#1
|
|||
|
|||
|
Ok guys, i should now this one, but i am second guessing myself. I was discussing this with a buddy of mine and he got me questioning myself.
I have a 150amp main disconnect panel outside at the meter that leads to a distribution panel inside with its own main disconnect rated at 200amps. isn't the 150amp followed by the 200amp wrong? In other words is the 200amp breaker over sized? Last edited by pkusic; 9/22/10 at 12:44 AM.. Reason: clearified question |
| Need a home inspection in Idaho? Check out InterNACHI's listing of Idaho certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
I would think the 200 amp breaker protects the panel, which can only suffer 150 amps at most anyway. I don't see a problem... other than someone, looking at the breaker, might incorrectly assume they have a 200 amp service.
Nick Gromicko, Certified Master Inspector Find a Home Inspector "Just as iron sharpens iron, one man sharpens another." Proverbs 27:17 |
|
#3
|
||||
|
||||
|
The 150 amp disconnect is the only "main" disconnect. The service installation the way you describe can not draw more than 150 amps.
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#4
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Other than the potential problem that Nick cited (not a code issue) the installation is code compliant.
|
|
#5
|
||||
|
||||
|
You should take the NachiTV electrical course, it addresses that nicely
|
|
#6
|
|||
|
|||
|
Thanks, i was over thinking. Of course the 150amp main disconnect is going to regulate the draw to 150amps only.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Panel Questions - main, mid, sub | lfoster | Electrical Inspections | 6 | 11/11/08 9:42 PM |
| Main and Sub Panel | gheller | Electrical Inspections | 10 | 9/25/08 9:22 PM |
| Outlet off of Main Panel? | jlevy | Electrical Inspections | 2 | 8/5/08 5:18 PM |
| Main at meter pole, distribution in home | lfoster | Electrical Inspections | 7 | 7/17/08 10:31 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |