Default 125 amp main 200 amp sub (Is it a issue)

I wanted to post this to see what others say.

Main disconnect located in garage. 125 amps.

Sub(remote distribution panel) located in basement with a 200 amp breaker. SEC was rated for 125 amps.

Q1) What is the service size 125 or 200 amps?
Q2) Is the 200 amp breaker acceptable in this application, are the SEC properly sized?

Q3) Seperate question
What are your thoughts on the split bolt connection for the GEC? Looks like a crappy connection, could we not just go to the available bar on the panel? This connects to the sub

Q4) I know the bonding screw needs to be removed at the sub, but is it acceptable to be there and not be in contact with the panel?

I now know the answer thanks to my friend Jeff Pope. (You are a good man to answer my calls)

I should post the other question to I had on the Bonding jumper to the grounding terminal.

I would of mis reported both if I had not talked to Jeff.
Attached Thumbnails
125-amp-main-200-amp-sub-issue-157910-013-small-.jpg.jpg
Views:	188
Size:	34.1 KB
ID:	36077   125-amp-main-200-amp-sub-issue-157910-022-small-.jpg.jpg
Views:	208
Size:	60.1 KB
ID:	36078  
Reply With Quote
Need a home inspection in Ohio? Check out InterNACHI's listing of Ohio certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/29/10, 4:58 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 125 amp main 200 amp sub (Is it a issue)

Quote:
Originally Posted by dmacy View Post
I wanted to post this to see what others say.

Main disconnect located in garage. 125 amps.

Sub(remote distribution panel) located in basement with a 200 amp breaker. SEC was rated for 125 amps.

Q1) What is the service size 125 or 200 amps?
Q2) Is the 200 amp breaker acceptable in this application, are the SEC properly sized?

Q3) Seperate question
What are your thoughts on the split bolt connection for the GEC? Looks like a crappy connection, could we not just go to the available bar on the panel? This connects to the sub

Q4) I know the bonding screw needs to be removed at the sub, but is it acceptable to be there and not be in contact with the panel?

I now know the answer thanks to my friend Jeff Pope. (You are a good man to answer my calls)

I should post the other question to I had on the Bonding jumper to the grounding terminal.

I would of mis reported both if I had not talked to Jeff.
Q1- 125 amp
Q2- Yes, since the conductors are protected by the 125 amp main. This could also be a Main Lug Only (MLO) panel if in the same dwelling.
Q3- The split bolt connection is improper since the GEC needs to connect directly the the neutral of the service disconnect. The EGC going to the subpanel can also connect there. The neutral should be bonded to the enclosure at the service disconnect.
Q4- If you mean that it's only threading into the plastic and not connected to the enclosure then IMO it can remain. Might fool someone in the future however.
Reply With Quote
  #3  
Old 3/30/10, 1:39 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: 125 amp main 200 amp sub (Is it a issue)

My question is what type of appliances are in the home. is everything gas or electric? With that many circuits on the sub panel, the main might be overloaded.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #4  
Old 3/30/10, 2:13 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 125 amp main 200 amp sub (Is it a issue)

The number of circuits is not directly related to the actual loads on the circuits. Someone may have just divided the circuits by area instead of load. You also have non-coindent loads where only one runs at a time like the heat and air conditioning.
Reply With Quote
  #5  
Old 3/30/10, 3:42 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: 125 amp main 200 amp sub (Is it a issue)

Quote:
The number of circuits is not directly related to the actual loads on the circuits. Someone may have just divided the circuits by area instead of load. You also have non-coindent loads where only one runs at a time like the heat and air conditioning.
Your answer still does not justify my original question. Without having all the info on what appliances are being used then you wont know. If everything appliance wise is electric and in a 2000 sf home, the the service is under rated IMO. I noticed one of the breakers was tagged double oven. So if both ovens are being used, the water heater is working and the heat pump running all at the same time, don't you think that could tax the 125 amps. Plus regular lighting being on. Great chance this could happen at Christmas time with family over. David would have to elaborate on this to know for sure.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net

Last edited by sfogarty; 3/30/10 at 4:21 PM..
Reply With Quote
  #6  
Old 3/30/10, 3:49 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: 125 amp main 200 amp sub (Is it a issue)

Range top was gas, dryer was gas.

I thought the double oven was both.
Reply With Quote
  #7  
Old 3/30/10, 3:51 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: 125 amp main 200 amp sub (Is it a issue)

Furnace??? Gas I am sure. They dont leave much room for upgrades do they David.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #8  
Old 3/30/10, 4:08 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 125 amp main 200 amp sub (Is it a issue)

Quote:
Originally Posted by sfogarty View Post
Your answer still does not justify my original answer. Without having all the info on what appliances are being used then you wont know. If everything appliance wise is electric and in a 2000 sf home, the the service is under rated IMO. I noticed one of the breakers was tagged double oven. So if both ovens are being used, the water heater is working and the heat pump running all at the same time, don't you think that could tax the 125 amps. Plus regular lighting being on. Great chance this could happen at Christmas time with family over. David would have to elaborate on this to know for sure.
Sean,
I see your point but as Jim noted the size and number of OCPD's is not really a good indicator of whether or not the service is adequate. Only a load calculation can accurately determine the required size for a service. Is adequacy in the size of the service even in question in David's post?
Reply With Quote
  #9  
Old 3/30/10, 4:19 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: 125 amp main 200 amp sub (Is it a issue)

Quote:
Is adequacy in the size of the service even in question in David's post?
No, that was not a question, and I am by no means saying David missed anything. I was mainly pointing out the fact that with all the right factors the home could be undersized. That 200 amp panel was designed to take on more than 125 amps, so the possiblility of adding more is there. I think the buyer should know that the home they are about to purchase is limited in changing major appliances because of the service. I occasionaly find homes with 100 and 125 amp service, and I make sure to explain to the buyer that it IS correct, but your options are limited.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #10  
Old 3/30/10, 5:35 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: 125 amp main 200 amp sub (Is it a issue)

I actually discussed having a load calculation done by an electrical contractor with the client. Something my client may consider if she decides to add any other circuits.

That 200 amp breaker is just being used as a switch in this case and I believe the max capacity for the panels would be 125 amps.

When I talked to Mr. Jeff Pope he explained it to me, I always seem to forget when this senerio happens again. Like in another 25-50 inspections.

If I did not talk to Jeff I would of improperly reported this as a safety issue, the agents would of had an electrician come out and say this is compliant and I would of looked like an idiot.

So I really am appreciative of Jeff explaining to me and I posted so others would not make the same mistake I almost made.
Reply With Quote
  #11  
Old 3/31/10, 10:30 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: 125 amp main 200 amp sub (Is it a issue)

IMHO, whether or not the panel and service is correctly sized for the load connected is well beyond the SOP for home inspections and a HI can create unnecessary liabiity for themselves by stating an opinion they are not qualified (or being paid) to make. While not intending to point a finger at any HI, I personally would not do that unless I had been hired to do an engineering evaluation. While the load question has not been answered, the condition is not hazardous in that the 125 amp breaker will protect the system if the load is excessive under some conditions.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Double tap at main lugs gmathias Electrical Inspections 4 8/8/07 7:20 PM
bonding main hose bib with pex Scott Schultz Electrical Inspections 5 6/21/07 11:39 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 5:12 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts