Default 2 GFCI questions

Hi,

This bathtub has air jets. The pump runs on its own circuit, but just a regular 15 amp breaker. I assume it needs to be GFCI protected.
Could the gfci protection be anywhere else, ie. behind the tub panel perhaps? Anyone seen that before?

Also, for 2nd picture, these kitchen receptacles, with the extra notch, they are rated for 20 amps, is that correct? They also were on regular circuit breakers and not gfci protected breakers.

1 and a half year old 500K home.

Thanks for feedback guys,

Paul-Marc
Attached Thumbnails
2-gfci-questions-img_1911.jpg   2-gfci-questions-img_1909.jpg   2-gfci-questions-img_1910.jpg  
Reply With Quote
Find an InterNACHI certified Ohio Home Inspector (and anywhere else in North America)
  #2  
Old 5/23/09, 9:23 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,403
Default Re: 2 GFCI questions

Quote:
Originally Posted by pabrioux View Post
Hi,

This bathtub has air jets. The pump runs on its own circuit, but just a regular 15 amp breaker. I assume it needs to be GFCI protected.
Could the gfci protection be anywhere else, ie. behind the tub panel perhaps? Anyone seen that before?

Yes, sometimes they are behind the access or tile, under the tub in the crawlspace or in the master closet or toilet room.

Also, for 2nd picture, these kitchen receptacles, with the extra notch, they are rated for 20 amps, is that correct? They also were on regular circuit breakers and not gfci protected breakers.

Did you try to trip them with a GFCI tester? They need to be on a GFCI circuit, the 20 amp version is good.


1 and a half year old 500K home.

Thanks for feedback guys,

Paul-Marc

sgdgfdgfg



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207

"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #3  
Old 5/24/09, 10:04 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,697
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 2 GFCI questions

Quote:
Originally Posted by pabrioux View Post
Hi,

This bathtub has air jets. The pump runs on its own circuit, but just a regular 15 amp breaker. I assume it needs to be GFCI protected.
Could the gfci protection be anywhere else, ie. behind the tub panel perhaps? Anyone seen that before?

Also, for 2nd picture, these kitchen receptacles, with the extra notch, they are rated for 20 amps, is that correct? They also were on regular circuit breakers and not gfci protected breakers.

1 and a half year old 500K home.

Thanks for feedback guys,

Paul-Marc
Howdy,

I believe Mr. King has addressed your conditions but I ( as always ) will elaborate on specific things. In your first question, you are correct in that it should be protected by a GFCI circuit ( NEC 680.71 ). The receptacle if and electrical equipment for the hydromassage bathtub must be accessible without damaging the structure or surface. If it is tiled and removing the access would damage the tile then nope...not allowed.

Now sad to say it is not until the 2008 NEC that we are clear that an individual branch circuit must be run to this type of tub which would make the location of the GFCI simple. Either it is at the panel in the form of a breaker or at the tub itself. Under the 2005 NEC it does not spell out the fact it is a individual circuit but we kinda get their with the loading issues of 210.23 in previous versions but again i digress.

In regards to the 20A receptacles on the kitchen counter area, indeed they need to be GFCI protected and if not it is wrong and I am shocked a local municipal would miss something like that. If my guys missed that and I went behind them as their supervisor I would be very upset.



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.
Reply With Quote
  #4  
Old 5/24/09, 10:36 AM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 967
Default Re: 2 GFCI questions

Quote:
Originally Posted by pabernathy View Post
In regards to the 20A receptacles on the kitchen counter area, indeed they need to be GFCI protected and if not it is wrong and I am shocked a local municipal would miss something like that. If my guys missed that and I went behind them as their supervisor I would be very upset.
Only if within 1 m (39.25 in.) of the sink and only after January 1/ 03, Rule 26-700(12) .

Different country, different rules.

Hope this help,



Marcel Gratton # NCA00376, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/

Reply With Quote
  #5  
Old 5/24/09, 12:27 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,697
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: 2 GFCI questions

Should have been posted in the Canada section then....



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.
Reply With Quote
  #6  
Old 5/24/09, 2:14 PM
Paul-Marc Abrioux Paul-Marc Abrioux is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Peterborough, ON
Posts: 129
Default Re: 2 GFCI questions

Thank you Paul, Marcel and Bruce! I am surprised as well as all other locations needing GFCI protection had the proper receptacles. Perhaps I missed something, we'll see. I only saw the AFCI breakers at the main panel for the bedrooms, no GFCI breakers.

Now, perhaps these outlets are downstream of a GFCI receptacle elsewhere? They did have their own breakers though...

I suppose they are not quite within 1m of the sink, but still very close (within 2m).

Thanks again,

Paul-Marc
Reply With Quote
  #7  
Old 5/24/09, 7:19 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 4,410
Send a message via Yahoo to jfunderburk
Default Re: 2 GFCI questions

I use this pretty often: "We could not confirm that the hydro-spa is equipped with ground fault protection, which is an important safety feature that should be verified as being present or added. Ground fault circuit interrupter (GFCI) receptacles have been required for spa tubs since 1987."



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 5/24/09, 9:31 PM
Paul-Marc Abrioux Paul-Marc Abrioux is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Peterborough, ON
Posts: 129
Default Re: 2 GFCI questions

Quote:
Originally Posted by jfunderburk View Post
I use this pretty often: "We could not confirm that the hydro-spa is equipped with ground fault protection, which is an important safety feature that should be verified as being present or added. Ground fault circuit interrupter (GFCI) receptacles have been required for spa tubs since 1987."
That's a good one, thanks.

Paul-Marc
Reply With Quote
  #9  
Old 5/29/09, 6:22 PM
Jerry Bettencourt Jerry Bettencourt is offline
InterNACHI Member
 
Join Date: Oct 2007
Location: Stoney Creek, ON
Posts: 516
Default Re: 2 GFCI questions

Paul, Marcel was correct. If you do not have it go to Home Depot and buy the Electrical Code Simplified book, it breaks down the Electrical safety Code and is a must have for a Home Inspector in my opinion. I believe it was only about $18.00, and yes there needs to be a GFCI for the whirlpool tub somewhere I find them behind the access panel many times.



JERRY BETTENCOURT
HOMETEST HOME INSPECTIONS
www.hometestinspections.com
www.hamiltonthermalimaging.com
hometestinspections@hotmail.com
I will keep my thoughts positive because my thoughts become my words. I will keep my words positive because my words become my actions. I will keep my actions positive because my actions become my values. I will keep my values positive because my values become my DESTINY!
United Family Martial Arts Student Creed
Reply With Quote
  #10  
Old 5/29/09, 8:49 PM
Paul-Marc Abrioux Paul-Marc Abrioux is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Peterborough, ON
Posts: 129
Default Re: 2 GFCI questions

Thanks Jerry, I'll have a look at that book. I didn't want to remove the front panel for the tub for fear of damaging the finish, but suggested that it might be there indeed.

Thanks,

Paul-Marc
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
More GFCI info from U/L Greg Fretwell Electrical 9 12/4/07 8:33 PM
GFCI Safety Notice rcooke Electrical 1 10/30/07 12:29 PM
GFCI Questions egriffin Electrical 3 1/27/07 7:10 PM
The question asked on the new HI Study test here? jtedesco1 Electrical 28 10/4/06 9:31 AM
AFCI Questions and Answers - Mike Holt pabernathy Electrical 0 7/7/06 12:24 PM