Default 1/0 awg with 200 amp main breaker

I've noticed that when i inspected houses in the 10 year old range and older, I'm seeing the 200 amp main breaker protecting a 1/0 awg SEC. NEC currently states 2/0 awg for this size breaker and I guess that it used to be 1/0 at some point? anyway, I have been recommending that an electrician take a look and make a recommendation, whether it's ok or it should be upgraded. Is this the right call to make? My head tells me it's improper according to today's guidelines. What's your call?

Thanks
Reply With Quote
Find an InterNACHI certified Connecticut Home Inspector (and anywhere else in North America)
  #2  
Old 6/16/09, 9:03 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,734
Default Re: 1/0 awg with 200 amp main breaker

Quote:
Originally Posted by Scott Schultz View Post
I've noticed that when i inspected houses in the 10 year old range and older, I'm seeing the 200 amp main breaker protecting a 1/0 awg SEC. NEC currently states 2/0 awg for this size breaker and I guess that it used to be 1/0 at some point? anyway, I have been recommending that an electrician take a look and make a recommendation, whether it's ok or it should be upgraded. Is this the right call to make? My head tells me it's improper according to today's guidelines. What's your call?

Thanks
It is wrong whether it is AL (#4/0 needed) or CU (#2/0 needed).



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #3  
Old 6/16/09, 9:34 AM
Jim Port Jim Port is offline
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 285
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 1/0 awg with 200 amp main breaker

What was probably done was the panel was changed out to a larger size but the wires feeding it were not. If there is a properly sized OCP ahead of these you would be fine. The interior main breaker would just be a redundant means to shut down the panel. If there is no OCP ahead of the panel, defer for correction.
Reply With Quote
  #4  
Old 6/16/09, 10:40 AM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is online now
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,951
Default Re: 1/0 awg with 200 amp main breaker

Not saying that 1 awg coming into the panel is correct, but isn't the 200AMP breaker AFTER the SEC? It's a shutoff that is protecting everything downstream from it. The SEC is bringing power to the breaker, not from it. If the SEC is protected at all, I would think that would be at the pole. Please correct me if I'm wrong.
Reply With Quote
  #5  
Old 6/16/09, 11:14 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 505
Default Re: 1/0 awg with 200 amp main breaker

Bear in mind that the size of the SEC (from the 'pole' to the house) is determined by the PoCo, not the NEC.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #6  
Old 6/16/09, 11:26 AM
Jim Port Jim Port is offline
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 285
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 1/0 awg with 200 amp main breaker

Marc,

The overcurrent protection is preventing too much current from flowing through the service entrance conductors.

Imagine feeding this panel with #6. Would the breaker properly protect the wire before it burned up? The breaker would not protect anything as it would not trip until over 200 amps were flowing through it. By that time the wires would have have overheated and potentially caused a fire.
Reply With Quote
  #7  
Old 6/16/09, 11:45 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Libertyville, Il
Posts: 448
Default Re: 1/0 awg with 200 amp main breaker

Quote:
Originally Posted by mnahrgang View Post
Not saying that 1 awg coming into the panel is correct, but isn't the 200AMP breaker AFTER the SEC? It's a shutoff that is protecting everything downstream from it. The SEC is bringing power to the breaker, not from it. If the SEC is protected at all, I would think that would be at the pole. Please correct me if I'm wrong.
I think that he just used the wrong term. By his descrip, he's talking about the load side of the meter. But, yes the SEC's are protected at the transformer.

Jeff



Jeff Wicklander
Corwick Home Services
224-715-0457
Reply With Quote
  #8  
Old 6/16/09, 11:54 AM
Jim Port Jim Port is offline
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 285
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 1/0 awg with 200 amp main breaker

Quote:
Originally Posted by jwicklander View Post
I think that he just used the wrong term. By his descrip, he's talking about the load side of the meter. But, yes the SEC's are protected at the transformer.

Jeff
Sorry Jeff,

The cables before a main breaker or disconnecting means are unfused for all practical purposes. The fusing levels for a transformer are sized for the entire load served, not the individual load of a house served by that transformer.

