Default 150amp Main to a 200amp distribution panel

Ok guys, i should now this one, but i am second guessing myself. I was discussing this with a buddy of mine and he got me questioning myself.

I have a 150amp main disconnect panel outside at the meter that leads to a distribution panel inside with its own main disconnect rated at 200amps. isn't the 150amp followed by the 200amp wrong? In other words is the 200amp breaker over sized?

Last edited by pkusic; 9/22/10 at 12:44 AM.. Reason: clearified question
Reply With Quote
Need a home inspection in Idaho? Check out InterNACHI's listing of Idaho certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/22/10, 12:46 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: 150amp Main to a 200amp distribution panel

I would think the 200 amp breaker protects the panel, which can only suffer 150 amps at most anyway. I don't see a problem... other than someone, looking at the breaker, might incorrectly assume they have a 200 amp service.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #3  
Old 9/22/10, 2:09 AM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: 150amp Main to a 200amp distribution panel

Quote:
Originally Posted by pkusic View Post

I have a 150amp main disconnect panel outside at the meter that leads to a distribution panel inside with its own main disconnect rated at 200amps. isn't the 150amp followed by the 200amp wrong? In other words is the 200amp breaker over sized?
The 150 amp disconnect is the only "main" disconnect. The service installation the way you describe can not draw more than 150 amps.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #4  
Old 9/22/10, 4:34 AM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 150amp Main to a 200amp distribution panel

Other than the potential problem that Nick cited (not a code issue) the installation is code compliant.
Reply With Quote
  #5  
Old 9/22/10, 8:37 AM
Kenneth Dolin's Avatar
Kenneth Dolin Kenneth Dolin is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Palm Beach County, Florida
Posts: 502
Default Re: 150amp Main to a 200amp distribution panel

You should take the NachiTV electrical course, it addresses that nicely



Ken Dolin
Kenco Home Inspections
WWW.Kenco.org
State of Florida Licensed Home Inspector HI 59
Reply With Quote
  #6  
Old 9/22/10, 6:46 PM
Paul A. Kusic Paul A. Kusic is offline
InterNACHI Member
 
Join Date: Nov 2007
Location: Orlando, FL
Posts: 20
Default Re: 150amp Main to a 200amp distribution panel

Thanks, i was over thinking. Of course the 150amp main disconnect is going to regulate the draw to 150amps only.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Panel Questions - main, mid, sub lfoster Electrical Inspections 6 11/11/08 9:42 PM
Main and Sub Panel gheller Electrical Inspections 10 9/25/08 9:22 PM
Outlet off of Main Panel? jlevy Electrical Inspections 2 8/5/08 5:18 PM
Main at meter pole, distribution in home lfoster Electrical Inspections 7 7/17/08 10:31 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 5:14 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts