#16
|
||||
|
||||
|
Quote:
Mark Nahrgang www.DaytonSpringfieldHomeInspector.com www.HeyMark.info Home Inspections for Springfield, Dayton, and surrounding OH areas. |
| Find an InterNACHI certified North Carolina Home Inspector (and anywhere else in North America) |
|
#17
|
||||
|
||||
|
The potential harm is that you could over-load the SEC without tripping the service breaker.
The house could be drawing nearly 125 amps (throughout its circuits or in a short-circuit condition) and not trip the breaker. The SEC (rated at 100 amps) is your "weak link," and could burn up. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#18
|
||||
|
||||
|
Guys I've run across something similar on new construction this afternoon. Maybe I'm just and idiot, and that's probably the case, but the panel is rated 200, the main disconnect is 200 and the underground service entry is 1/0 Aluminum. Meter is not on but similar construction in the neighborhood is using a meter rated for 200 amps. Here's the pic?? What am I missing besides some brain matter?
|
|
#19
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Are you are asking about the conductors coming from the underground to feed the meter? If so these are sized by the power company, which operates under a different set of rules than the NEC.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| 200 main breaker X 2 | sfalvey | Electrical Inspections | 11 | 10/10/08 12:31 AM |
| main Breaker | vriverajr | Electrical Inspections | 5 | 1/2/08 11:52 AM |
| Arching Causes Main Breaker To Trip? | msylvester | Electrical Inspections | 10 | 10/22/07 4:57 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 10:26 PM |