This is the reason that the NEC requires the cables to be "as short as practical" inside a house without being fused.
Reply With Quote
  #9  
Old 6/16/09, 1:21 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Libertyville, Il
Posts: 448
Default Re: 1/0 awg with 200 amp main breaker

Yes, the entire transformer itself is protected for all the loads coming off of it. Actually, I knew this but I had a temporary brainfart.

Jeff



Jeff Wicklander
Corwick Home Services
224-715-0457
Reply With Quote
  #10  
Old 6/16/09, 1:48 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: 1/0 awg with 200 amp main breaker

This type of set up should be reported as a 100 amp service capacity, regardless of the breaker rating. The SEC has effectively reduced the maximum capacity of the residence.

If this were my inspection, I would certainly suggest replacing the SEC or reducing the service disconnect to 100 amps.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #11  
Old 6/20/09, 2:15 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: 1/0 awg with 200 amp main breaker

Quote:
Originally Posted by jpope View Post
This type of set up should be reported as a 100 amp service capacity, regardless of the breaker rating. The SEC has effectively reduced the maximum capacity of the residence.

If this were my inspection, I would certainly suggest replacing the SEC or reducing the service disconnect to 100 amps.
BINGO......give this man a PRIZE.

The conductors on the load side of the meter and for that much the conductors on the load side of the service point at the drip loop is under the guidelines of the NEC. So if you have a conductor going to a breaker in the main panel and the breaker i sized larger then the SEC feeding it....most certainly a problem that needs to be reported and let your client choose to what level of acceptance they choose to live with...you have done your job.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 6/20/09, 10:20 AM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is online now
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,951
Default Re: 1/0 awg with 200 amp main breaker

Quote:
Originally Posted by pabernathy View Post
BINGO......give this man a PRIZE.

The conductors on the load side of the meter and for that much the conductors on the load side of the service point at the drip loop is under the guidelines of the NEC. So if you have a conductor going to a breaker in the main panel and the breaker i sized larger then the SEC feeding it....most certainly a problem that needs to be reported and let your client choose to what level of acceptance they choose to live with...you have done your job.
Paul,
What is the concern in this situation? I had a similar situation yesterday with a 100 Amp service that had a 125 Amp main breaker. I simply told the client that it was a 100 Amp service, and not 125.
Reply With Quote
  #13  
Old 6/20/09, 10:44 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: 1/0 awg with 200 amp main breaker

Well...what size were the conductors? Are they rated to handle 125A of potential current safely based on 310.15(B)(6) or are they sized per 310.16 from your visual observation?. Do you know the actual load....probably not so we have to take it at its face value.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Find an InterNACHI certified Connecticut Home Inspector (and anywhere else in North America)
  #14  
Old 6/20/09, 1:34 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is online now
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,951
Default Re: 1/0 awg with 200 amp main breaker

Quote:
Originally Posted by pabernathy View Post
Well...what size were the conductors? Are they rated to handle 125A of potential current safely based on 310.15(B)(6) or are they sized per 310.16 from your visual observation?. Do you know the actual load....probably not so we have to take it at its face value.
From the meter to the panel it was #2 Alum. That was the smalled component, so that is why I defined it as a 100 Amp service. The main breaker in the panel was 125 amps.
Reply With Quote
  #15  
Old 6/20/09, 2:27 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: 1/0 awg with 200 amp main breaker

The reality is the 2 AWG is only good for 100A as you have stated. You put on the report the capacity but their is another issue...you provided the weakest link but the new issue is the se conductors are not rated for 125A...that would need a 1/0 minimum based on 310.15(B)(6). so this should also go on the report.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
200 main breaker X 2 sfalvey Electrical 11 10/10/08 12:31 AM
main Breaker vriverajr Electrical 5 1/2/08 11:52 AM
Arching Causes Main Breaker To Trip? msylvester Electrical 10 10/22/07 4:57 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 2:52 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts