Default 120V loads only

note: This does not apply to a normal residential scenario.


How many maximum amps on each leg of a regular residential 240/120V panel can you get if you only have 120V loads connected with each side balanced?

Main breaker rating is 240V, 200 amp, 48,000 watts

List the amps on each leg and total amps pulled from the service.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #2  
Old 3/31/08, 10:10 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 120V loads only

200 amps at 120V on leg A = 24,000va (watts)
200 amps at 120V on leg B = 24,000va (watts)
48,00va total

200 amps at 240v between A and B = 48,000va (watts)

Same diff...
Reply With Quote
  #3  
Old 3/31/08, 10:30 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: 120V loads only

Can you have 400 amps of load if only 120V loads are used and balanced?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #4  
Old 3/31/08, 10:46 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 120V loads only

No, you can have 200 amps on each of two legs at 120v. Or 200A @ 240v.

No, this is not equivalent to 400A @ 120v. At least not in the real world. Because no where will you every see much over 200 amps.
Reply With Quote
  #5  
Old 3/31/08, 10:50 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: 120V loads only

Quote:
Originally Posted by Speedy Petey
No, you can have 200 amps on each of two legs at 120v. Or 200A @ 240v.

No, this is not equivalent to 400A @ 120v. At least not in the real world. Because no where will you every see much over 200 amps.
But theoretically you could have 400 A total assuming balance loads correct?



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #6  
Old 3/31/08, 10:53 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 120V loads only

I'm not trying to be a jerk, but what is the fascination with this 400A @ 120v thing??? So many folks pressure us to say "Yes, it is 400A at 120v.". It is not.

How come 200A @ 240v is not good enough?
Reply With Quote
  #7  
Old 3/31/08, 10:58 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: 120V loads only

Quote:
Originally Posted by Speedy Petey
I'm not trying to be a jerk, but what is the fascination with this 400A @ 120v thing??? So many folks pressure us to say "Yes, it is 400A at 120v.". It is not.

How come 200A @ 240v is not good enough?
It's an ongoing discussion somewhere else.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #8  
Old 3/31/08, 11:00 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: 120V loads only

Let me ask it this way.

Could you have 40 20 Amp breakers in a panel each with a 10 amp load?



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #9  
Old 3/31/08, 11:07 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 120V loads only

Absolutely.
But put an amp meter on the neutral and tell me what you read.
See what I am getting at?
Reply With Quote
  #10  
Old 3/31/08, 11:11 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 120V loads only

It's 48,000 volt-amps, regardless of how you divvy it up.
Reply With Quote
  #11  
Old 4/1/08, 9:51 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: 120V loads only

I agree, you can actually look at it as two 120VAC power sources and have a maximum of 48000 watts divided by 120Volts = 400 amps of 120V power.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #12  
Old 4/1/08, 12:30 PM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: 120V loads only

Bruce and Michael,

You are incorrect in your assumptions. In the hypothetical situation you have outlined, (200 amp balanced loads on each of the two legs), you will only measure 200 amps at any point in the system.

Lets follow the electrons. For 1/120th of a second, 200 amps will flow into the panel through Leg A, the same 200 amps will then flow through the 120V loads connected to leg A, the same 200 amps will then flow to the neutral bus, the same 200 amps will then flow through the 120V loads connected to leg B, then the same 200 amps will flow out of the panel through leg B. Then the current reverses and takes the same path backwards. It is all the same electrons.
Reply With Quote
  #13  
Old 4/1/08, 12:48 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: 120V loads only

Thats a good explanation of the actual operation and the reason why AC is used for power distribution instead of DC.

The highest measured current will be 200 but you have 48,000 watts of power dissipated on 120V loads. It takes the equivalent of 400 amps to produce this amount of power on 120V loads.

This "never to be found" setup in residential is best described in watts rather that amps since the voltage on the loads is not 240V.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #14  
Old 4/1/08, 12:54 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: 120V loads only

Quote:
Originally Posted by pdickerson
Bruce and Michael,

You are incorrect in your assumptions.
What did we assume?
You mean Marc and speedy are wrong?

Your description is correct.

I thought I made it simple when I said:

40 breakers with 10 A load each.

The panel is still 120/240 @ 200 A but is capable of supplying 400 A @ 120V as long as the load is balanced.

I think we are in agreement but it's all how you look at it.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #15  
Old 4/1/08, 1:31 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Default Re: 120V loads only

Bruce, Michael

Your looking at the concept of current, load and A/C incorrectly.

Alternating current A/C is not like DIRECT current or DC.. meaning a constantly current level..

I was going to go into a very long explanation on the theory but figured it would be best if Paul Abernathy would explain it ..

On a side note, Tangent.

By the way A/C was found to be easier to "transmit" via overhead "High" power lines over great distances. Loss factors are very high that is why we don't use DC in homes these days. Samuel Insull... He had a HUGE part in it..see......http://www.geocities.com/WallStreet/...48/insull.html
http://en.wikipedia.org/wiki/Samuel_Insull

245MKV at the towers and 12,500 volts at the wires at very top of the poles around the neighborhoods in my area to transformers 240 volts to the house...

Side note:

What happens to the voltage in the summer time when everyone runs there AC Compressors??
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 2 1/8/11 8:04 PM
Unfamiliar newer floor structure -- span too long for engineered joists? fbartlo Structural Inspections 8 2/10/08 12:11 PM
Determining Existing Loads jtedesco1 Electrical Inspections 11 1/7/08 10:46 PM
Where do I put the Aquarium? mcyr Structural Inspections 3 11/6/07 4:05 PM
Emergency Lighting (commercial) mcyr Electrical Inspections 24 6/10/06 11:06 AM


All times are GMT -4. The time now is 4:58 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts