Old 10/3/12, 10:51 PM
John Graham, II John Graham, II is offline
Default 14 gauge on a 20 amp breaker
O.K. Here goes... Whenever I've found a 14 gauge wire on a 20 amp breaker, I've always said it was a safety hazard for reasons we all know. Here's the tricky part. I spoke with an electrician in the area that told me on older systems, it was fine (but not for new construction). Apparently, a 14 gauge wire can carry 20 amps safely but the "powers-that-be" say it can only carry 15 amps just as a built-in safety measure.
My gut feeling is still call it out as a safety hazard but technically, according to this electrician, it's O.K.
Thoughts?
Jonathan Graham
HouseCalls Home Inspection Services
Need a home inspection in Massachusetts? Check out InterNACHI's listing of Massachusetts certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
Old 10/3/12, 11:07 PM
Robert Meier's Avatar
Default Re: 14 gauge on a 20 amp breaker
Short answer electrician is incorrect. There are some instances where it may be permitted (A/C units, motor, etc.) but in general it is not permitted by the NEC. Here's the relevant NEC section:
240.4(D) Small Conductors. Unless specifically permitted in
240.4(E) or (G), the overcurrent protection shall not exceed
that required by (D)(1) through (D)(7) after any correction
factors for ambient temperature and number of conductors
have been applied.
(1) 18 AWG Copper. 7 amperes, provided all the follow-
ing conditions are met:
(1) Continuous loads do not exceed 5.6 amperes.
(2) Overcurrent protection is provided by one of the fol-
lowing:
a. Branch-circuit-rated circuit breakers listed and marked
for use with 18 AWG copper wire
b. Branch-circuit-rated fuses listed and marked for use
c. Class CC, Class J, or Class T fuses
(2) 16 AWG Copper. 10 amperes, provided all the follow-
(1) Continuous loads do not exceed 8 amperes.
lowing:
marked for use with 16 AWG copper wire
(3) 14 AWG Copper. 15 amperes
Old 10/3/12, 11:31 PM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
Yep, I hear this kinda "crap" all too often - "It used to be ok like this but they changed the code."
Like Robert said - the electrician is wrong...
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE «
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Old 10/4/12, 6:30 AM
You can always ask for the letter that will never come, that is the letter with here opinion on there letter head with there license #.
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Certified Level II Infrared Thermographer
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Old 10/5/12, 1:59 AM
wblackmon's Avatar
wblackmon wblackmon is offline
In all honesty, the older code was generally more stringent on conductor ampacity. Like all has said, the electrician was dead wrong. I could not tell you how many misinformed or underinformed electricians I have dealt with over the years. Quick reference books are a major contributor to the problem.
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 10:51 PM
Main panel...recommendation ? dnasser Electrical Inspections 6 11/22/09 10:55 PM
Re-Inspection apolillo Electrical Inspections 7 11/14/09 8:01 PM
Double Tapped Breaker tjohnson3 Electrical Inspections 8 4/20/07 10:04 AM
wire gauge / breaker rating jweinberg Electrical Inspections 19 7/16/06 5:36 PM