Hi Guys,

When do you recommend upgrading from a 100 amp circuit breaker panel to a 200 amp ?
I just inspected a 1970 home with 1930 sq ft, someone just put in a new panel, but only a 100 amp. Why not just put in a 200 amp ?
Any general guidelines for amperage vs sq ft or other rules of thumb ?

Thanks,

Darrell Freshour
Darrells Home Inspections
Reply With Quote
  #2  
Old 10/17/07, 10:00 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 100 Amp vs 200 Amp

three watts per square foot plus other connected loads.

first 10kw at 100% and the rest at 40% plus heat and or AC
Reply With Quote
  #3  
Old 10/17/07, 11:16 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 100 Amp vs 200 Amp

To expand more on mikes reference....

1.) They can use a Standard Method or Optional Method.......Mike explains he optional method (220.82)which in most all cases is a less sized service than the standard method.

The good thing about electricity is diversification.......

Basically as an HI you need to understand that depending on whats in the dwelling will determine if the 100A service is large enough....if their is considerable gas appliances and so on 100A service may be fine.

If you see a 100A panel that has multiple double taps an just looks "SPACE CHALLENGED" inside then quite possibly it could stand a review.....but again this is something an electrician is going to have to do.

On a side note....It quite possibly was a 100A straight change over from an older fuse 100A....happens alot because they dont have to increase the SE conductors size....and in many cases the 100A will serve he dwelling fine.

So many varibles can come into play on this.......nothing can take the place of the actual calculations that a licensed electrician SHOULD be doing...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #4  
Old 10/17/07, 11:38 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,707
Send a message via Yahoo to jfunderburk
Default Re: 100 Amp vs 200 Amp

I would never recommend an upgrade unless you are a licensed electrician. I simply say that the amperage is 100 and that is considered the minimum necessary by today's modern homes and advise them to talk to a licensed electrician about the limitations of this type of service.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 10/17/07, 11:59 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 100 Amp vs 200 Amp

100 amp may be the futures 60 amp but as long as it is common at this time there is no reason to stir the pot during inspection.
Reply With Quote
  #6  
Old 10/17/07, 12:07 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 100 Amp vs 200 Amp

Quote:
Originally Posted by jfunderburk
I would never recommend an upgrade unless you are a licensed electrician. I simply say that the amperage is 100 and that is considered the minimum necessary by today's modern homes and advise them to talk to a licensed electrician about the limitations of this type of service.


Could you be talked into moving North East a couple of hundred miles?

You sound like my kind of HI.

Just did a call where the HI stated that the service needed an upgrade to a 200 amp service on a house that had a 150 amp service and the range, water heater and heat was gas. The house was 1550 square feet and the only appliances installed were a dishwasher, microwave and a dryer.

My recommendation was to leave everything alone. The calculated load came to 82 amps to the best of my recollection.
Reply With Quote
  #7  
Old 10/17/07, 12:09 PM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: 100 Amp vs 200 Amp

If I am in doubt, I perform a rough load calculation myself (the Codecheck Electrical has a great example page that will walk you through how to do it). I do not share the results of the calculation with the client, but if my load calc is close to or over the service capacity of the home, then I recommend that they consult with an electrician to determine if their service has adequate capacity. In a home that has gas heat, gas range, and gas hot water, 100 ams is almost always OK unless the home is huge.
Reply With Quote
  #8  
Old 10/17/07, 12:18 PM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: 100 Amp vs 200 Amp

Quote:
Originally Posted by Mike Whitt

The calculated load came to 82 amps to the best of my recollection.
Mike, I am surprised that it was that high with gas heat, hot water, and range.
Reply With Quote
  #9  
Old 10/17/07, 12:35 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 100 Amp vs 200 Amp

Quote:
Originally Posted by relliott
100 amp may be the futures 60 amp but as long as it is common at this time there is no reason to stir the pot during inspection.
Paul may confirm this but many 100 amp services (at 240V= 24,000 Watts) never get above 50-60 amps draw. So why think the home needs a 200 amp service if it has not been added to or had some major electrical appliance additions, like an electric kiln for pottery. Here we have electrically heated homes of 1500-1600 sq ft meeting code at 100 amps.

Better to size the entrance properly than to guess that it needs more power. I find many electricians way oversize the entrance here especially if there is some electric heat in the home, automatically go to 200 amps!! Probably 125 or 150 amps would have been adequate.

This is a waste of materials that may never get used......no wonder copper is up 300%+ and oil is $88 per barrel......conservation is a word that many do not have in their vocabulary. On the Fine Home Building forum, they call the large poorly built homes with all the fixins on oversized lots .....McMansions!!!
Reply With Quote
  #10  
Old 10/17/07, 12:40 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 100 Amp vs 200 Amp

Quote:
Originally Posted by Mike Whitt


My recommendation was to leave everything alone. The calculated load came to 82 amps to the best of my recollection.
That sounds quite high!! What else eelctrical was in the house?
Reply With Quote
  #11  
Old 10/17/07, 1:07 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 100 Amp vs 200 Amp

Yes, I have been in homes with a 320/400 service and had (2) ovens, (4) AC Units, (2) Sub-Zero fridges, and all lights on ( 125 Recess Lights ) and so on and everything you could think of plugged in and running....and only read about 185 A on the service......

Basically..it boils down to diversification of loads.......and thats a wonderful thing about electricity......The NEC is always going to be a cautious standard...meaning things are always a bit oversized.....take the difference between a standard calculation and an optional method calculation....can be a HUGE difference....and both quite legal.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #12  
Old 10/17/07, 2:16 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 100 Amp vs 200 Amp

To add another side to this discussion: some of the older (and newer) 100 amp panels don't have a whole lot of room in them for all the necessary circuits required today (new and remodeled homes). AFCI's take up a lot of space, lots of dedicated circuits etc. Sometimes having the bigger panel (given that costs aren't that different for the panels themselves) and all that extra room is worth the larger service regardless of the calculated load of the home.
Reply With Quote
  #13  
Old 10/17/07, 3:07 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 100 Amp vs 200 Amp

Quote:
Originally Posted by pdickerson
Mike, I am surprised that it was that high with gas heat, hot water, and range.
1550 x 3 = 4650
2 small appliance and laundry = 4500
Dryer = 5000
Microwave and dishwasher (estimate) 2400

Total of all the above = 16550

First 10000 at 100% = 10000

6550 at 40% = 2620


Total = 12620

Air conditioner at 7200

Total = 19820

19820 divided by 240 volts = 82.85

This 82.85 amp load is not what the service will draw all the time it is only the load that was calculated to size the service with.
Reply With Quote
  #14  
Old 10/17/07, 3:33 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 100 Amp vs 200 Amp

Charles,

Electrically speaking...nothing in the NEC says you have to size in regards for the future...in fact their is a myth that you must leave 10% of OCPD space in a panel for future installation...when in fact you can fill a panel to 100%.

It is important to take the dwelling at what it is at the time of inspection, if the house is finished and the panel was updated to the 100A and it runs all existing appliances and so on.......you can't force to future needs....as the buyer is buying what the see....not what they want....to see

I agree with you in that you need to make the statement that the panel may not be fine if the client plans on making changes and additions to the dwelling in the future...but as of right now unless you do a calculaion and qualified to do so.....the service may be fine even at 100A.....remember 100A is the minimum size required.

As for AFCI and so on......they make AFCI Classified listed breakers that will fit most any brand panel now ( excluding FPE and Zinsco...)...so if their is a breaker for a bedroom in the panel now......making it an AFCI breaker is not a big problem for a client if they wish to update that for their safety...

I agree with your premise...and I understand ( remember I am a Home Inspector also ).....but the 100A panel may be fine...heck I see plenty of 200A panels that leave no room for expanding....in regards to breakers but it does not need a 400A service upgrade because of it......so it is very important to understand diversification in electrical services.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #15  
Old 10/17/07, 8:10 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 100 Amp vs 200 Amp

Quote:
Originally Posted by pabernathy
I agree with you in that you need to make the statement that the panel may not be fine if the client plans on making changes and additions to the dwelling in the future...but as of right now unless you do a calculaion and qualified to do so.....the service may be fine even at 100A.....remember 100A is the minimum size required.
Is this required by codes or insurance companies?

I did a very small house (550-600 sq ft over a crawl space, no laundry) inspection for a retiring single lady a few years back which had a 10-15 years old 240v, 60 amp entrance. Did the standard calcs by the local codes and it was OK at 60 amps but I warned the lady that the insurance company would want to see a 100 amp service. 3-4 months later, got a call from her saying she finally bought the house but it had been upgraded to 100 amps by the vendor even though the local electrical inspector said it was still alright. The insurance companies have too much power!!!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 8:44 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts