Old 6/16/09, 12:08 AM
Scott Schultz Scott Schultz is offline
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default 1/0 awg with 200 amp main breaker
I've noticed that when i inspected houses in the 10 year old range and older, I'm seeing the 200 amp main breaker protecting a 1/0 awg SEC. NEC currently states 2/0 awg for this size breaker and I guess that it used to be 1/0 at some point? anyway, I have been recommending that an electrician take a look and make a recommendation, whether it's ok or it should be upgraded. Is this the right call to make? My head tells me it's improper according to today's guidelines. What's your call?
Thanks
Find an InterNACHI certified Massachusetts Home Inspector (and anywhere else in North America)
Old 6/16/09, 8:03 AM
Default Re: 1/0 awg with 200 amp main breaker
Thanks
It is wrong whether it is AL (#4/0 needed) or CU (#2/0 needed).
Larry Kage, CMI
231 929 3525
Old 6/16/09, 8:34 AM
Jim Port Jim Port is offline
Unmoderated Guest
What was probably done was the panel was changed out to a larger size but the wires feeding it were not. If there is a properly sized OCP ahead of these you would be fine. The interior main breaker would just be a redundant means to shut down the panel. If there is no OCP ahead of the panel, defer for correction.
Old 6/16/09, 9:40 AM
mnahrgang's Avatar
Not saying that 1 awg coming into the panel is correct, but isn't the 200AMP breaker AFTER the SEC? It's a shutoff that is protecting everything downstream from it. The SEC is bringing power to the breaker, not from it. If the SEC is protected at all, I would think that would be at the pole. Please correct me if I'm wrong.
Mark Nahrgang
www.HeyMark.info
Old 6/16/09, 10:14 AM
Bear in mind that the size of the SEC (from the 'pole' to the house) is determined by the PoCo, not the NEC.
Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Old 6/16/09, 10:26 AM
Unmoderated Guest
Marc,
The overcurrent protection is preventing too much current from flowing through the service entrance conductors.
Imagine feeding this panel with #6. Would the breaker properly protect the wire before it burned up? The breaker would not protect anything as it would not trip until over 200 amps were flowing through it. By that time the wires would have have overheated and potentially caused a fire.
Old 6/16/09, 10:45 AM
I think that he just used the wrong term. By his descrip, he's talking about the load side of the meter. But, yes the SEC's are protected at the transformer.
Jeff
Jeff Wicklander
Corwick Home Services
Join my business on Facebook
Old 6/16/09, 10:54 AM
Unmoderated Guest
Jeff
Sorry Jeff,
The cables before a main breaker or disconnecting means are unfused for all practical purposes. The fusing levels for a transformer are sized for the entire load served, not the individual load of a house served by that transformer.
This is the reason that the NEC requires the cables to be "as short as practical" inside a house without being fused.
Old 6/16/09, 12:21 PM
Yes, the entire transformer itself is protected for all the loads coming off of it. Actually, I knew this but I had a temporary brainfart.
Jeff
Jeff Wicklander
Old 6/16/09, 12:48 PM
Jeffrey R. Pope's Avatar
This type of set up should be reported as a 100 amp service capacity, regardless of the breaker rating. The SEC has effectively reduced the maximum capacity of the residence.
If this were my inspection, I would certainly suggest replacing the SEC or reducing the service disconnect to 100 amps.
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Old 6/20/09, 1:15 AM
BINGO......give this man a PRIZE.
The conductors on the load side of the meter and for that much the conductors on the load side of the service point at the drip loop is under the guidelines of the NEC. So if you have a conductor going to a breaker in the main panel and the breaker i sized larger then the SEC feeding it....most certainly a problem that needs to be reported and let your client choose to what level of acceptance they choose to live with...you have done your job.
Paul W. Abernathy
Old 6/20/09, 9:20 AM
mnahrgang's Avatar
Paul,
What is the concern in this situation? I had a similar situation yesterday with a 100 Amp service that had a 125 Amp main breaker. I simply told the client that it was a 100 Amp service, and not 125.
Mark Nahrgang
www.HeyMark.info
Old 6/20/09, 9:44 AM
Well...what size were the conductors? Are they rated to handle 125A of potential current safely based on 310.15(B)(6) or are they sized per 310.16 from your visual observation?. Do you know the actual load....probably not so we have to take it at its face value.
Paul W. Abernathy
Old 6/20/09, 12:34 PM
mnahrgang's Avatar
From the meter to the panel it was #2 Alum. That was the smalled component, so that is why I defined it as a 100 Amp service. The main breaker in the panel was 125 amps.
Mark Nahrgang
www.HeyMark.info
Old 6/20/09, 1:27 PM
The reality is the 2 AWG is only good for 100A as you have stated. You put on the report the capacity but their is another issue...you provided the weakest link but the new issue is the se conductors are not rated for 125A...that would need a 1/0 minimum based on 310.15(B)(6). so this should also go on the report.
Paul W. Abernathy
200 main breaker X 2 sfalvey Electrical Inspections 11 10/9/08 11:31 PM
main Breaker vriverajr Electrical Inspections 5 1/2/08 10:52 AM
Arching Causes Main Breaker To Trip? msylvester Electrical Inspections 10 10/22/07 3:57 PM