Default 1 service drop 2 service entrance

I have never seen this before. Any reason this is a problem? This is a strata complex. There is a 60 AMP rating on the service box. Thanks.
Attached Thumbnails
1-service-drop-2-service-entrance-dscf1817-medium-.jpg.JPG
Views:	169
Size:	78.9 KB
ID:	29421   1-service-drop-2-service-entrance-dscf1818-medium-.jpg.JPG
Views:	117
Size:	114.5 KB
ID:	29422   1-service-drop-2-service-entrance-dscf1801-medium-.jpg.JPG
Views:	90
Size:	45.6 KB
ID:	29423  
Reply With Quote
Find an InterNACHI certified Ohio Home Inspector (and anywhere else in North America)
  #2  
Old 6/20/09, 1:37 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: 1 service drop 2 service entrance

Parallel service - no issue based on your pictures. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 6/21/09, 11:13 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 1 service drop 2 service entrance

It is still a single service drop as the Popester has indicated.....just so happens they are running two different lines down which could mean many things....(2) different occupancies on a single service drop, or a par. drop for a single building...in any case it is typically fine.

Now the only potential issues I might note ( but cant see in the image real well ) is that the connection points need to be below the service head ( 230.53(E) )



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Service Drop Q alarsen1 Electrical Inspections 11 2/25/07 10:45 AM
Service Drop Was Finally Removed! jtedesco1 Electrical Inspections 1 12/1/06 3:40 AM
Service Entrance jcampbell Electrical Inspections 9 10/30/06 1:14 AM
Service Drop and SEC jpope Electrical Inspections 11 1/15/06 12:15 AM
Service entrance conductor jjackson Electrical Inspections 30 1/7/06 6:05 AM


All times are GMT -4. The time now is 3:53 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts