Default 100 amp Service w/new 200 amp panel

Inspected an older house yesterday that has a 100 amp service with 2 awg aluminum service entrance cable going into a small 100 amp service panel with no main disconnect.

The current owner, who appears to have done the wiring himself, has now installed a new 200 amp panel, with 200 amp main disconnect next to the old 100 amp panel. He has connected the feed to the new 200 amp panel directly to the main terminal lugs of the old 100 amp panel, eliminated distribution to the house from the old 100 amp panel and essentially made the 100 amp panel a junction box for the 200 amp panel. All distribution to the house now goes out from the 200 amp panel via the original 100 amp service panel.

Am I correct in my thinking that this is an incorrect application? Shouldn't the main disconnect be 100 amp or else upgrade the entrance cable to 4/0 awg and overall service to 200 amp?



Mark
MD HI Lic # 30090
PA DEP Radon Cert # 2457
Certified Home Energy Tune-uP Inspector
Reply With Quote
  #2  
Old 2/1/08, 8:02 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 100 amp Service w/new 200 amp panel

I think it's fair to say that in the areas in which you inspect, the power companies (not the local jurisdictions) require an inspection after modifications to the service equipment. I think it is also fair to say that this work was done without the benefit of such inspections. This can lead to the new owners getting their power shut off without notice. Just a head's up on that. Oh, and by the way... what he's done there is not proper, and it doesn't sound like he changed the meter can either. That has a max rating too.
Reply With Quote
  #3  
Old 2/1/08, 8:17 AM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: 100 amp Service w/new 200 amp panel

Am I correct in my thinking that this is an incorrect application? YES

Shouldn't the main disconnect be 100 amp or else upgrade the entrance cable to 4/0 awg and overall service to 200 amp? Dont they believe in permits where you live. That whole system is wrong. I always recommend that the client check for permits for any upgrades that are done. In this case it will just make your case stronger for replacement. You are looking at one hell of a potential fire hazard there, not to mention other numerous violations (I'm sure)
Reply With Quote
  #4  
Old 2/1/08, 8:41 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 100 amp Service w/new 200 amp panel

Please post some pictures of this installation.
Reply With Quote
  #5  
Old 2/1/08, 10:03 AM
Joseph Hagarty's Avatar
Joseph Hagarty Joseph Hagarty is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 3,434
Default Re: 100 amp Service w/new 200 amp panel

Quote:
Originally Posted by wsiegel
Dont they believe in permits where you live....
Most areas of Pennsylvania do not require municipal permitting and inspections.

Electricians also are not required to be trained, licensed or insured by the State of PA.



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #6  
Old 2/1/08, 10:07 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,630
Default Re: 100 amp Service w/new 200 amp panel

Am I correctly understanding from your description that the main disconnects are downstream from the branch circuit disconnects --- or that the main disconnects, upstream from the barnch circuits, are 200 amp?
Reply With Quote
  #7  
Old 2/1/08, 1:30 PM
Mark R. Long Mark R. Long is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Thurmont, MD
Posts: 320
Default Re: 100 amp Service w/new 200 amp panel

Quote:
Originally Posted by Marc D. Shunk
I think it's fair to say that in the areas in which you inspect, the power companies (not the local jurisdictions) require an inspection after modifications to the service equipment. I think it is also fair to say that this work was done without the benefit of such inspections. This can lead to the new owners getting their power shut off without notice. Just a head's up on that. Oh, and by the way... what he's done there is not proper, and it doesn't sound like he changed the meter can either. That has a max rating too.
No the meter can was not changed either. There were enough other electrical issues that evaluation by an electrician was warranted even without this particular issue, but I just wanted to double check my thinking on this item. Thanks, Marc.



Mark
MD HI Lic # 30090
PA DEP Radon Cert # 2457
Certified Home Energy Tune-uP Inspector
Reply With Quote
  #8  
Old 2/1/08, 1:40 PM
Mark R. Long Mark R. Long is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Thurmont, MD
Posts: 320
Default Re: 100 amp Service w/new 200 amp panel

Quote:
Originally Posted by jbushart
Am I correctly understanding from your description that the main disconnects are downstream from the branch circuit disconnects --- or that the main disconnects, upstream from the barnch circuits, are 200 amp?
No, the branch circuits are in the new 200 amp panel after the 200 amp disconnect. The 200 amp panel is being fed through the old 100 amp service panel, but the branch circuits in that panel have been eliminated. The old 100 amp service panel is now essentially a junction box (with no cover any where to be found, by the way). The service to the house appears to still be 100 amp.



Mark
MD HI Lic # 30090
PA DEP Radon Cert # 2457
Certified Home Energy Tune-uP Inspector
Reply With Quote
  #9  
Old 2/1/08, 1:42 PM
Mark R. Long Mark R. Long is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Thurmont, MD
Posts: 320
Default Re: 100 amp Service w/new 200 amp panel

Quote:
Originally Posted by jtedesco1
Please post some pictures of this installation.
I would have liked to do that, Joe, but I dropped my camera and blew out my flash and didn't have a spare camera. So my pictures in that area of the dank 100 year old basement were very dark. Have to go out and buy a new camera now. You just can't replace the bulb like in the old days.



Mark
MD HI Lic # 30090
PA DEP Radon Cert # 2457
Certified Home Energy Tune-uP Inspector
Reply With Quote
  #10  
Old 2/1/08, 1:48 PM
jbettencourt jbettencourt is offline
InterNACHI Member
 
Join Date: Oct 2007
Location: Stoney Creek, ON
Posts: 507
Default Re: 100 amp Service w/new 200 amp panel

Worst case scenario the cellphone camera can come in handy in a pinch. Not the greatest quality but will work in a jam.
Reply With Quote
  #11  
Old 2/7/08, 3:08 AM
Jon Randolph Jon Randolph is offline
New User
 
Join Date: Sep 2007
Location: Indianapolis, IN
Posts: 33
Please Note: Jon Randolph is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 100 amp Service w/new 200 amp panel

Was the supply for the "sub" panel protected in the main sevice panel by a 100 amp disconnect? Though it would be nice, the NEC does not require a disconnect in both panels.

Was the first 100 amp panel actually used as a "junction box" or was the 200 amp panel fed from a disconnect inside the 100 amp panel?

Sounds like the owner needed more circuits and added the 100 amp panel, then decided that it still wasn't enough and went for the 200 amp panel. Either way, it SHOULD be protected inside the original service equipment by a 100 amp disconnect. Simply adding a 200 amp panel after the main panel does not mean that you have 200 amp service at the home. For the service to have been upgraded to 200 amps, the SEC, meter and drop should hvave been changed out if they were not rated at 200 amps.

Yes, this is an "unconventional" installation and it would be better to be properly replaced with an panel appropritely sized to the service available to the home (or the service upgraded). However, a properly installed "sub" panel with a 200 amp main disconnect will not constitute a overcurrent hazard for the meter, SEC, service drop, etc. if it is protected by a disconnect properly sized for the lowest rating of all components involved, assuming that it is not double tapped prior to the main disconnect in the first panel. A 200 amp main in this panel, if protected by a 100 amp disconnect at the original source, would be nothing more than a big conductor that can carry more current that it will ever see.

Last edited by Jon Randolph; 2/7/08 at 3:54 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Service Panel Quiz? hmcclard Electrical 5 10/25/07 12:53 AM
Panel Inspection Safety roconnor Electrical 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 7:56 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts