Ran across a situation for an AC condenser with a 12-2 NM sheathed cable feeder on a 30A breaker. The breaker/wire combination wasn't what rubbed me the wrong way as it met the listed nameplate max breaker size, and was within 175% of the RLA. But I did do a double take when I saw a listed "minimum circuit ampacity" of 25A on the nameplate (RLA x 125%) with the #12 Cu wire.
I would have expected #10 Cu wire with the listed 25A required circuit ampacity. But after digging a little deeper it seems that the usual small branch circuit limitations of 15A for #14Cu, 20A for #12Cu, and 30A for #10Cu (NEC 240.4.D) do not necessarily apply to AC circuits. Found that it seems you are allowed to use the full 25A rating for 12-2 NM cable (NEC Table 310.16) in certain cases (NEC 240.4.G) which includes HVAC equipment. Does anyone know if thats considered poor field practice in general, even though it may be allowed by current construction standards, as it's the first time I came across this. Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
Robert,
Manytimes the ratings of the actual outside compressor unit will be like that in that you rate the minimum rating for the conductor and the max rating for the OCPD. This factor has already been figured for the electrician when doing the installation and the NEC says in specific cases where the NEC allows it. Used to me an "oblist" on the 310-16 chart beside the 14AWG, 12AWG and 10AAWG...in fact I just did a seminar on that in Denver explaining all those little details for the HI's........ Notice on the chart 310-16 the * beside the 14,12 and 10....at the bottom it refers you to 240.4(D) Now....240.4(D) says unless specified in 240.(E) through (G)...then 14 AWG must be 15A, 12 AWG must be 20A and 10 AWG must be 30A.....now... So 240.4(G) allows ampacity differences in many listed areas other than what is listed for 240.4(D)...which then in turn revert to the ACTUAL ampacity table of 310-16 Now the sizing of the Protection and Conductor size is marked on the equipment nameplate which has been already calculated by the manufacturer...important to know the MAX FUSE SIZE is the MAX for the protection and the MIN Circuit Ampacity is for the coductors...many get that confused...even some local inspectors... BTW..if it says MAX FUSE SIZE..it has to have a fuse protection it somewhere...either at the unit disconnect or beside the panel...then it can be to a circuit breaker...BUT if it says FUSE it must be fused protected... If it says protected by "HACR" then it should be protected by a circuit breaker. Ok....Now...the size of the conductors to the unit is based on the NEC 440.32 ( which should already be done on the nameplate...as shown above) So....with no nameplate...you would use NEC 440.22 for the OCPD and 440.32 to size the conductors....and the 440.4(G) denotes this is a listed special allowance refered to in 240.4(D) and shown in 240.4(G) to refer you to 440 for A/C units... At that point the verbage says to use 310-16...and then you are allowed to use the ratings of the charge..so here is an example nameplate 40A MAX FUSE SIZE 23A MIN CKT AMPACITY Translation - 40A OCPD Translation - 25A Wire ( 12 AWG THHN rated at 25A under 60 degrees since it is under 100A..and we know that under 100A uses the 60 degree column) I make things like this very simple in my seminars...lol....harder online. Paul W. Abernathy |
Here is a good example and we will use it to learn from with the replies...
Question: What size THHN conductor and fuse protection are required for a 24A, 240V motor compressor. A.) 10 AWG, 40A Fuse B.) 10 AWG, 50A Fuse C.) A or B D.) none of these Should be interesting........again use Art 440.22 and 440.32 to come up with the answer.... Ok....for those who dont want to learn and B*tch about code....SKIP IT....don't waste my time...trying to teach something here....not something you QUOTE to someone as code.....GESSSH>>>i get tired of having to put that in my posts... Paul W. Abernathy |
... or 60a?
We are very lucky the manufacturer puts that label on. They get to do the engineering and give us an answer that will work.
I dont believe 60A will apply here Greg...Upsizing is not allowed in these cases...>>>>>BUT brings up a GREAT devils advocate type question if someone says 60A......great stuff...
Dang I get too excited over this crap...I really need a life other than electricity.. Paul W. Abernathy Last edited by pabernathy; 6/26/06 at 3:19 PM.. |
Paul W. Abernathy |
HOw will the upgraded new units effect us with new seer requirements . I understand they will cost more will the current draw be any different for the upgraded units ?
Roy Cooke sr ....Royshomeinspection.com |
Hey Roy,
I wanted an ANSWER fella...thehehe....BUT good question... I think with anything new like that the nameplates will reflect it and they are good about doing that now days..its the old ones you have to worry more about. When someone upgrades a unit since the SEER is changing the actual nameplate will change and you HIT a great point....people are only talking about the piping size change...and the cost of that....the better understand the COSTS of having the potential feeder changed as well to meet the new equipment. Now I must confess.....I have not done any RETRO's yet for clients.....but in new construction it wont really matter...we will size to the new nameplate but you are right...once an old model needs replacment...the new nameplate ratings will have to be met. Paul W. Abernathy |
Typically a higher SEER will use less power so the wire should be OK but the O/C device may need to be replaced.
As for the 60a. 440.22(A) says "...where the protection specified is not sufficient for the starting current of the motor, the rating or setting shall be permitted to be increased but shall not exceed 225 percent of the motor rated-load current or branch-circuit selection current, whichever is greater." Starting with 24a I get a max of 54, that rounds up to 60 since there is no 55. I would want to see the 45 or 50 trip before I believed the 225% was necessary. That is one reason the label is so great. If the label says that machine should run on a 45 or 50 and it trips one ... it is broke, fix it, don't just put in a bigger fuse. |
P.S. At least newer AC equipment almost always has "MAX FUSE OR HACR BREAKER" on the nameplate ... so either a fuse or breaker could be used. Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... Last edited by roconnor; 6/27/06 at 11:36 AM.. |
Paul ... I generally recalled the minimum NEC requirements which would allow #12 Cu NM on an AC circuit with a 25A required ampacity, which is why I looked it up to confirm that. But an electrician I know thought that would be very poor practice cuting it so close given the breakers are often oversized for a given wire to begin with, and AC units often draw more than the nameplate rating after only a short time in-service.
Thus the reason I threw it out for discussion, and to see if anyone else thought that may be poor field practice (where sometimes what is considered good field practice differs from code "minimums") ... Quote:
I think defects such as having a breaker that exceeds the max fuse/breaker listing on the condenser nameplate will become more common as older equipment is replaced. JMO & 2-nickels ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
OK...guys....no assumption of Start UP is needed to figure this example I gave....it is quite simple using the NEC...I will explain.....You only need to know the 24A and voltage to figure this using the NEC....
Answer: a.) 10 AWG, 40A Fuse Note: I said what is required not what is the MAX allowed.... Branch-Circuit Conductors ( Table 310.16 and 440.32 ) 24A x 1.25 = 30A, 10 AWG, rated 30A at 60 Degrees C.( 110.14(C) and Table 310.16) Branch-Circuit Protection ( 240.6(A) and 440.22(A) 24A x 1.75 = 42A, next size down = 40A Why next size DOWN....well you already made the adjustment for the 175%...do you think the NEC will let you adjust again...lol OK...here is the TRICK....the NEC says IF the 40A protection device is not capable of carrying the starting current, then the protection device can be sized up to 225% of the equipment load current rating ( 24A x 2.25= 54A, next size down 50A ) So why not answer (C) .......is we said required......not the adjustment....you can only use 225% IF the 175% rated OCPD can't handle the start up......sneaky....sorry........just wanted to use it as a learning experience for the other guys.... Paul W. Abernathy Last edited by pabernathy; 6/27/06 at 10:17 AM.. |
Hmmm ... lets think about this. It's actually not known what the "required" fuse would be.
42A (175%) would be the "maximum" allowed (NEC 440.22 actually uses "not exceeding ... shall be permitted"), which means using up to a 40A fuse ... UNLESS the 40A fuse is not sufficient for the start-up load, in which case the "maximum" would be 54A (225%) and a 50A fuse would indeed be "required". P.S. Sorry Paul ... couldn't resist ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... Last edited by roconnor; 6/27/06 at 11:37 AM.. |
lol......man....I am die hard NEC...thehehe....it says 440 shall have exception in regards to the sizing....so you MUST size the OCPD to sizing of 175%...at which point ONLY then if the OCPD can't handle the start up can you increase to 225%.....
BZZZZZZZZZZ......the NEC lists 175% as the rating to determine the OCPD...so it is the REQUIRED size......the 225% is the MAX only IF........IF...IF.....IF...IF...IF.....theheheheh Leave it to Education Committee Members to FRY members brains..thehehehe....lol..... Paul W. Abernathy |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 7 | 4/16/12 9:51 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Article 240 : Overcurrent Protection Article | pabernathy | Electrical Inspections | 0 | 5/23/07 11:40 AM |
| Bare wire on old dryer or stove circuit: neutral or ground? | fbartlo | Electrical Inspections | 9 | 8/28/06 1:08 AM |