE |
|
#4
|
||||
|
||||
|
Erby, what Code is that from? The 2003 IRC section R314 deals with Foam Plastic Insulation not stairs.
|
|
#5
|
|||
|
|||
|
Please Note:
rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Never mind the drywall I don't like the way the stringer is attached to the floor joist. It appears as if the joist has been omitted.
|
|
#6
|
||||
|
||||
|
It is R311.2.2
Greg Bell Titusville, Fl 02111507 Serving Central Florida
|
|
#7
|
||||
|
||||
|
Yep, there it is...thanks, Greg. Not sure why I didn't see that earlier.
Last edited by mboyett; 10/24/06 at 11:46 PM.. |
|
#8
|
||||
|
||||
|
The quote is from the current Kentucky Residential Code 2002 which is based on the IRC 2000.
We're kinda ahead of the times here in Kentucky. Next year we're supposed to adopt the 2007 Kentucky Residential Code based on the 2003 IRC. We're kinda ahead of the times here in Kentucky. Erby Crofutt B4U Close Home Inspections Georgetown, Kentucky KY Lic# HI-2041 www.b4uclose.com http://www.kentuckyradon.com Kentucky Home Inspections Kentucky Home Inspectors NACHI02090301 "LIKE" me on Facebook Kentucky Homeowner Resources @ http://www.kentuckyhomeinspections.com BLOG by Erby, The Central Kentucky Home Inspector Join Active Rain HERE |
|
#9
|
||||
|
||||
|
It is the same wording just a different code reference.
Greg Bell Titusville, Fl 02111507 Serving Central Florida
|
|
#10
|
|||
|
|||
|
Please Note:
jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
House is only two years old and built by a large builder. I like to know how they get away with so much. Thanks for everyones help.
|
|
#11
|
||||
|
||||
|
Quote:
Just graphics Raymond, ha. ha. Here is a better graphic. http://www.shalla.net/ LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#12
|
|||
|
|||
|
Please Note:
jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Would there be any exceptions to this rule? For example, if the underside of the stairwell is accessible thru the garage. I cant find anything that this would be allowed.
|
|
#13
|
||||
|
||||
|
If it were accessible through the garage, the garage "firewall" separation requirements would also come into play.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#14
|
|||
|
|||
|
Please Note:
jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
It was accessible thru the garage and the the door into the stairwell was not rated. I did note the door and defer this area for further evaluation. Thanks
|
|
#15
|
|||
|
|||
|
Please Note:
rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Why recommend drywalling over what appears to be improper framing and attachment of the stringer? Is the stair improperly attached? In my opinion drywalling is the secondary concern. Why recommend covering a framing issue with firewall under the guise of fire rating, you cannot omit one problem over that of another, or am I missing something?
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 7 | 4/16/12 9:51 PM |
| Gas line protection | jlybolt | Exterior Inspections | 2 | 5/30/07 12:18 PM |
| Article 240 : Overcurrent Protection Article | pabernathy | Electrical Inspections | 0 | 5/23/07 11:40 AM |
| Lightning Protection Systems- Do You Check It? | pabernathy | Electrical Inspections | 20 | 12/29/06 9:38 PM |
| Electrical Inspection Training for Home Inspectors | jtedesco1 | Inspection Education & Training | 6 | 4/27/06 10:43 PM |