I know this issue was covered in another thread so my apologies straight away I feel like I'm going crazy. I ran across this issue on new construction. Not something I'm inpsecting I'm just nosing aroung my neighborhood and this caught my interest. Maybe I'm just and idiot, and that's probably the case, but the panel is rated 200, the main disconnect is 200 and the underground service entry is 1/0 Aluminum. Meter is not on but similar construction in the neighborhood is using a meter rated for 200 amps. Here's the pic?? What am I missing besides some brain matter? Is this a PoCo issue? Even if it is, can this arrangement be correct??
Attached Thumbnails
1-0-service-entry-200-amp-panel-133.jpg   1-0-service-entry-200-amp-panel-135.jpg  

Last edited by mmixson; 7/27/09 at 8:15 PM.. Reason: added pics
Reply With Quote
Find an InterNACHI certified Maryland Home Inspector (and anywhere else in North America)
  #2  
Old 7/27/09, 9:09 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 1/0 Service Entry on 200 amp Panel

It is not uncommon for the POCO to install conductors way smaller than we would use if sized per the NEC. With that said the SE Conductors should be protected at their ampacity. If they used 310.15(B)(6) then 1/0CU would be good for 175A but I would expect to see the panel OCPD not to exceed 175A.

So with that said.....who actually ran the SE Conductors as usualy the POCO does not do this until after the load side of the meter has been hooked up.

So in reality the conductors from the load side of the meter to the service disconnect should be sized properly to the OCPD. If the service conductors are rated a 175A then the OCPD should not exceed the 175A in this example.



Paul W. Abernathy

Last edited by pabernathy; 7/27/09 at 9:15 PM..
Reply With Quote
  #3  
Old 7/27/09, 9:25 PM
mmixson's Avatar
mmixson mmixson is offline
InterNACHI Member
 
Join Date: May 2009
Posts: 23
Default Re: 1/0 Service Entry on 200 amp Panel

Paul, thank you very much. I'm in the middle of viewing your NACHI TV electrical inspection course which I must say is OUTSTANDING. Thanks again.
Reply With Quote
  #4  
Old 7/27/09, 9:32 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 1/0 Service Entry on 200 amp Panel

Glad you like it Michael.....Enjoy !



Paul W. Abernathy
Reply With Quote
  #5  
Old 7/27/09, 9:37 PM
mmixson's Avatar
mmixson mmixson is offline
InterNACHI Member
 
Join Date: May 2009
Posts: 23
Default Re: 1/0 Service Entry on 200 amp Panel

Almost missed one your points, you mentioned 175A using copper. In this example I'm observing Aluminum, that only compounds the problem correct?
Reply With Quote
  #6  
Old 7/27/09, 10:16 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 1/0 Service Entry on 200 amp Panel

Yes....it means the SE Conductors are rate even less than we thought. Remember now we cn't govern the POCO and what they install. We can only wait to see what is actually run to the Service Disconnect. If the electrical contractor runs in 4/0AL or 2/0CU then they would be fine......unless of course the electrical contractor ran the underground SE Conductors...then it would not be outside the scope of the NEC because it is not under exclusive control of the POCO...then we have problems.



Paul W. Abernathy
Reply With Quote
  #7  
Old 7/27/09, 10:22 PM
mmixson's Avatar
mmixson mmixson is offline
InterNACHI Member
 
Join Date: May 2009
Posts: 23
Default Re: 1/0 Service Entry on 200 amp Panel

Paul thanks again. For those of us who think we're comfortable with electrical inspections, I would still advise you to take advantages of Paul's expertise in the Nachi TV inspection course. Everyone can benefit to some degree no matter what your level of comfort with this topic.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Breakers in Challenger Service Panel bhartley Electrical Inspections 2 2/3/09 9:35 PM
Electrical Safety Foundation International Links jtedesco1 Electrical Inspections 5 12/8/07 3:10 PM
Service wire size to breaker panel sfalvey Electrical Inspections 12 10/31/06 4:28 PM
Zinsco Service Disconnect Panel pdickerson Electrical Inspections 7 9/16/06 11:59 AM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 4:29 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts