Default $100 Reward

We have all learned that knob & tube wiring may not be covered with thermal insulation. The usual explanation is that it was designed to be installed in open air in order to dissipate heat. The problem that I see is that every reference I have come across is in retrospect, for example, a contemporary publication stating that K&T HAD been designed to dissipate heat… I have searched high and low for some proof of this. I believe it is plausible that K&T was developed because it was a fast, efficient way of installing single conductors with cotton cambric insulation. That being in open air facilitated soldered splices and protected conductors from abrasion and physical damage. I believe it is plausible that the K&T design has little to do with heat dissipation / ampacity.

The inachi article on K&T indicates the K&T has a higher ampacity than other conductors because of it’s open air design. Many HI's would state that a #14 AWG copper conductor should be protected at 15 amps, regardless of it’s true ampacity and insulation composition. Also- what effect do long lengths of cambric loom have on the ampacity??

Now don’t get me wrong, I’m not looking to bring back the glory days of K&T. But this has bugged me since it first became in issue in the 80’s. Lots of people regurgitating something they heard from someone else who kind of knows. Never, in 26 years (including 13 as an AHJ) have I seen proof of this purported design limitation. Yes the NEC began to address it in the 80’s, but from what I can find on my own, the claims of the fire hazard seem to be unfounded, or at the very least, unreported or unpublished.

I would love to obtain an old electrician’s handbook, code book, electrical design book etc. that clearly states the K&T must be installed in open air for the purposes of cooling. Maybe an old patent or such.

I will pay $100 for an original, definitive publication. If you have and old document like this and would like to sell it, email me.

homewiseinspections@live.com

Thanks!
Reply With Quote
Need a home inspection in Kentucky? Check out InterNACHI's listing of Kentucky certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/30/11, 7:49 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: $100 Reward

This is from the 1987 NECH. Under Uses Not Permitted it mentions heat dissipation in insulation.

Reply With Quote
  #3  
Old 1/30/11, 7:50 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: $100 Reward

Quote:
Originally Posted by jcundiff View Post
We have all learned that knob & tube wiring may not be covered with thermal insulation. The usual explanation is that it was designed to be installed in open air in order to dissipate heat. The problem that I see is that every reference I have come across is in retrospect, for example, a contemporary publication stating that K&T HAD been designed to dissipate heat… I have searched high and low for some proof of this. I believe it is plausible that K&T was developed because it was a fast, efficient way of installing single conductors with cotton cambric insulation. That being in open air facilitated soldered splices and protected conductors from abrasion and physical damage. I believe it is plausible that the K&T design has little to do with heat dissipation / ampacity.

The inachi article on K&T indicates the K&T has a higher ampacity than other conductors because of it’s open air design. Many HI's would state that a #14 AWG copper conductor should be protected at 15 amps, regardless of it’s true ampacity and insulation composition. Also- what effect do long lengths of cambric loom have on the ampacity??

Now don’t get me wrong, I’m not looking to bring back the glory days of K&T. But this has bugged me since it first became in issue in the 80’s. Lots of people regurgitating something they heard from someone else who kind of knows. Never, in 26 years (including 13 as an AHJ) have I seen proof of this purported design limitation. Yes the NEC began to address it in the 80’s, but from what I can find on my own, the claims of the fire hazard seem to be unfounded, or at the very least, unreported or unpublished.

I would love to obtain an old electrician’s handbook, code book, electrical design book etc. that clearly states the K&T must be installed in open air for the purposes of cooling. Maybe an old patent or such.

I will pay $100 for an original, definitive publication. If you have and old document like this and would like to sell it, email me.

homewiseinspections@live.com

Thanks!
I know that in my area of the Canadian Atlantic provinces there are thousands of homes over 90-100+ years old that have operating K&T in insulation......It never has become an issue here......yet!
Reply With Quote
  #4  
Old 1/30/11, 7:55 PM
jcundiff's Avatar
jcundiff jcundiff is offline
Active Poster
 
Join Date: May 2005
Location: Fairview Park, OH
Posts: 251
Please Note: jcundiff is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: $100 Reward

Robert- I'm well aware of the NEC pubs. What I'm looking for is a publication from say... 1920, supporting this widely held, but so far historically unsubstantiated belief.
Reply With Quote
  #5  
Old 1/30/11, 8:10 PM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: $100 Reward

The original 1899 NEC states-
18. Wires – Continued.
rigidly
at least eight inches from each other, except within the structure of lamps, on hanger-boards, in cutout boxes, or like places, where a less distance is necessary.
e. Must, on side walls, be protected from mechanical injury by a substantial boxing, retaining an air space of one inch around the conductors, closed at the top (the wires passing through bushed holes), and extending not less than seven feet from the floor.


http://www.mikeholt.com/documents/nec/NCSE1899.pdf

The knobs that were used kept the wire off the studs to allow the wire to dissipate the heat. It would have been easier to staple them to the wood like we do today. They knew that the insulation on the wire gets brittle from heat.
Reply With Quote
  #6  
Old 1/30/11, 8:32 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: $100 Reward

Quote:
Originally Posted by rernst1 View Post
The original 1899 NEC states-
18. Wires – Continued.

rigidly
at least eight inches from each other, except within the structure of lamps, on hanger-boards, in cutout boxes, or like places, where a less distance is necessary.
e. Must, on side walls, be protected from mechanical injury by a substantial boxing, retaining an air space of one inch around the conductors, closed at the top (the wires passing through bushed holes), and extending not less than seven feet from the floor.

http://www.mikeholt.com/documents/nec/NCSE1899.pdf

The knobs that were used kept the wire off the studs to allow the wire to dissipate the heat. It would have been easier to staple them to the wood like we do today. They knew that the insulation on the wire gets brittle from heat.


Interesting...... but that was still in the infancy of residentail wiring and learning about this newly harnessed energy transferred in metal wires......

Many have said that they have not heard of problems of insulation and fires from K&T.....could they have been overly concerned about the new untried systems back then?

Reply With Quote
  #7  
Old 1/30/11, 8:46 PM
jcundiff's Avatar
jcundiff jcundiff is offline
Active Poster
 
Join Date: May 2005
Location: Fairview Park, OH
Posts: 251
Please Note: jcundiff is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: $100 Reward

Robert E, your excerpt and the balance of the 1899 NEC still says nothing about the disipation of heat as it relates to ampacity of the conductor. The spacing only refers to separation from combustible materials (which I'n not challanging). Even the except is refering to 1" spacing in "boxing" as protection from physical damage exposed on walls less below 7 feet. Again, I believe this is a clearance from combustibles issue, as most old "boxing" is wooden.
Reply With Quote
  #8  
Old 1/30/11, 11:09 PM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: $100 Reward

Ok here is more from the 1896 Meeting of the NATIONAL CONFERENCE ON STANDARD ELECTRICAL RULES

Board of Fire Underwriters code. This table adds 25 percent to the first nine currents in
concealed work, and represents an elevation of temperature amounting roughly to about 14
degrees C. or 25 degrees F. at steady full load.
The recently issued rules of the British Board of Trade call for a maximum temperature
elevation of 30 degrees F., or about 17 degrees C., and are equivalent to a still further increase in the permissible current strengths, and a corresponding reduction in the margin of safety.
Mr. Stone:
I would like to ask if there is any difference in the matter of disintegration or
injury to the insulation of the wires by any increase in the heat above 16 degrees C. or 25 degrees F.?

Mr. Kennelly:
I am not aware that there is any danger at a temperature below that at
which you can hold your bare hand upon a wire.

Mr. Greene:
It seems to me that this question resolves itself into a question of what is a
safe current carrying capacity of wires. Certainly, from the information given by Mr. Kennelly
the carrying capacities as shown in column 1, are very conservatively rated and there is a large

factor of safety, considerably larger than is the case with the capacities given in table 2


I think it would be much more satisfactory to everyone. I think it is quite proper that there
should be a distinction between open and concealed work, because it is a well known fact thatthe conductor can carry a larger amount of current when “open” than when concealed in a moulding, with the same temperature rise in each case.
The heating of the fusewill depend upon its resistance. Its contacts, which often afford a variable element and the rate of getting rid of heat will depend upon the size of the fuse and its contacts and the temperature. The time of melting and the current strength will also depend on the temperature of the surrounding air. A fuse in a boiler room, where the surrounding temperature is high, will melt with a small current.

On ordinary wires, the heating limit is determined by the insulation on the wire. When we had
paraffin insulation, it was desirable to run the wires cool; with the present grade of wires they
may be run warmer. We would like to have insulation not affected by heat, so that they might be run warmer than is now proposed.

http://www.mikeholt.com/documents/nec/NCSE1896.pdf
Reply With Quote
  #9  
Old 1/31/11, 12:15 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: $100 Reward

Fascinating stuff.
I have a couple books from 1910 and 1913 where both mention Knob and Tube being on its way out because of the NEC even though it costs 1/2 to 1/3 that of conduit.

The wire needs to stay away from moisture also and insulation gets wet.I doubt they had moisture barriers under insulation back then if there was insulation at all.
[ATTACH]100-reward-knob-and-tube-clearance.jpg[/ATTACH]

Go to Google Books and punch in keywords with Knob and tube plus install or something similar to find more.I saved 2 PDF versions which you can do on the site.
Here is the 1913 book from above.Electric wiring and lighting ...: Part I--Electric wiring By American School (Chicago, Ill.), Charles Edwin Knox, George Carl Shaad
Just give me a kind word if you find what you are looking for.
P.S if they are made to disperse heat you would not want to cover them with flammable insulation...now would you.

http://books.google.com/books?id=YUN...wiring&f=false
Attached Thumbnails
100-reward-knob-and-tube-abolishment.jpg  
Reply With Quote
  #10  
Old 1/31/11, 11:25 AM
jcundiff's Avatar
jcundiff jcundiff is offline
Active Poster
 
Join Date: May 2005
Location: Fairview Park, OH
Posts: 251
Please Note: jcundiff is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: $100 Reward

OK- so here the NEC is acknowledging K&T being covered with thermal insulation with absolutely no reference to heat dissipation or ampacity adjustment.

Excerpt from 1930 NEC

Article 502 - Concealed Knob & Tube

J. When thermal insulation is used in the hollow spaces of walls and ceilings in which concealed knob-and-tube work is installed, only approved non-corrosive, non-combustible, non-conducting, materials shall be used, and these shall be applied in a manner not liable to place a strain upon the wires or supports.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AAA Construction school offers grandfathering help. gromicko Florida Inspectors 169 10/27/10 9:44 PM
$5000.00 Reward rmyers1 Inspection Education & Training 0 12/11/06 10:50 PM
InspectVue... The Best Home Inspection Software and Save $100 buying It from Me! jwatts1 Inspection Hardware, Software & Publications 60 12/1/06 2:07 AM


All times are GMT -4. The time now is 5:11 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts