#1
|
|||
|
|||
|
I run into this often. #10 wire on a 40-amp breaker which powers the A/C condenser unit. By code, 40-amp breakers should have #8 wire or larger. I've been told that when its for an A/C that #10 on a 40 is OK since you only need it for starting current of the compressor.
Is this allowed by code? Is it simply accepted in practice? Or is it not accepted? Thanks, Mike |
|
#2
|
||||
|
||||
|
Look at the data plate on the condenser. It will state the max and minimum breaker size per the manufacturer. As long as the wiring size covers the minimum required breaker size, you are ok.
The data plate will probably say something like this: Max overcurrent protection: 40 amps Min circuit ampacity: 28.5 amps Wiring for these motor circuits are sized differently. "The manufacturer has already calculated the conductor size to be based on the total of all of the motor loads in the combination-load equipment times 125 percent. It is not necessary to do these calculations again. For this type of equipment, the installer and the inspector only have to install and verify that the branch-circuit conductors supplying the equipment have an ampacity equal to or greater than the minimum circuit ampacity marked on the nameplate of the equipment." Last edited by awalters; 2/15/06 at 10:45 AM.. |
|
#3
|
|||
|
|||
|
Andrew,
Thanks for the info. Mike |
|
#4
|
|||
|
|||
|
Yeppers.....Got here late on this one.....Nicely Done Andrew......saved me from going into alot of additional detail...
Always refer to the Name Plate...... Paul W. Abernathy 1-703-825-5235 * If you need me.....call me. Disclaimer - All my posts on this forum are of my own personal opinion and in no way represent the opinions of any association, organization or affiliation. The voices in my head are mine and mine alone. |
|
#5
|
|||
|
|||
|
Please Note:
billy6139 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Seems to me, if you had a fault in the circuit(a slight short) the # 10 wire could draw 125% of 40 amps without tripping the breaker causing the conductor to overheat and possible threat of fire.I was always under the impression you could never put a conductor on less rated ampacity than the overprotection device.
|
|
#6
|
|||
|
|||
|
Quote:
|
|
#7
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
You have to remember there are two levels of protection of a circuit. You have short circuit protection and overload protection. In most cases both are taken care of by the branch circuit O/C device (fuse/breaker for you home gamers)
In the case of a larger motor based appliance you can have overLOAD protection in the motor starter or thermal protection in the motor. This is what keeps the wire from burning up. Short circuit protection is going to be at a much higher level, typically 175% of full load amps, in the case of a motor. They are recognizing that a short circuit will draw a huge amount of current, compared to the safe normal load. Another example of this principle is an 18ga lamp cord or fixture wire. Since the load is limited by the light sockets or other equipment installed, you can't burn up the cord with an overload but an 18ga in limited length has the ampacity to operate the 15/20a O/C device if you have a short. Of course you can still overload this circuit if you put in a medium base to receptacle adapter or hook up a 1440w heater on a 18-16ga extension cord, but nothing is idiot proof. |
|
#8
|
||||
|
||||
|
Quote:
- Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
|
#9
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
I am surprised an adapter from medium base bulb socket to NEMA 1-15R even exists. It can be the biggest potential hazard I can think of, using "listed" equipment you can buy at the Piggly Wiggly.
|
|
#10
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#11
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Changing a breaker is not something a teenage girl is likely to do. Plugging her hair dryer into the sconce above her bed, using one of these adapters, is more likely.
|
|
#12
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
ok how about a hair dryer plugged into a socket adapter screwed into a sconce wired with #14 connected to a 30 amp breaker installed by Pop.
|
|
#13
|
|||
|
|||
|
Quote:
|
|
#14
|
||||
|
||||
|
Quote:
|
|
#15
|
||||
|
||||
|
Quote:
NACHI 2005 U.S. Member of the Year
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 7 | 4/16/12 9:51 PM |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Ground wire in neutral bar, neutral to breaker, hot to ground? | rmc3inspection | Electrical Inspections | 4 | 8/1/06 9:44 AM |
| wire gauge / breaker rating | jweinberg | Electrical Inspections | 19 | 7/16/06 4:36 PM |