also this panel has few breakers for a 200 amp main. Is the size of the main going to be an issue?
Richard W. Washington, owner RW Home Inspections, Inc. www.RWHOMEINSPECTIONS.com Texas Real Estate Commission (TREC) Professional Inspector License #7238 Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter InterNACHI member since 2004 Based in Katy, serving Houston and all surrounding communities |
| Need a home inspection in Illinois? Check out InterNACHI's listing of Illinois certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Was there a disconnect ahead of this panel?
Why do you think that 16 breakers is too few? |
|
#3
|
||||
|
||||
|
No there was no disconnect ahead.
I gave it some more thought and am not sure why I am concerned about the number of breakers.
Richard W. Washington, owner RW Home Inspections, Inc. www.RWHOMEINSPECTIONS.com Texas Real Estate Commission (TREC) Professional Inspector License #7238 Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter InterNACHI member since 2004 Based in Katy, serving Houston and all surrounding communities |
|
#4
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Hard to tell, but those look like #1 AGW wires, which would be too small for a 200 amp breaker.
|
|
#5
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
For a 200 dwelling service {NEC Table 310.15(B)(6)} you are permitted to use #2/0 Cu or #4/0 Al conductors. That appears to be neither. Also the several equipment grounding conductors under one lug is also a violation.
|
|
#6
|
|||
|
|||
|
As well as the lug has been installed with a sheet metal screw.
1st Inspection Services Bruce M. Graham III Gainesville, FL 32608 352 871 8989 Florida Licensed Home Inspector #HI10 Radon Measurment Technician # R2279 NACHI05091592 ICC 5268478 www.1stinspectionsfl.com www.bungalowstomansions.com |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Light Switch Near Shower | vsantos | Electrical Inspections | 204 | 3/19/12 9:58 AM |
| Total galvanic reaction? | jtribuzio | Plumbing Inspections | 19 | 4/3/10 2:18 AM |
| Looking for comment by Caoimhín P. Connell | phinsperger | Ancillary Inspection Services & Additional Topics | 2 | 2/18/06 11:22 AM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |