Default 120/240 4 wire?

I ran into this panel during a recent inspection, but did not expect to find 2 hot conductors, one gray neutral and one bare ground. There was no apparent connection between the neutral and ground. This is not a subpanel, although the main 200A disconnect was outside next to the meter. How common is this arrangement?
Attached Thumbnails
120-240-4-wire-panel.jpg  



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #2  
Old 6/10/08, 11:27 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 120/240 4 wire?

If the service disconnect is outside this is a sub panel.
Reply With Quote
  #3  
Old 6/10/08, 11:54 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 120/240 4 wire?

Quote:
Originally Posted by fnewman
the main 200A disconnect was outside next to the meter.
That makes it a "sub" panel. The service disconnect is located in the "service" panel. All other panels require a 4 wire feed, with isolated neutrals and bonded grounds (some exceptions apply).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 6/10/08, 1:35 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: 120/240 4 wire?

Well, I suspected that would be the answer, although I don't always see that arrangement in homes around here. So, here's another question - as you may be able to see from the picture, there are a LOT of neutrals - so many that each could not possibly be landed on an individual terminal. What would be the proper solution for the installer? I would think that a second terminal strip should have been installed.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #5  
Old 6/10/08, 4:17 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 120/240 4 wire?

If there are more neutrals than neutral lugs I would be looking closer at the number of breakers installed vs what the panel max is.
You can't mix grounds up with neutrals on the busses in a sub either. There is a ground bus system and a neutral bus system, not connected.
Some panels do have expansion kits for the neutral bus and ground bus expansions are available for virtually any panel.
Reply With Quote
  #6  
Old 6/10/08, 6:01 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 120/240 4 wire?

Quote:
Originally Posted by fnewman
What would be the proper solution for the installer?
They would install an accessory neutral bar. It is basically another ground bar with insulated standoffs.
Reply With Quote
  #7  
Old 6/11/08, 9:53 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: 120/240 4 wire?

That is essentially what I told the homeowner (who was present for the inspection). However, I found it interesting that the electrician who did the work carefully terminated the neutrals and ground conductors on their correct bus locations, but bunched the neutrals - I assume out of ignorance because there were a few screws left unused. Given that this is a 40 circuit panel with relatively few 2 pole circuits, the need for an auxiliary neutral bus would seem to be quite a frequent occurrence.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #8  
Old 6/11/08, 10:30 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 120/240 4 wire?

Quote:
Originally Posted by fnewman
Given that this is a 40 circuit panel with relatively few 2 pole circuits, the need for an auxiliary neutral bus would seem to be quite a frequent occurrence.
Depends on the brand and model of the panel. I can count on one hand the number of times when I've had to add an accessory neutral bar to a panel that I've added circuits to or installed. I've seen a great number of panels, however, that should have had them put in to correct existing nonconformities.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 5 3/25/07 10:41 PM
Bare wire on old dryer or stove circuit: neutral or ground? fbartlo Electrical Inspections 9 8/28/06 1:08 AM


All times are GMT -4. The time now is 5:12 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts