I typically call out when I find two grounded conductors attached to the same terminal on a bus bar as "improper condition. Each netral conductor should have it's own terminal". I had a client ask me why, and I started to think about various scenarios, but decided not to guess. So, I thought I would ask this forum for an educated answer to this.
|
|
#2
|
||||
|
||||
|
Greg,
This particular issue has been asked about many times over. Catch up on some great info (regarding double lugged neutrals) at the following two threads... http://www.nachi.org/forum/f19/speaking-double-lugging-3778/ http://www.nachi.org/bbsystem/viewtopic.php?t=1620 |
|
#3
|
|||
|
|||
|
Please Note:
gmathias is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks. Those links were very informative.
|
|
#4
|
|||
|
|||
|
Hmm...I think I have covered this issue MANY times.....So a search on 408.21 on this board......or check some of my older posts from my profile page and you may find it helpful. Too tired to go into it all over again....
Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Electrician signs off 'ganged neutrals'...now what? | mgault | Electrical Inspections | 16 | 6/2/07 11:09 PM |
| Double lugged neutrals | lschmid | Electrical Inspections | 14 | 8/11/06 9:11 AM |
| Speaking of double lugging | tgardner | Electrical Inspections | 16 | 4/19/06 5:09 AM |
| grounds and neutrals | nbhi | Electrical Inspections | 4 | 4/4/06 11:14 PM |
| Double lugging neutrals? | JohnH515 | Electrical Inspections | 17 | 3/3/06 10:05 AM |