Default Re: 1/0 awg with 200 amp main breaker

Quote:
Originally Posted by pabernathy View Post
The reality is the 2 AWG is only good for 100A as you have stated. You put on the report the capacity but their is another issue...you provided the weakest link but the new issue is the se conductors are not rated for 125A...that would need a 1/0 minimum based on 310.15(B)(6). so this should also go on the report.
So if the meter is rectangular (200 Amps), and the main breaker is 125 Amps: The sec (between the two) which is rated at 100 Amps is too small? And that is an issue correct? What is the potential harm in such a layout? (The house was 60 years old.)
Reply With Quote
Find an InterNACHI certified Connecticut Home Inspector (and anywhere else in North America)
  #17  
Old 6/20/09, 7:40 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: 1/0 awg with 200 amp main breaker

The potential harm is that you could over-load the SEC without tripping the service breaker.

The house could be drawing nearly 125 amps (throughout its circuits or in a short-circuit condition) and not trip the breaker. The SEC (rated at 100 amps) is your "weak link," and could burn up.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #18  
Old 7/27/09, 9:05 PM
Michael M. Mixson's Avatar
Michael M. Mixson Michael M. Mixson is offline
InterNACHI Member
 
Join Date: May 2009
Posts: 22
Default 1/0 awg with 200 amp main breaker

Guys I've run across something similar on new construction this afternoon. Maybe I'm just and idiot, and that's probably the case, but the panel is rated 200, the main disconnect is 200 and the underground service entry is 1/0 Aluminum. Meter is not on but similar construction in the neighborhood is using a meter rated for 200 amps. Here's the pic?? What am I missing besides some brain matter?
Attached Thumbnails
1-0-american-wire-guage-200-amp-main-breaker-133.jpg   1-0-american-wire-guage-200-amp-main-breaker-135.jpg  
Reply With Quote
  #19  
Old 7/27/09, 9:36 PM
Jim Port Jim Port is offline
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 285
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 1/0 awg with 200 amp main breaker

Are you are asking about the conductors coming from the underground to feed the meter? If so these are sized by the power company, which operates under a different set of rules than the NEC.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
200 main breaker X 2 sfalvey Electrical 11 10/10/08 12:31 AM
main Breaker vriverajr Electrical 5 1/2/08 11:52 AM
Arching Causes Main Breaker To Trip? msylvester Electrical 10 10/22/07 4:57 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 12:29 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts