  #16  
Old 8/4/07, 11:27 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 12 year old electrocuted by AC unit

No, no. This was my point, sort of, in #3.
No one is going to check the case of an A/C for voltage for no reason. Your job gives you a reason.
I'm not sure if I'd say this should be a common thing to test for due to the extremely rare circumstances, but similar tests could become routine.
Reply With Quote
  #17  
Old 8/4/07, 11:40 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: 12 year old electrocuted by AC unit

Quote:
Originally Posted by Speedy Petey
No, no. This was my point, sort of, in #3.
No one is going to check the case of an A/C for voltage for no reason. Your job gives you a reason.
I'm not sure if I'd say this should be a common thing to test for due to the extremely rare circumstances, but similar tests could become routine.
It is not in the SOP for a home inspector to carry or use a volt meter.
Where do we draw the line we are to do a visual inspection of the home . We have enough to inspect with out getting to complicated .
............ Cookie

I can give a 100 things we could do .
It is not our job and most do not have the expertise ar knowledge to do most.



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #18  
Old 8/5/07, 8:58 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 12 year old electrocuted by AC unit

OK, then other than a visual inspection of the conduit system, how would you have found this potentially lethal problem?
Reply With Quote
  #19  
Old 8/5/07, 9:14 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: 12 year old electrocuted by AC unit

Hi to all,

This is (I hope) a rhetorical question, is there any reason why a voltage tic would not have found this problem, personally I have one in my back pocket on all inspections and check every service panel and most HVAC cabinets and things like rigid duct work.

Having found several "hot" enclosures and pipes over the years I am now very cautious.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #20  
Old 8/5/07, 9:31 AM
klott's Avatar
klott klott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,707
Default Re: 12 year old electrocuted by AC unit

Quote:
Originally Posted by rcooke
It is not in the SOP for a home inspector to carry or use a volt meter.
Where do we draw the line we are to do a visual inspection of the home . We have enough to inspect with out getting to complicated .
............ Cookie

I can give a 100 things we could do .
It is not our job and most do not have the expertise ar knowledge to do most.
Roy, it would not be any harder or take any longer to check the case or conduit with a voltage ticker, than it would to look at the data plate. Small price to pay, big reward for saving a life. Especially for a CMI, you should have the knowledge and be willing to use it to show why you are worth the higher fees.

Last edited by klott; 8/5/07 at 9:45 AM..
Reply With Quote
  #21  
Old 8/5/07, 9:52 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: 12 year old electrocuted by AC unit

Quote:
Originally Posted by klott
Roy, it would not be any harder or take any longer to check the case or conduit with a voltage ticker, than it would to look at the data plate. Small price to pay, big reward for saving a life. Especially for a CMI, you should have the knowledge and be willing to use it to show why you are worth the higher fees.
Excuse me please read my previous post.
Please do not put words on some thing I did not say.
I stand behind my statements and my inspections Thanks....... Cookie

Quote:
Originally Posted by rcooke
I can not and will not inspect from a picture .
I am paid to be sceptically and see what others do not see.
Sorry but to assume could get one of us into trouble.
......... Cookie



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #22  
Old 8/5/07, 10:15 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 12 year old electrocuted by AC unit

Man Roy, why so defensive?
NO ONE is asking you to armchair inspect this. These are all rhetorical questions and personal opinion based on the information provided.
Don't worry, you're not gonna get sued over what you say in this thread.
Reply With Quote
  #23  
Old 8/5/07, 11:24 AM
klott's Avatar
klott klott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,707
Default Re: 12 year old electrocuted by AC unit

I'm not putting words to your comments, but you conveniently switched your post to dodge your reason,("to much work, to complicated") for not checking the A/C case.
Reply With Quote
  #24  
Old 8/5/07, 11:50 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: 12 year old electrocuted by AC unit

Quote:
Originally Posted by klott
I'm not putting words to your comments, but you conveniently switched your post to dodge your reason,("to much work, to complicated") for not checking the A/C case.
Kenneth!!!!!!
I think you are just trying to be a ***** disturber .
No where Did I mention tickler .
I wonder why you bring the CMI into this discusion.
I said I needed more information to make any thoughts on this .
I said I would not inspect from a picture. .
No where did I wish to get involved in a long distance inspection .
Switched my post NO F IN WAY.
Unless you where able to read more from the news article then I .
I wonder what the he77 you are up too.
Please read I think all my posts are below.

Thanks Cookie


Quote:
Originally Posted by rcooke
Looking at the AC and how close it is to the fence .
Quote:
Originally Posted by rcooke
I would like to hear the rest of the story .
This unit looks pretty new it said they worked on it in 2006.
Well it is so close to the fence I do not see how it could not have been touched the same time as the fence in the last two years.
I expect there could be a lot more info comming down with this one and I would love to hear what they find.

Cookie
Quote:
Originally Posted by rcooke
I can not and will not inspect from a picture .
Quote:
Originally Posted by rcooke
I am paid to be sceptically and see what others do not see.
Sorry but to assume could get one of us into trouble.
......... Cookie
Quote:
Originally Posted by rcooke
I guess we have to disagree on this one . Thanks
Quote:
Originally Posted by rcooke

Cookie
Quote:
Originally Posted by rcooke
It is not in the SOP for a home inspector to carry or use a volt meter.
Quote:
Originally Posted by rcooke
Where do we draw the line we are to do a visual inspection of the home . We have enough to inspect with out getting to complicated .
............ Cookie

I can give a 100 things we could do .
It is not our job and most do not have the expertise ar knowledge to do most.
Quote:
Originally Posted by rcooke
Excuse me please read my previous post.
Quote:
Originally Posted by rcooke
Please do not put words on some thing I did not say.
I stand behind my statements and my inspections Thanks....... Cookie



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.




Last edited by rcooke; 8/5/07 at 11:57 AM..
Reply With Quote
  #25  
Old 8/5/07, 11:54 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 12 year old electrocuted by AC unit

Wow!
Reply With Quote
  #26  
Old 8/5/07, 1:44 PM
klott's Avatar
klott klott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,707
Default Re: 12 year old electrocuted by AC unit

Reply With Quote
  #27  
Old 8/5/07, 1:52 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: 12 year old electrocuted by AC unit

Quote:
Originally Posted by klott
Now you are speakless .

Tell me about things I did not say and your defense is MT.

Go have a Kawphy Ken you will feel good.
ME I am going to have a Pepsi and watch NASCAR.
Will not be as good as yesterdays BUSH.
Or todays Formula One
.......... Cookie
</IMG></IMG></IMG></IMG>



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #28  
Old 8/5/07, 2:07 PM
klott's Avatar
klott klott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,707
Default Re: 12 year old electrocuted by AC unit

Kawphy in hand, enjoy Roy! The race that is.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
HVAC age tspeerstra General Inspection Discussion 11 3/7/12 8:25 AM
Nominations for The Year 2007 mcyr Miscellaneous Discussion for Inspectors 0 11/9/07 8:18 PM
Nominations for The Year 2007 mcyr Miscellaneous Discussion for Inspectors 0 8/14/07 5:54 PM
Nominations for The Year 2007 mcyr General Inspection Discussion 0 8/14/07 5:51 PM


All times are GMT -4. The time now is 5:12 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts