I ran into this panel during a recent inspection, but did not expect to find 2 hot conductors, one gray neutral and one bare ground. There was no apparent connection between the neutral and ground. This is not a subpanel, although the main 200A disconnect was outside next to the meter. How common is this arrangement?
Frank P. Newman Emerald City Inspections, LLC Dublin, GA |
|
#2
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
If the service disconnect is outside this is a sub panel.
|
|
#3
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#4
|
|||
|
|||
|
Well, I suspected that would be the answer, although I don't always see that arrangement in homes around here. So, here's another question - as you may be able to see from the picture, there are a LOT of neutrals - so many that each could not possibly be landed on an individual terminal. What would be the proper solution for the installer? I would think that a second terminal strip should have been installed.
Frank P. Newman Emerald City Inspections, LLC Dublin, GA |
|
#5
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
If there are more neutrals than neutral lugs I would be looking closer at the number of breakers installed vs what the panel max is.
You can't mix grounds up with neutrals on the busses in a sub either. There is a ground bus system and a neutral bus system, not connected. Some panels do have expansion kits for the neutral bus and ground bus expansions are available for virtually any panel. |
|
#6
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#7
|
|||
|
|||
|
That is essentially what I told the homeowner (who was present for the inspection). However, I found it interesting that the electrician who did the work carefully terminated the neutrals and ground conductors on their correct bus locations, but bunched the neutrals - I assume out of ignorance because there were a few screws left unused. Given that this is a 40 circuit panel with relatively few 2 pole circuits, the need for an auxiliary neutral bus would seem to be quite a frequent occurrence.
Frank P. Newman Emerald City Inspections, LLC Dublin, GA |
|
#8
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Proper Marr Connectors for Aluminum Pigtails | jskrypka | Canadian Inspectors | 5 | 3/25/07 10:41 PM |
| Bare wire on old dryer or stove circuit: neutral or ground? | fbartlo | Electrical Inspections | 9 | 8/28/06 1:08 AM |