Default Is it 1/0 or 2/0 copper main?

also this panel has few breakers for a 200 amp main. Is the size of the main going to be an issue?
Attached Thumbnails
1-0-2-0-copper-main-dsc01383.jpg   1-0-2-0-copper-main-dsc01384.jpg   1-0-2-0-copper-main-dsc01379.jpg  



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
Need a home inspection in Illinois? Check out InterNACHI's listing of Illinois certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/28/10, 12:11 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is it 1/0 or 2/0 copper main?

Was there a disconnect ahead of this panel?

Why do you think that 16 breakers is too few?
Reply With Quote
  #3  
Old 4/28/10, 1:27 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: Is it 1/0 or 2/0 copper main?

No there was no disconnect ahead.

I gave it some more thought and am not sure why I am concerned about the number of breakers.



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #4  
Old 4/28/10, 2:17 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is it 1/0 or 2/0 copper main?

Hard to tell, but those look like #1 AGW wires, which would be too small for a 200 amp breaker.
Reply With Quote
  #5  
Old 4/28/10, 4:06 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is it 1/0 or 2/0 copper main?

For a 200 dwelling service {NEC Table 310.15(B)(6)} you are permitted to use #2/0 Cu or #4/0 Al conductors. That appears to be neither. Also the several equipment grounding conductors under one lug is also a violation.
Reply With Quote
  #6  
Old 4/28/10, 4:47 PM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: Is it 1/0 or 2/0 copper main?

As well as the lug has been installed with a sheet metal screw.



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Light Switch Near Shower vsantos Electrical Inspections 204 3/19/12 9:58 AM
Total galvanic reaction? jtribuzio Plumbing Inspections 19 4/3/10 2:18 AM
Looking for comment by Caoimhín P. Connell phinsperger Ancillary Inspection Services & Additional Topics 2 2/18/06 11:22 AM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 5:11 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts